    Wrap a load of PTFE round it and it won't leak.

    I don't use compression fittings as this tends to happen, never have. Rare to get a leak from a flared fitting. I only use compressions where there are space contraints.
    Last edited by WHPES; 17-03-2013 at 06:17 PM.

  2. #38
    UK Plumbersforums Trusted Advisor.


    Join Date
    Jan 2008
    Location
    North Yorkshire
    Posts
    4,781
    Thanks
    2
    Thanked 329 Times in 300 Posts

    Default Re: Sooted up boiler and other tips

    If you can't find the test point plug / screw for the boiler after you've finished doing a combustion test, it's usually stuck to the magnet on the back of your analyser.

  3. #39
    UK Plumbersforums Trusted Advisor.


    Join Date
    Jan 2008
    Location
    North Yorkshire
    Posts
    4,781
    Thanks
    2
    Thanked 329 Times in 300 Posts

    Default Re: Sooted up boiler and other tips

    List of suggested oil engineers tools (by no means definitive)

    I only carry one type of flexi hose, the one HWOS calls Long01. If I find a different one on, I change the fittings to suit the Long01 hose. I don't see the point of carrying loads of different ended hoses. In all the time I have been doing boilers I have only ever come across 2 boilers which this hose did not fit and needed an elbow at the opposite end to the pump because of shortage of space.

    I recommend that everyone gets into the habit of using flared fittings as opposed to compressions. The best price seems to be HWOS or BES


    1. Combustion analyser and printer (I scrounge till rolls from my local pub for it as one lasts ages and I'd never get through a full box of them)
    2. Smoke pump and papers
    3. Pressure and vacuum gauge set
    4. Fuel priming pump (one from an automotive supplier is adequate) and rubber hose that will fit on the end.
    5. Bearing puller for removing fans and motor bearings - I find this is the best BERGEN Prof Heavy Duty Bearing Puller 'B' Type 24-55mm on eBay (end time 06-Mar-11 19:11:56 GMT)
    6. couple of pairs of 6202RS bearings (from Ebay - but only get good branded ones, SKF, NTC etc) You'll know when the bearings are worn as the burner motor will make a rumbling / whining noise. You can also purchase from an automotive supplier as they are the same as alternator bearings.
    7. Pump drive couplings from HWOS
    8. Selection of nipples, elbows, couplings etc from the fittings page at HWOS
    9. Pipe flaring tool
    10. OFTEC forms - servicing and commissioning, oil storage risk assessment, installation
    11. One of those magnetic pickup tools which looks like a radio aerial with a magnet on the end
    12. 1/4" ratchet set and extension pieces (get a good quality set such as Britool)
    13. T handle long reach hex set
    14. Screwdriver handled socket driver
    15. glass rope and glass rope adhesive
    16. STAG B jointing compound (prefer this to Heldite another post mentioned as Heldite is awful to get off your fingers etc)
    17. PTFE tape (normal and gas tite (yellow spool))
    18. rolls of 10mm and 8mm copper pipe (white plastic coated) and roll of uncoated
    19. spare 3m 65 and 90 degreesC Teddington KBB fire valves (you can get more of different sizes as you go on) 1.5m is too small for many sites.
    20. GOOD selection of nozzles (from 0.50 to 1.0 USgall/h - larger ones you won't come across often and can order them as required. Get just kerosene ones to begin with (ES & EH). Some boilers will specify W nozzles you can buy as and when on next day delivery)
    21. PLENTY of 10mm brass inserts for copper pipe (HWOS do packs of 100)
    22. Selection of steel nuts for when you loose some behind the back of a boiler so you don't need to spend ages looking for them.
    23. Heat proof gloves for dismantling hot combustion chambers (I use welders gloves)
    24. disposable vinyl gloves like the dentist uses
    25. Barrier cream
    26. Beaded hand cleaner
    27. Hand cream
    28. One of each of the cleaning brushes that HWOS do
    29. Container to put waste oil into when cleaning out filters etc
    30. Spare filter elements (just get the two Crossland ones to begin with)
    31. Vacuum cleaner and spare bags (I use an old VAX cleaner but any will do)
    32. Dust sheets
    33. Kneepads (a MUST HAVE!)
    34. Tub of fire cement
    35. Tube of heatseal silicone and gun
    36. Multimeter
    37. Spare 3 amp fuses (a lot of boilers just have 13 amp fitted so should be changed)
    38. Boiler manufacturers literature to show to customers when persuading them to change to a new boiler.
    39. long 18/19mm drill but for drillling holes through walls for oil lines / fire valve capillaries
    40. Parts organiser boxes for all your fittings
    41. Nozzle box
    42. Set of flat, pozi and philips screwdrivers
    43. 8mm copper pipe and fittings for where you have a tank lower than the boiler (lot of people post problems on here caused by too large diameter pipe where tank is lower than boiler - always follow the table in the OFTEC book!)
    44. Set of combination spanners from 6mm up to 21mm and inlcuding ALL the inbetween sizes
    45. Scraper (paint scraper)
    46. Selection of metric machine screws (probably be able to get an assortment box from Toolstation these days)
    47. Torch (head torches are useful)
    48. Tape measure
    49. Circlip pliers
    50. pump pliers
    51. Standard pliers/nippers
    52. Set of adjustable spanners
    53. Selection of brass bushes, 3/8 to 1/4, 1/2 to 1/4 and 1/2 to 3/8 for example
    54. Mini pipe bender
    55. Round profile drift for reshaping deformed pipe ends.
    56. Small flat, rat tail and half round files
    57. Set of T handled Torx drivers
    58. Selection of o rings including 13mm ID x 4mm for Sika flow switches
    Last edited by croppie; 29-03-2013 at 08:04 PM. Reason: Someone forgot a couple of bits........
    Newpark7 likes this.

  4. The Following 3 Users Say Thank You to WHPES For This Useful Post:


  5. #40
    UK Plumbersforums Trusted Advisor.


    Join Date
    Apr 2009
    Location
    Tunbridge Wells
    Posts
    5,774
    Thanks
    576
    Thanked 472 Times in 397 Posts

    Default Re: Sooted up boiler and other tips

    Good work WHEPES. A comprehensive list there mate.
    Kent based plumber and heating engineer. Gas Safe and OFTEC registered

    www.prestigeplumbers.co.uk

  6. #41
    UK Plumbersforums Trusted Advisor.

    dontknowitall's Avatar
    Join Date
    Apr 2008
    Location
    Herefordshire
    Posts
    6,122
    Thanks
    516
    Thanked 683 Times in 614 Posts

    Default Re: Sooted up boiler and other tips

    Another tip:

    Intermittent cut out problem that happens only a few times a year with balanced flues.

    This could be wind blowing fumes back into the flue which starves the boiler of oxygen.
    I'm not a complete idiot; some parts are missing

  7. #42
    Member
    Join Date
    Jul 2012
    Location
    derbyshire
    Posts
    124
    Thanks
    3
    Thanked 7 Times in 7 Posts

    Default Re: Sooted up boiler and other tips

    Good ones there

  8. #43
    Forum Thug



    super-mod
    croppie's Avatar
    Join Date
    Jul 2010
    Location
    Lurking somewhere, generally up to no good........
    Posts
    23,888
    Thanks
    1,541
    Thanked 1,848 Times in 1,684 Posts

    Default Re: Sooted up boiler and other tips

    If you lose your smoke chart then help is at hand!

    http://www.soliftec.com/Ringelmann%20Smoke%20Chart.pdf

    Also a handy app for nozzle calculation - Both Android and Iphone.

    EOGB launch nozzle calculator App for iPhone and Android phones | EOGB Energy Products Ltd
    Propino Tibi Salutem! Usque ad Mortem Bibendum!

    Croppie
    (By the way, I'm commercial!)


    IMPORTANT:
    Carbon Monoxide can be produced when ANY fuel is burnt, including oil, gas, wood and coal
    .


    GSR? Want gas safety or boiler repair advice? We will check out that you're genuine via the gas safe website, so please don't be offended when we ask for your details. DIYers, odd job people and have a go heroes need not apply.


  9. #44
    Member
    Join Date
    Jul 2012
    Location
    derbyshire
    Posts
    124
    Thanks
    3
    Thanked 7 Times in 7 Posts

    Default Re: Sooted up boiler and other tips

    Quote Originally Posted by croppie View Post
    If you lose your smoke chart then help is at hand!

    http://www.soliftec.com/Ringelmann%20Smoke%20Chart.pdf

    Also a handy app for nozzle calculation - Both Android and Iphone.

    EOGB launch nozzle calculator App for iPhone and Android phones | EOGB Energy Products Ltd
    Lol cheers mate did steve PM ya mate

  10. #45
    Forum Thug



    super-mod
    croppie's Avatar
    Join Date
    Jul 2010
    Location
    Lurking somewhere, generally up to no good........
    Posts
    23,888
    Thanks
    1,541
    Thanked 1,848 Times in 1,684 Posts

    Default Re: Sooted up boiler and other tips

    Quote Originally Posted by b.lynch plum View Post
    Lol cheers mate did steve PM ya mate
    aye, he did.
    Propino Tibi Salutem! Usque ad Mortem Bibendum!

    Croppie
    (By the way, I'm commercial!)


    IMPORTANT:
    Carbon Monoxide can be produced when ANY fuel is burnt, including oil, gas, wood and coal
    .


    GSR? Want gas safety or boiler repair advice? We will check out that you're genuine via the gas safe website, so please don't be offended when we ask for your details. DIYers, odd job people and have a go heroes need not apply.


  11. #46
    UK Plumbersforums Trusted Advisor.


    Join Date
    Jan 2008
    Location
    North Yorkshire
    Posts
    4,781
    Thanks
    2
    Thanked 329 Times in 300 Posts

    Default Re: Sooted up boiler and other tips

    Stuck baffles - smear the edges with open gear grease (aerosol type is less messy), put a rag on top of the baffle and soak rag with spray from a DIY pipe freezing aerosol. You will need a large adjustable or mole wrench clamped up tight on the baffle edge to give you some leverage.

    Have removed sulphur debris jamming baffles using swimming pool tile cleaner (make sure the combustion chamber is thoroughly washed down and dried out afterwards so you don't leave any in)
    Last edited by WHPES; 16-04-2013 at 10:14 AM.
    lame plumber likes this.

  12. #47
    Member
    Killy Bing's Avatar
    Join Date
    Nov 2012
    Location
    Maidstone, kent
    Posts
    4,257
    Thanks
    146
    Thanked 370 Times in 338 Posts

    Default Re: Sooted up boiler and other tips

    I cant believe this hasnt been said! Always...always....always kill the power to the boiler or unplug the burner!

    who knew a pair of snickers trousers could withstand a .60 es for a second.......
    yeah kinda wondering why i continued on with my apprentiship after that!

  13. #48
    UK Plumbersforums Trusted Advisor.


    Join Date
    Jan 2008
    Location
    North Yorkshire
    Posts
    4,781
    Thanks
    2
    Thanked 329 Times in 300 Posts

    Default Re: Sooted up boiler and other tips

    I cant believe this hasnt been said! Always...always....always kill the power to the boiler or unplug the burner!

    who knew a pair of snickers trousers could withstand a .60 es for a second.......
    yeah kinda wondering why i continued on with my apprentiship after that!
    It hasn't been said as we kind of assume that anyone working on boilers is not sufficiently clueless or intoxicated as to need to be told something like this any more than they need to be told to bring a toolbox with them when they go to work on a boiler, or to put their underpants on when they get dressed. Anyone who actually needs to be told to kill the power shouldn't be let anywhere near a boiler, or for that matter be allowed to drive a vehicle to get to said boiler either.
    Last edited by WHPES; 05-05-2013 at 10:00 PM.
    villa_tom and Dannypipe like this.

Everybody loves a good deal: Deals and Discounts on Dozens of Powertools!
Everybody loves a good deal: Deals and Discounts on Dozens of Powertools!

Similar Threads

  1. boiler breakdown tips from training centre
    By lordyjordy111 in forum Gas Safe Register Forum - Public Forum
    Replies: 22
    Last Post: 27-05-2013, 10:49 PM
  2. boiler breakdown tips from training centre
    By lordyjordy111 in forum Central Heating Forum
    Replies: 2
    Last Post: 26-05-2013, 10:46 PM
  3. Tips on removing a back boiler
    By gregg1908 in forum Gas Safe Register Forum - Public Forum
    Replies: 9
    Last Post: 25-08-2011, 08:01 PM
  4. Baxi 552 BBU - sooted up
    By maintain2let in forum Central Heating Forum
    Replies: 8
    Last Post: 21-02-2011, 01:01 PM

Visitors found this page by searching for:

boiler sooting up

oil boiler sooting up