Rach1984

Hi all,

I'm looking to relocate my kitchen sink to a new location that will involve digging a trench through the length of the kitchen and laying pipes in the concrete floor. So far I've had inconsistent advice from our plumber, our builder (who took advice from a plumber he knew), and the building control team at our local council.

The distance between our proposed sink location to the soil stack is 4m, and we plan to get there in a straight run with no bends. My query has three parts:

What pipe size do I need? (It will be servicing a sink and dishwasher)?
What fall do I need over the 4m run?
How much concrete cover is required?

Any help or guidance will be appreciated. Thanks in advance for your help.

Rach :)
 
The rule of thumb for fall is 1 in 80, so about 5cm over 4m.
No matter how careful you are you will get grease/fat down that pipe so make sure there's a rodding point at each end. I'd put one in the middle too if practical although that may be overkill.
As for pipe size, I think 50mm is required for a 4m run, although I don't know the regs off the top of my head, I normally look it up in my 15 year old Treloar book if I need to know for sure, or google it :)
 
Thanks JCPlumb,

We've been told by our plumber that a 4" pipe will be needed as it's underground and will be stronger and also less prone to blocking. Our builder thought 2" was sufficient though, and he confirmed this with a plumber he'd worked with in the past. I have since gone back and queried it with our plumber who has confirmed with a colleague that a 4" pipe is definitely needed. I'm really just in the middle trying to make a judgement call based on the advice I've had so far. I'd be interested if anyone else had a view...?

With regards to the access point, would one in the middle of the run be sufficient rather than one at each end? There will be a kitchen island in the middle of the run so we could conceal an access point underneath.

Thanks again JCPlumb, your reply was appreciated.

Rach.
 
They're on my to do list for tomorrow, although I've already had some contradictory advice from them on a separate issue. The annoying thing is everyone is being really helpful, it's just nobody seems to agree with each other.

I'll let you know what they say after I've spoken to them, but in the meantime if anyone else has a view I'd really like to hear it. So far a 2" pipe has three votes and the 4" pipe two!! :)
 
Me personally a 4" pipe, just because kitchen sinks get all sorts of chucked down them. Lot cheaper to go a bit overkill now than redo later or have the hassle of keep unblocking.
 
Aswell as JCplump giving very good information to Rach, he/she has also given me some good information too. Thanks for the good info JC :)
 
I do not know that you are plump, i just know that you gave me some great info, your name is also JCplump. :D
 
Hi, would you mind sharing what Building Control requested regarding pipe thickness? I'm in the same boat at present. thanks a lot
 
Status
Not open for further replies.

Reply to Relocating kitchen sink in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello. I am planning to build a small half bath in my garage, next to a washing machine, using old showers plumbing. There was a stand-alone shower in the garage which has been removed. Unfortunately the pipes are only 1.5" on that side of the house since there's no bathroom and the house is...
Replies
0
Views
274
For residential housing, what are the current regulations and/or recommended/standard practices regarding the supply of cold water to the taps on kitchen sinks and bathroom washbasins? Must the supply come directly from the mains or can it come from the cold water storage tank? Or is the...
Replies
6
Views
691
Hello - I really need some solid advice. I recently purchased a home that has started having an awful smell coming from kitchen sink. I've cleaned multiple times, including p-pipe. Finally called a plumber & they said they will have to tear out the wall & lower the pipe where my kitchen piping...
Replies
4
Views
713
J
Hi all, Just in process of relocating kitchen & utility to other side of house but have a question re venting requirements. I intend to connect a sink and dishwasher in the kitchen and a sink and washing machine in the utility room to a 50mm waste pipe running within the suspended floor to...
Replies
0
Views
655
Joeab88
J
Looking for advice please, our plumber has left us in it and I think I may know why. So they where supposed to be fitting a cloakroom sink putting the pipe work in the wall then fitting these black shut off valves and black trap but can’t see how this is possible the way the work has been...
Replies
5
Views
332
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock