flueing problem
I have a problem on a site where the flue on a HRM Wallster is too close to an extract vent.
In the gas industry the distance for this should be 300mm but if it is too close the problem can be overcome by using an open and shut extract terminal.
With oil this distance is 600mm and oftec will not sanction the use of the same terminal. HRM do not make a pluming kit either.
I'm resolved to having to move the boilers or vents but any ideas would be gratefully recieved.
-
23-07-2012 #2UK Plumbersforums Trusted Advisor.


- Join Date
- Jan 2008
- Location
- North Yorkshire
- Posts
- 4,150
- Thanks
- 2
- Thanked 285 Times in 261 Posts
Re: flueing problem
Duct the vent away from the terminal, or relocate the vent
Similar Threads
-
flueing/brewing problem
By stani in forum Plumbing ForumReplies: 5Last Post: 17-02-2012, 04:03 PM -
Commercial flueing
By diamondgas in forum Gas Safe Register Forum - Public ForumReplies: 36Last Post: 04-01-2012, 08:39 AM -
flueing through a pitched,felted plywood roof help.
By moogwai in forum Central Heating ForumReplies: 26Last Post: 16-01-2011, 11:08 PM -
flueing question for a cdi
By moogwai in forum Central Heating ForumReplies: 8Last Post: 14-12-2010, 10:22 AM -
flueing question
By moogwai in forum Gas Safe Register Forum - Public ForumReplies: 19Last Post: 05-01-2010, 07:17 PM



Reply With Quote










Electric towel rail
58 Minutes Ago in Bathrooms, Showers and Wetrooms