Hi
Just done a Flow and pressure test
Flow 3,3 L in 10 secs =19.8
( did it 3 times pretty consistent)
Pressure 4 Bar
This however was at kitchen sink downstairs but looking to install Unvented Cylinder ( santon or Mega or similar) in loft ( servicing 1 bathroom + 1 onsuite ) will/ is this going to decrease by much going up approx 5.3 mtrs ( 2 storeys ) I think the pressures ok but the Flow may be on the cusp ?? Any thoughts
Thanks
Just done a Flow and pressure test
Flow 3,3 L in 10 secs =19.8
( did it 3 times pretty consistent)
Pressure 4 Bar
This however was at kitchen sink downstairs but looking to install Unvented Cylinder ( santon or Mega or similar) in loft ( servicing 1 bathroom + 1 onsuite ) will/ is this going to decrease by much going up approx 5.3 mtrs ( 2 storeys ) I think the pressures ok but the Flow may be on the cusp ?? Any thoughts