Donald777

Hi, my first post here,
I rent out a property with a open flue Johnson & Starley warm air heater (installed in the house in 1978!). The property is currently empty so I ran the heater for 30 mins to check it all worked OK, which it seemed to. A gas safety check was passed a few months ago. However I noticed a slight gas smell with the heater turned off which I though might be the gas valve needing some grease (I'd lived in the property years ago and an engineer had fixed it with grease so I suspected the same problem. The rental agency arranged for an engineer on there books to look at it. He phoned me to tell me:
1. Gas leak on inlet valve - (as expected)
2. Ventilation sub-standard - the heater is housed in a cuboard on the landing and there is a warm air outlet vent just below the cuboard and the a return air duct just above the cuboard - he advised that it should'nt have both this outlet and return in the same room.
3. Flue sub-standard above warm air unit (he explained on the phone that there was a right angle in the flue just above the unit because of a joist.
4. Return air-duct sub-standard - there is a 1inch gap in the ducting inside the heater cuboard between the grill and the ducting. This same ducting sits on top of the heater unit but is not screwed on to it. It should be screwed on and taped to seal it.
5. Flue terminal, not connected to flue. He explained the flue was unsupported in the loft and the underside of the ridge tile had disintegrated perhaps because of the weight.
He advised that it would be best to fit a conventional wet system (~£4600).

Obviously a bit shocked I looked at the system myself, just to come to terms with things myself. I also called a heating engineer myself and he looked at things. Regarding:
2/ The new engineer said that it's not a problem have the return duct in the same room (the landing) as one of the warm air outlet ducts (registers?).
3/ There is no right-angle in the flue but there are a couple of 30 or 45degree elbows to get the flue to come up under the ridge tile in the roof but at no time is the flue anywhere near horizontal.
4/ I can see the 1 inch gap problem here myself and so did the new engineer. Perhaps the whole unit has moved back on the plenum or per it was never fitted correctly.
5/ I can see both the flue and the venilation air-vent (that carries the air required for combustion) going up through the loft to two separate ridge tiles. They both appear to be connected, I'll try to get really close tomorrow for a detailed inspection. The new engineer didn't seem concerned about them.

The new engineer found two further problems though (call these 6 and 7):
6/ The heater unit was not securely fixed to the plenum and could move.
7/ The air vent that comes down from one of the ridge tiles is split just inside the top of the cuboard with one open end right at the top of the cuboard and the other continuing down to about a foot from the bottom. He explained that new regulations require each to have it's own vent to the outside air, they can't share a vent then split.

The new engineer is going to give me a quote for a replacement warm air unit from Johnson & Starley. We discussed the alternative new systems but I've tenants that need to move in, in 2 weeks and am worried that putting a wet system in would make mess and require carpets to be relaid and redecorating etc.

As there seem to be some serious differences of opinion about what is wrong with the system I thought I'd try to lookup the regulations myself. I've got as far as discovering BS5440-2:2009 but see that it's about £150. Then there's the challenge of reading and understanding it!

Do these new regulations apply to existing systems when they need repair?

I'd be grateful for any advice anyone has to offer, either on the problems or my best option. Ideally I'm hoping to hear that the existing system could be repaired and made safe for much less than a new warm air unit would cost to install. The second engineer explained that J&S were the only firm making warm air units for the UK now so could name there price to some extent. I'll make sure I'm sitting down when he calls with his quote!

I gather that CO detector would be a good idea as these open flue units are intrinsically less safe than sealed units.

Thanks
Donald
 
The WAU set up can be confusing and as so I wouldn't like to comment without seeing the majority of the issues with my own eyes. But if your gona pay to replace the system then I'd suggest that you get a combi in, there's far less issues to worry/think about.

Ps if your flue terminal is disconnected from the flue then I'd be inclined to classify this as AR (AT RISK). However I'd want to double check that in the unsafe sits book.
 
Iam a gas fitter although not ticketed in WAU but i can tell u that if u are having work carried out it needs to be to current standards.
The standards may have changed alot over the years on these but that is partially because when they go wrong they can kill poeple.
If your concerned about your tenents bite the bullet and get rid of this open flued appliance,for a couple of room sealed combis which will save you money over the coming years.
Just the fact it leaking gas for a second time ,it in a cupboard might add up to no property 5 years down the line.
IMHO ud be mad to buy a new WAU when u have alternatives.
Good luck
Paul
 
Thanks for your reply Mbear. I'd better check-out the Combi possibility rather than dismiss it due to the radiator/pipework installation upheaval.

About the AT RISK classification etc. he may have done this, he put a WARNING sticker on the unit and disconnected the gas and capped.

Thanks
Donald

Thanks Paul (prs1), that makes two on here advising to take the combi option. It is just one 3-bed house that I rent as a house (rather than split into flats etc) so I'm only after the single heater unit. If I can't find an engineer to safely repair the existing system, I'll get the second engineer to quote for both combi and non-combi (with water on Economy 7 as at present) too I think.
Thanks
Donald
 
Last edited by a moderator:
No harm in checkin it out pal

If hes cu and capped supply to WAU hes classed it as "ID" immeadiatly dangerous.
 
Last edited by a moderator:
cutting and capping is done to both at risk and immediately dangerous situations.

i would advise along the combi/system boiler as well.

anything with a balanced flue. there is no reason to install an open flued appliance in any domestic property.
 
Migo- at risk action is turn off appliance or supply and issue warning notice-with customers permission otherwise your phoning transco.

ID- disconnect(with customers permission) and issue warning notice,again if they will not give permission phone call to transco who will disconnect.
 
never bad practise to cut and gap an At Risk situation if the customer allows you to do so.
 
i dont give the client a choice. i cut and cap AR & ID - then inform the client, and ask for permission. if its refused then they can call the supplier for help. my conscious is clear.
 
i dont give the client a choice. i cut and cap AR & ID - then inform the client, and ask for permission. if its refused then they can call the supplier for help. my conscious is clear.

Agree,as far as I am concerned,they have allowed me to work on installation and that is permission enough for me
 
I see alot of folk agreeing that an At Risk is automatically a cut and cap.

At Risk means that there is a RISK of an ID type situation coming to fruition. So if a back boiler has no vent, this would be cut and capped? Of course not, the most you should do is turn the gas and elec off to the BBF with the customers permission, label it AR and leave the relevant paperwork. By doing this you are folowing the unsafe sits procedure correctly and you let the cust know that if they turn the gas & elec back on and use the BBF again then it's their resposibility if anything happens as you have warned them about the issues and they have signed to say they had read and understood the paperwork.

Cut and cap is for ID. When an appliance IS spilling or HAS a gas leak. An immediate danger to life or property.

I think be cautioun about safety issues is good obviously. But you can be overly cautious. If you cut and capped every back boiler with no vent then alot of folk wouldn't have any heating.
 
I think be cautioun about safety issues is good obviously. But you can be overly cautious. If you cut and capped every back boiler with no vent then alot of folk wouldn't have any heating.


Yes and a lot of folk would be alive

If I go to a back boiler with no ventilation I cap off as ID,if ventilation undersized or incorrectly positioned I would class as AR,if burning correctly ,I may leave on if requested in this instance but depends on each siduation

Same as if I go to a back boiler and the front room is being used as a bed room,boiler maybe working ok and ventilation ok but would cap off

I do not want dead customers and bits of paper saying it is ok for me to leave them to die

I want live customers even if it means them ringing me up and shouting and whinging at me

I have had arguments with customers at the time but when things sorted out,by me or another, most will say thank you when you see them at a later date

imho
 
I'm sorry puddle but At risk does not mean cut and cap. A bbf with no vent is AT RISK therefore no cap is necessary as per unsafe sits June/July 09 IIRC.Ie more than 90% ventilation free area provided is ok. Less than 90% is AR and turned off/labelled.

Ps
I'm talking about this issue as a standalone issue. Ie everything else is spot on with flue,spillage,flue flow,no gas leaks,no signs of distress. If any of these issues are apparent along with the No vent then it's an entirely different scenario of course.
 
I'm sorry puddle but At risk does not mean cut and cap. A bbf with no vent is AT RISK therefore no cap is necessary as per unsafe sits June/July 09 IIRC.Ie more than 90% ventilation free area provided is ok. Less than 90% is AR and turned off/labelled.

Ps
I'm talking about this issue as a standalone issue. Ie everything else is spot on with flue,spillage,flue flow,no gas leaks,no signs of distress. If any of these issues are apparent along with the No vent then it's an entirely different scenario of course.

One mans at risk is another mans Imediately dangerous, I use my own judgement , better to err on the side of caution than try and argue in court as to why you didnt take any action, this is why I hate doing landlords certs as if you look hard enough you will always find a problem. I dont have the best people skills, I have 2 settings, chilled out, and ready to punch somone in the face when custards question somthing Iam doing for thier safety.Having said that in 13 yrs Ive only had to shut down 2 apliances
 
I have 2 settings, chilled out, and ready to punch somone in the face when custards question somthing Iam doing for thier safety.Having said that in 13 yrs Ive only had to shut down 2 apliances

Thought you was going to say
In 13 yrs Ive only had to punch 2 custards in the face :D:eek::p
 
Thought you was going to say
In 13 yrs Ive only had to punch 2 custards in the face :D:eek::p

lol:), Ive been very close a few times, Ive had to grow up alot and alter my behavoir (sp) since running my own business, things like not ogleing girls at bus stops, not getting road rage, you never know if they might be your next customer.Iam a business man now in my local comunity and to comand respect youve got to respect others...... everyone has thier breaking point though.
 
theoretical question for you then mbear.
youve seen your back boiler with no vent and decide to turn off and label AR.
As said above you said it could become ID.
your client is cold and decides to turn it on a couple of days later - "just for tonight"
she dies.
i wouldnt be happy with that possibility - even knowing my paperwork is right, and i dont think many of your existing customers would be calling you to service their boilers any time soon.
capping an AR appliance gives me piece of mind, if the client decides to risk reconnecting it themselves then their stupidity is not my problem, you also gain a name for yourself as being over safe. whats the problem with that? if they want somebody just to keep it going, then they know i wont do that and will call someone else - either way im happy
by the way that was theoretical - its never gonna happen to you is it ???!!!
 
theoretical question for you then mbear.
youve seen your back boiler with no vent and decide to turn off and label AR.
As said above you said it could become ID.
your client is cold and decides to turn it on a couple of days later - "just for tonight"
she dies.
i wouldnt be happy with that possibility - even knowing my paperwork is right, and i dont think many of your existing customers would be calling you to service their boilers any time soon.
capping an AR appliance gives me piece of mind, if the client decides to risk reconnecting it themselves then their stupidity is not my problem, you also gain a name for yourself as being over safe. whats the problem with that? if they want somebody just to keep it going, then they know i wont do that and will call someone else - either way im happy
by the way that was theoretical - its never gonna happen to you is it ???!!!

what's the point in having an AR classification then? You may aswell have NCS and ID only the way alot of folk on here say they cap things that are AR only.

If you leave the job IAW the unsafe sits book (paperwork, capped or turned off as appropriate, label appliance) then you have done your job to the letter. There is no case to answer, you have told the cust both verbally and in writing, it is now their responsibility to act appropriately to the advice you've given.

I can kinda understand this if you're self employed to be a bit cap happy. Our gaffer tells us (paraphrasing a bit here) "if you do the job right, leave correct paperwork, cap/turn off appropriately, label and explain the issue to the cust and explain a resolution with costing etc, then you have done your job to a 'T'
and you can sleep easy at night".

Only thing I would say is that if I come accross 2 AR's on the same appliance then I'd be ID-ing it. No doubt about that
 
just a difference in opinion mbear, i would be quite happy with an ncs or id choice in the real world. sometimes its best to ignore your line manager and do what you feel is right. nobody can say your a bad engineer for that.
 
just a difference in opinion mbear, i would be quite happy with an ncs or id choice in the real world. sometimes its best to ignore your line manager and do what you feel is right. nobody can say your a bad engineer for that.

I'D or NCS only would be better for us folk. It'd Save trying to fix 20yr old boilers and force the Custs hand to replace, give us more boiler changes which I prefer doing when the chances arise.

Don't get me wrong though migo, for talking sake roughly 2month ago I went to a back boiler that had no fire on the front(just a bare back boiler) that was still operational to carry out a service. While I did look through the unsafe sits book for this issue or something remotely similar, I couldn't find anything that refered to it. My gaffer said as long as it's not spilling then AR would suffice but he left it to my eng judgement. But I wasn't happy with that myself so It got capped. The vent wasn't correct either but I didn't take this into account when ID-ing it. The bare back boiler was enough for me in this situation. The cust was furious saying it had been like that for yrs (I don't think she'd had it serviced in 10yrs). No chance was it getting left on, no chance!!
 
One mans at risk is another mans Imediately dangerous, I use my own judgement , better to err on the side of caution than try and argue in court as to why you didnt take any action, this is why I hate doing landlords certs as if you look hard enough you will always find a problem. I dont have the best people skills, I have 2 settings, chilled out, and ready to punch somone in the face when custards question somthing Iam doing for thier safety.Having said that in 13 yrs Ive only had to shut down 2 apliances


that statement may be true for some situations, IUP is always going to cause some debate, BUT there are described faults in each group, no vent on BBU is AR, you have no right to cap without permission, and in these days of no win no fee, sue your backside off, it is only a matter of time before someone sues a gas guy for trying to save someone from themselves, if i correctly AR something, then follow the regs I am completely safe and sleep well at night
 
that statement may be true for some situations, IUP is always going to cause some debate, BUT there are described faults in each group, no vent on BBU is AR, you have no right to cap without permission, and in these days of no win no fee, sue your backside off, it is only a matter of time before someone sues a gas guy for trying to save someone from themselves, if i correctly AR something, then follow the regs I am completely safe and sleep well at night

exactly, you can't go to jail for doing it all by the book.

The regs are there to protect the cust but also us engineers.
 
lol:), Ive been very close a few times, Ive had to grow up alot and alter my behavoir (sp) since running my own business, things like not ogleing girls at bus stops, not getting road rage, you never know if they might be your next customer.Iam a business man now in my local comunity and to comand respect youve got to respect others...... everyone has thier breaking point though.

very big of you to stop ogling my daughter now that you are a self employed grown up, i am so happy you only ogled her from the comfort of a sign written van that your employer paid for and hoped that the young lady would contact his firm to get some work done, now he realises why they didnt phone him before

I'D or NCS only would be better for us folk. It'd Save trying to fix 20yr old boilers and force the Custs hand to replace, give us more boiler changes which I prefer doing when the chances arise.

Don't get me wrong though migo, for talking sake roughly 2month ago I went to a back boiler that had no fire on the front(just a bare back boiler) that was still operational to carry out a service. While I did look through the unsafe sits book for this issue or something remotely similar, I couldn't find anything that refered to it. My gaffer said as long as it's not spilling then AR would suffice but he left it to my eng judgement. But I wasn't happy with that myself so It got capped. The vent wasn't correct either but I didn't take this into account when ID-ing it. The bare back boiler was enough for me in this situation. The cust was furious saying it had been like that for yrs (I don't think she'd had it serviced in 10yrs). No chance was it getting left on, no chance!!

this scenario is AR, and only from the point that there is a burn risk from the heat exchanger (assuming, i know we shouldnt, that the gas supply was properly capped) it cant be ID which is causing an immediated danger to life as a gas engineer has to run it like that while doing a service and safety checks on a BBU
 
