hi guys. I'm one day closer to get my oftec ticket!
My customer has a old oil boiler that been getting served every year but recently the boiler been over heating and switching off but she said when she removes the front cover that it works. Would this be the case of a new thermostat?
 
hi guys. I'm one day closer to get my oftec ticket!
My customer has a old oil boiler that been getting served every year but recently the boiler been over heating and switching off but she said when she removes the front cover that it works. Would this be the case of a new thermostat?

Sounds a bit odd.
Test the calibration of the stat!!
Thermometer on flow out of boiler, (use your FGA on temp diff), turn stat to full. The stat should let it get to 82 degree's C plus or minus 3 degrees.

Hope I'm on same wave length and answering the right question??
 
Status
Not open for further replies.

Reply to Oil boiler thermostat problem in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

G
I have a danesmore 20/25 oil boiler and it is firing up but it’s producing no heat to the water or the radiators My next door neighbour an electrician has checked the cylinder and thermostat and they all check out ok so he thinks the problem is within the boiler Can Someone help give me some...
Replies
1
Views
383
I
I've had my tado system in my new build for 5 years now and it's been fine. Yesterday morning I changed the batteries on the second floor thermostat and now it's not switching on the boiler to heat that floor. The thermostat display is fine and the app is fine. All systems say they are fine and...
Replies
3
Views
296
Hi I am somewhat confused. My daughter has a combi boiler bought 2-3 years ago and has it timed to come on in morning for an hour and at night for a few hours using "auto"? mode I had been brought up to leave boilers on manual and set the thermostat low at night to prevent pipes from...
Replies
2
Views
316
Any advice welcome as plumber stumped Had 36-46 grant vortex utility boiler 7 years no problem recently oil tank move and tigerloop install (tank about 1m lower). 10 days later and boiler either doesn't fire or fires stops, fires runs splutters stops. Most it runs now is 10 mins, but that's...
Replies
4
Views
572
Grant Vortex 50/90 condensing oil boiler where the air tube spigot over the fan is not connected to the existing flue, should this be closed off with a Reillo cover plate to stop vermin getting into the open fan motor.If is blanked over will need a further combustion test to confirm adequate...
Replies
1
Views
332
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock