Went to a job recently where the radiator balancing was completely out.

Initially the customer was complaining of 2 radiators not warming up, 1 garage conversion room and another was the master bedroom. I've adjusted every rad, closest being on minimal and so on. The garage conversion radiator had a lot of gunk within it when i was bleeding it, so being only 600x600 i pulled it off and blasted it with a hose pipe to clear and crap.

Two day's later i get a call from them stating the rad's have gone cold again, bedroom this time being midly warm and the garage conversion stone cold.

Any idea's what might be happening now?

The system does look like it's had a lot of chop/change + add 0n's, in its lifetime. There are a total of 15 rads on the entire system, 4 being at least 2000mm wide and double panels.

Boiler is a Baxi Mains platinum combi, around 4 years old.
 
pump size?
boiler kw size?
 
I'd have a look at how they are piped. If they've added radiators and tee'd off the 15?mm feeds to other rads the pipework may not have the heat carrying capacity to heat all the radiators at once. If the weather gets cold and they turn on extra radiators (or up the TRVs) they might be robbing the two you are concerned with.
 
Sounds like micro. Dodgy piping or is pump on way out.
 
I'd have a look at how they are piped. If they've added radiators and tee'd off the 15?mm feeds to other rads the pipework may not have the heat carrying capacity to heat all the radiators at once. If the weather gets cold and they turn on extra radiators (or up the TRVs) they might be robbing the two you are concerned with.

problem is, the loft bedrooms are all under acoustic chipboards, ground floor is all under either tiling or solid wood flooring, 2 rooms are only carpetted, therefore i cant lift to see the piping layout
 
I was thinking about the expansion vessel and or pump, either add another expansion vessel or secondary pump.?? :(
 
Expansion vessel issue can't really stop the heating working, so not that.
Pump can be failing or clogged inside, or some crud is moving about system and blocking lockshield rad valves that are closed nearly off
 
I'd have a look at how they are piped. If they've added radiators and tee'd off the 15?mm feeds to other rads the pipework may not have the heat carrying capacity to heat all the radiators at once. If the weather gets cold and they turn on extra radiators (or up the TRVs) they might be robbing the two you are concerned with.
But if the OP has balanced the system, presumably he did it with all TRVs fully open, and so has already verified that the system works with all radiators on?
 
Run system turn off working rads drop last rad and drain from pipework see can you get any dirt from pipework or heat through will eliminate if pump getting to last rads or if its gone
 
Status
Not open for further replies.

Reply to Unusual radiator problem in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Creating content since 2001. Untold Media.

OFFICIAL SPONSORS

OFFICIAL SPONSORS

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock