Discuss Pump or stat at UK Plumbers Forums; Hi can anyone please help with a control issue I'm not sure about. Old system no motorized valves or wall stat, just a pipe stat at hotpress. 1 circulating pump ...
  1. #1
    Member
    Join Date
    Jan 2013
    Posts
    49
    Thanks
    0
    Thanked 1 Time in 1 Post

    Default Pump or stat

    Hi can anyone please help with a control issue I'm not sure about. Old system no motorized valves or wall stat, just a pipe stat at hotpress. 1 circulating pump for oil boiler and fire. Boiler fires up NP but only for 5 to 10 mins so I thought pump. Householder checked for vibration when boiler turned on, no vibration so thought def pump. Now he says it is vibrating and a little heat in rads since he lit the fire. Boiler still won't keep firing unless u turn boiler stat up. I'm now thinking dodgy boiler stat although its not going onto the high limit and tripping out. Any ideas and thanks in advance.

  2. #2
    Member

    Join Date
    Oct 2011
    Location
    N.Ireland, United Kingdom
    Posts
    7,114
    Thanks
    247
    Thanked 812 Times in 792 Posts

    Default Re: Pump or stat

    One pump for the oil boiler and fire??? That can't be right, unless the system is a DIY bodge.
    I would still say it could be circulating pump. It could be vibrating but not pumping.
    Check directly the pipes at the oil boiler temperature first to see if hot.

  3. #3
    Member
    Join Date
    Jan 2013
    Posts
    49
    Thanks
    0
    Thanked 1 Time in 1 Post

    Default Re: Pump or stat

    Thanks best, I wud personally like to fix this if I can as the guys father did me a favour with my car before. The old woman who did live in the house for 70 years says def only 1 pump. If the time clock powers the pump when boiler is running, what powers the pump when the boiler is off and the fire is only lit. Is there a sensor from the back boiler. I've no idea only oftec 101 not a plumber.

  4. #4
    Member
    Last Plumber's Avatar
    Join Date
    Aug 2016
    Location
    Lancashire
    Posts
    1,589
    Thanks
    1
    Thanked 149 Times in 147 Posts

    Default Re: Pump or stat

    This sounds like a DIY installation?

    I would recommend you get a heating engineer to look it over for you to rule out any lurking dangers

  5. #5
    Member

    Join Date
    Oct 2011
    Location
    N.Ireland, United Kingdom
    Posts
    7,114
    Thanks
    247
    Thanked 812 Times in 792 Posts

    Default Re: Pump or stat

    Definitely sounds DIY. It might be done in a stupid way with primary flow & return from
    fire also linked to rad circuit and maybe some upstairs rads are working on gravity.
    It is the fire side I would be worried about as it is uncontrolled.
    Tell the owner not to light the fire until a heating engineer checks the system and gives advice on any issues. The pump, if it is definitely doing the oil boiler could be replaced to test
    Last Plumber likes this.

  6. #6
    Member
    Join Date
    Jan 2013
    Posts
    49
    Thanks
    0
    Thanked 1 Time in 1 Post

    Default Re: Pump or stat

    Thanks for all the input, safety first. While I service, repair oil boilers , replace circulating pumps , motorized valves etc I'm not a plumber so don't get involved. I have done oftec 101 and serviced and repaired quite a lot in the last 11 years. His plumber friend coming out tonight, I still think its pump, its fitted so the bearings won't get lubricated. No pump at boiler , just a pump near the fire and the elderly couple who owned the house insist 1 pump for both oil and back boiler.

Everybody loves a good deal: Deals and Discounts on Dozens of Powertools!
Everybody loves a good deal: Deals and Discounts on Dozens of Powertools!

Similar Threads

  1. Cylinder stat or pipe stat? Best way
    By Cubbs in forum Plumbing Forum
    Replies: 4
    Last Post: 15-02-2016, 01:04 AM
  2. Draton combi-stat. Moving a room stat.
    By cjonesguitar in forum Central Heating Forum
    Replies: 1
    Last Post: 26-01-2013, 08:14 PM
  3. frost stat.... and room stat wiring
    By handsomejackuk in forum Central Heating Forum
    Replies: 1
    Last Post: 26-11-2012, 10:35 PM
  4. Existing room stat with wireless programmer and stat?
    By p0bber in forum Central Heating Forum
    Replies: 2
    Last Post: 08-11-2010, 11:20 PM

Visitors found this page by searching for:

Nobody landed on this page from a search engine, yet!

Tags for this Thread


Try our Talk Electrician Forum and our popular Tilers Forums for more free advice from professional tradesmen.
Tens of thousands of tradesmen and over 2 million combined posts.


Plumbers Forums is a community-driven forum shared between all members.