Last edited by a moderator:
very big of you to stop ogling my daughter now that you are a self employed grown up, i am so happy you only ogled her from the comfort of a sign written van that your employer paid for and hoped that the young lady would contact his firm to get some work done, now he realises why they didnt phone him before
this scenario is AR, and only from the point that there is a burn risk from the heat exchanger (assuming, i know we shouldnt, that the gas supply was properly capped) it cant be ID which is causing an immediated danger to life as a gas engineer has to run it like that while doing a service and safety checks on a BBU

Wtfs got into you tonight Kirkgas:D:p?, I dont know your daughter, Ive never ogled a girl from the comfrot of an employers sign written van, Ive got a big love bus with blacked out windows for that.

that statement may be true for some situations, IUP is always going to cause some debate, BUT there are described faults in each group, no vent on BBU is AR, you have no right to cap without permission, and in these days of no win no fee, sue your backside off, it is only a matter of time before someone sues a gas guy for trying to save someone from themselves, if i correctly AR something, then follow the regs I am completely safe and sleep well at night

Your interpretation of a described fault maybe different to mine or the next mans, Ive only ever had to cap off 2 aplainces before, a boiler with the flue terminating into a sun lounge, and a gas fire that the gas pipe was leaking badly corroded as it was exposed to soot.
 
Last edited by a moderator:
and in these days of no win no fee, sue your backside off, it is only a matter of time before someone sues a gas guy for trying to save someone from themselves

There are to many variables here,no one is going to sue you,a good defense lawyer would have any prosecution running for the door
There is no win ,no fee,but if the lawyer knows he can not win,therefore not get paid (the insurance scam is over),he is not going to waste his time
You are going to have all the industry on your side and probably the judge

Every year the powers that be get stricter and stricter on open flued appliances,encouraging more and more for people to replace


You leave on and something happens,with or without a bit of paper ,you are in trouble because obviously something else was wrong,directly or indirectly,which is quite possible

ID ,AR,in other areas we would probably agree but on a open flued appliance if all the main boxes are not ticked,I ID
and all the main agents and main landlords I work for agree


imho
 
Last edited by a moderator:
There are to many variables here,no one is going to sue you,a good defense lawyer would have any prosecution running for the door
There is no win ,no fee,but if the lawyer knows he can not win,therefore not get paid (the insurance scam is over),he is not going to waste his time
You are going to have all the industry on your side and probably the judge


i'm not sure how many from the industry would stand up in court to back an engineer who admitted breaking the regs by capping an AR without permission, out of court there would be sympathy but could you honestly agree that them breaking the regs that you stick by was the right decision, some might even go down the route of saying it was capped as a way of forcing more work/money, a dangerous place to be, why not turn off the AR and advise as per the law



Wtfs got into you tonight Kirkgas:D:p?, I dont know your daughter, Ive never ogled a girl from the comfrot of an employers sign written van, Ive got a big love bus with blacked out windows for that.

thats all right then
 
Last edited by a moderator:
very big of you to stop ogling my daughter now that you are a self employed grown up, i am so happy you only ogled her from the comfort of a sign written van that your employer paid for and hoped that the young lady would contact his firm to get some work done, now he realises why they didnt phone him before



this scenario is AR, and only from the point that there is a burn risk from the heat exchanger (assuming, i know we shouldnt, that the gas supply was properly capped) it cant be ID which is causing an immediated danger to life as a gas engineer has to run it like that while doing a service and safety checks on a BBU

well what I was put my ID down to was these factors

1. As you say, serious burn risk
2. Air flow is affected because the fire is missing, ie not the way that baxi intended
3. It's a parent and child appliance which share the same flue and as such should always be fitted together
4. Below 90% ventilation

I classified as ID for 1-3, ie if the vent was ok I would still have capped it. The vent being wrong just adds flames to the fire obviously
 
Status
Not open for further replies.

Reply to Open Flue and Ventilation query in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Creating content since 2001. Untold Media.

OFFICIAL SPONSORS

OFFICIAL SPONSORS

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock