So went to a job today, replaced an old Randall 130 mechanical timer with a Honeywell st9400c on a y-plan system.

Water channel fine. Heating channel was fine in that it sent a signal (if the room stat was calling) to the 3 port, but nothing on SL. Figured a faulty head. Replaced the head and same thing. So took off the head and manually moved the paddle and seems free as a bird.

I’ve said to the custard I need to drain down and replace the entire valve as I don’t think it’s pushing far enough to make the connection.

Thing is, when demand is on heating and the actuator kicks in, I can hear the micro switch click at the end (unless it’s the spring I can hear but I doubt it), but still nothing on SL.

Am I missing something obvious here? (Can you hear the 2nd guessing???)
 
so you have 240 on heating calling and hot water (seperately) ?
 
I have 240 coming from the thermostat to the white on the 3 port when heating is in demand, nothing on water if not in demand.

Same with water and nothing on the heating ?
 
Same with water and nothing on the heating ?
But if I’m getting 240 on the white and the actuators moving over why wouldn’t that send 240 to SL (orange)? Unless the paddle isn’t moving over enough to make the connection..
 
Last edited:
Correct doesn't need much for it to not contact
 
But if I’m getting 240 on the white and the actuators moving over why wouldn’t that send 240 to SL (orange)?
If you are talking about CH only, there needs to be 240V on the grey wire (from HW thermostat Sat/Programmer HW Off) as well as 240V on the white wire from room stat.

In mid-position (CH and HW) the boiler gets its SL directly from the HW thermostat, not via the orange wire.
 
If you are talking about CH only, there needs to be 240V on the grey wire (from HW thermostat Sat/Programmer HW Off) as well as 240V on the white wire from room stat.

In mid-position (CH and HW) the boiler gets its SL directly from the HW thermostat, not via the orange wire.
Stupid f***ing 3 ports :D I wondered if that was needed but thought if the actuator was in operation after getting 240 on the white it would make the connection..
 

Reply to Timer replacement on a y plan system in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I want to reconnect some outbuildings to an existing water supply. The supply pipe is old 22mm MDPE and buried for a fair distance so not going to dig it up and replace it 😬. Question is can I use normal 22mm plumbing push-fit connectors to make the connection as finding 22mm MDPE fittings...
Replies
1
Views
201
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
249
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
5
Views
122
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock