Hi all, I'm having problems with my boiler.

It fires up fine, will run for about 30 mins then all gas will cut off causing the burners and pilot to go out. Which I assume is the high temp stat doing its job? What I need to know is why is it over heating?

I have a feeling the themostat isn't working. When you turn the dial, now matter what setting you have it on (1-6) the burners still 'run' the same. I'm assuming when the boiler reaches the temp setting its set at, the thermostat SHOULD turn off the burners and leave the pilot on before the high temp stat has a chance to shut it down? Would this be a faulty potentiometer or could it be the sensor? Or both?

Any help appreciated!
 
It's not just a dodgy pilot or t/cupl is it? 30 mins doesn't seem that long for a cx to get up to max temp...? What model is your boiler? What light is on as fault?
 
Thankyou for replying. the thermocouple has recently been changed and is working fine( if electric is turned off the pilot will stay on) it is definately overheating as the overheat reset has to be pressed to re-light pilot. It may stay on for longer than 30 mins but it all depends on how long its been since it was last on!

Its a concord cx340 and is ancient and has no lights!
 
Maybe time for an upgrade. As gasman says get a GSR engineer in to have a look.
 
Thankyou for replying. the thermocouple has recently been changed and is working fine( if electric is turned off the pilot will stay on) it is definately overheating as the overheat reset has to be pressed to re-light pilot. It may stay on for longer than 30 mins but it all depends on how long its been since it was last on!

Its a concord cx340 and is ancient and has no lights!

Your first thoughts regarding temperature thermostat seems the more likely route to take but as gas man says ... call someone registered out to take a look, it ain't something you want to be messing with IHO
 
Hi, thanks for your help before. I can't afford to upgrade the system as I have been quoted 10k! I have changed the boiler thermostat and the sensor yet the burners will still not turn off. The thermostat 'clicks' as if it is sensing it has hit the set temperature but the burners continue to run until it overheats.

Could it be the gas valve that controls the burners is jammed open? Or maybe a faulty PCB?

Any help appreciated :)
 
You could be on the money once again Robbie .... easiest way to check that out is to cut the power to the boiler (Not Literally) and see if the burner goes out straight away! I've known of gas valves to stick or open/close slowly. By turning off the power to the boiler you'll know whether the cause is electrical or mechanical.
 
If it is the gas valve you will need to get someone qualified to replace it as there are perameters that will need checking/adjusting.
 
Thankyou for the quick reply! When the power to the boiler is turned off the burners go straight out ( this is how we have been turning it on and off without having to relight the pilot). Would this suggest it is the gas valve causing the problem?
 
Less likely to be the gas valve, more likely one of the boards depending on how your boiler is set up. The thermostat should interrupt the power supply to the gas valve when shut off. What your describing seems to indicate that this is not happening. Possibly a fused relay on the board, but that's a guess! You'll need to get someone familiar with your boiler, it's a commercial appliance, to trace the cause.
 
Thankyou once again, ive ordered 2 new boards will see how I get on with those.
 
Well if it ain't any of those then you'll have re-built the bleedn' thing!! LOL Well all except the gas valve!! I'd imagine they aren't cheap parts ...
 
Got the thermostat assy kit for £50 and both circuit boards come to £160 so not to bad...
 
Status
Not open for further replies.

Reply to Problem with Ideal Concord CX in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler pump menu for either 70% or 100%, so, is the pump set at either one of two fixed speed percentages or does the pump actually vary speed, (modulate)...
Replies
1
Views
102
Hi they used to say as a last resort you could discharge the D2 pipework at high level and turn it back to the wall. Similar to a combi boiler. I have just looked back through the regs this seems to have changed and it isn't mentioned now. It now mentions if at high level it should be discharged...
Replies
11
Views
180
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
3
Views
324
I have had a look at previous posts and think I know the answer to this but just before I make it worse could I just check what you think about this one. Granddaughter just moved house and this valve decided to leak when it was closed. When open its fine. Normally I have repacked the gland on...
Replies
6
Views
118
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
276
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock