Plumbing & Plumbers Forum - suitable materials for filling gap around flue
Like Tree12Likes

suitable materials for filling gap around flue

Discuss suitable materials for filling gap around flue in the Gas Safe Register Forum - Public Forum at Plumbers Forums; Doing landlords i frequently come across flues with large gaps around them where they pass through walls that have never been filled in, sometimes theres those rubber collars hidding the ...
  1. #1
    Plumbers Arms member
    ambrosia's Avatar
    Join Date
    Dec 2010
    Posts
    372
    Thanks
    13
    Thanked 14 Times in 14 Posts

    Default suitable materials for filling gap around flue

    Doing landlords i frequently come across flues with large gaps around them where they pass through walls that have never been filled in,
    sometimes theres those rubber collars hidding the hole, but often you can look along the flue to daylight
    (occasionally on bigger holes i see newspaper stuffed in by the tenant to stop draughts)

    I dont why hole are so common, maybe some engineers meant to return to make good others are just plain lazy. needless to say its not really exceptable


    to make good, with a small gap i've seen engineers use silicon to seal the hole and on larger gaps expanding foam

    logically both would work, both can be purchased with heat resistant qualities, both are hard wearing and should last, and both should stop any air flow or transfer of unwanted gases

    however in my gas book it says flues should be sealed with sand and cement, with no mention of any other suitable products.
    Is foam and silicon a no no


  2. #2
    Plumbers Arms member

    Join Date
    Nov 2008
    Posts
    741
    Thanks
    7
    Thanked 54 Times in 53 Posts

    Default

    I work for a HA and I'd say at least 50% flues are not made good it's ridiculous poor workmanship in my opinion. I'd cement them in... However have seen them made good with silicone and other products.


  3. #3
    BOD
    BOD is offline
    Moderator


    BOD's Avatar
    Join Date
    Nov 2009
    Location
    THE BEST COUNTY IN THE LAND - YORKSHIRE
    Posts
    10,544
    Thanks
    461
    Thanked 554 Times in 510 Posts

    Default Re: suitable materials for filling gap around flue

    Don't some books read a suitable material ? Yet another grey area in our trade lets not forget the outer flue if twin lined is only air flow in

  4. #4
    Steady Plumbing Forum Contributor
    Join Date
    Jun 2011
    Posts
    106
    Thanks
    1
    Thanked 5 Times in 5 Posts

    Default Re: suitable materials for filling gap around flue

    when i do istalls i stitch drill quite tight, soim notgoin gooutand buy a bag of sand and cement which ive then ot to carry round with me, when i can just use some heat resistand silicone which ive already goton the van

  5. #5
    Steady Plumbing Forum Contributor
    Join Date
    Jun 2011
    Posts
    106
    Thanks
    1
    Thanked 5 Times in 5 Posts

    Default Re: suitable materials for filling gap around flue

    typing in the dark so there sum mistakes in that last post haha

  6. #6
    UK Plumbersforums Trusted Advisor.

    tamz's Avatar
    Join Date
    Apr 2010
    Location
    Scotland
    Posts
    9,363
    Thanks
    281
    Thanked 1,178 Times in 1,045 Posts

    Default Re: suitable materials for filling gap around flue

    Quote Originally Posted by stokecity View Post
    typing in the dark so there sum mistakes in that last post haha
    Are you under the stairs? Sun still shining here but just going down.

  7. #7
    Plumbers Arms member

    Join Date
    Apr 2010
    Posts
    1,399
    Thanks
    61
    Thanked 167 Times in 157 Posts

    Default Re: suitable materials for filling gap around flue

    Quote Originally Posted by tamz View Post
    Are you under the stairs? Sun still shining here but just going down.
    Or hiding from the wife in the cupboard? Maybe he short of her housekeeping money for the week.

  8. #8
    Banned
    Join Date
    Dec 2009
    Location
    Portsmouth
    Posts
    672
    Thanks
    64
    Thanked 70 Times in 68 Posts

    Default Re: suitable materials for filling gap around flue

    Quote Originally Posted by stokecity View Post
    when i do istalls i stitch drill quite tight, soim notgoin gooutand buy a bag of sand and cement which ive then ot to carry round with me, when i can just use some heat resistand silicone which ive already goton the van
    Who still stitch drills in this day and age?

    The last time that I had to was on an install in Paulsgrove. cast concrete walls as hard as nails, with rebar. Core wouldnt even touch it.

    As to the OP, I have used all methods exp. foam can be wasteful if using tins, as it would have to be a big gap to use a whole tin.

    Sand and cement is my preference.

    But then how do you seal the outside wall on a sixth floor install, when flue has been put in from the inside?
    Last edited by grahamgas; 09-08-2012 at 09:50 PM.

  9. #9
    UK Plumbersforums Trusted Advisor.

    tamz's Avatar
    Join Date
    Apr 2010
    Location
    Scotland
    Posts
    9,363
    Thanks
    281
    Thanked 1,178 Times in 1,045 Posts

    Default Re: suitable materials for filling gap around flue

    I took the baby kango to one on monday. Bloody nofines and i wasn't loosing the tooth off a £100 core bit drilling it.
    grahamgas and AWheating like this.

  10. #10
    UK Plumbersforums Trusted Advisor.

    AWheating's Avatar
    Join Date
    Dec 2010
    Location
    WestMidlands
    Posts
    5,803
    Thanks
    124
    Thanked 572 Times in 546 Posts

    Default Re: suitable materials for filling gap around flue

    Quote Originally Posted by dave1 View Post
    I work for a HA and I'd say at least 50% flues are not made good it's ridiculous poor workmanship in my opinion. I'd cement them in... However have seen them made good with silicone and other products.
    i worked on simular work, in the end i went around and disconnected and labeled them, gave the tenant the comapny phone number and told them to phone and complain that the boiler is dangerous and has been turned off. Once the HA get wind of the compliants they will start to get patched or the work passed to another company......... give them a quote
    Ammonia is found on Pluto, Jupiter and, in small amounts, on Uranus.

    are you Gas Safe? want gas safety or boiler repair advice?we will check out that your genuine via the gas safe website,so please dont be offended when we ask for your details.Diyers,potchers,odd job people and have a go heroes need not apply!

    AW Heating and Plumbing Services. Take the Plunge!

    btw im commercial,
    NOT.


  11. #11
    UK Plumbersforums Trusted Advisor.

    AWheating's Avatar
    Join Date
    Dec 2010
    Location
    WestMidlands
    Posts
    5,803
    Thanks
    124
    Thanked 572 Times in 546 Posts

    Default Re: suitable materials for filling gap around flue

    an unpatched flue (std flue) is AR unless allowed by the manufacture imo. either patch it or turn off and quote for the patching.
    Ammonia is found on Pluto, Jupiter and, in small amounts, on Uranus.

    are you Gas Safe? want gas safety or boiler repair advice?we will check out that your genuine via the gas safe website,so please dont be offended when we ask for your details.Diyers,potchers,odd job people and have a go heroes need not apply!

    AW Heating and Plumbing Services. Take the Plunge!

    btw im commercial,
    NOT.


  12. #12
    Plumbers Arms member
    neily01's Avatar
    Join Date
    Jul 2012
    Location
    norfolk
    Posts
    303
    Thanks
    9
    Thanked 13 Times in 13 Posts

    Default Re: suitable materials for filling gap around flue

    speaking to our local vokera breakdown engineer about this very subject and he use fire cement to seal around flues if not done and the gap is not to big. i thought not a bad idea quick and easy, [messey stuff] but not to sure how it will react with the lack of heat?

  13. #13
    SUPER MODERATOR


    REDSAW's Avatar
    Join Date
    Jan 2009
    Location
    sherrif county
    Posts
    9,101
    Thanks
    241
    Thanked 529 Times in 492 Posts

    Default Re: suitable materials for filling gap around flue

    i use pre mixed tile adhesive if i have some scrags left over from a bathroom job, keep it in a tub and last for ages. takes 2 mins and sticks like ......,sure its heat proof?.
    ¡ƃuıɥʇou ʍouʞ ı˙˙˙ɹǝqɯǝɯǝɹ puɐ
    ˙ʎlddɐ ʇou pǝǝu sǝoɹǝɥ oƃ ɐ ǝʌɐɥ puɐ ǝldoǝd qoɾ ppo `sɹǝ,ʎıp ˙slıɐʇǝp ɹnoʎ ɹoɟ ʞsɐ ǝʍ uǝɥʍ pǝpuǝɟɟo ǝq ʇ,uop ǝsɐǝld os `ǝʇısqǝʍ ǝɟɐs sɐƃ ǝɥʇ ɐıʌ ǝuınuǝƃ ǝɹ,noʎ ʇɐɥʇ ʇno ʞɔǝɥɔ llıʍ ǝʍ ¿ǝɔıʌpɐ ɹıɐdǝɹ ɹǝlıoq ɹo ʎʇǝɟɐs sɐƃ ʇuɐʍ noʎ op
    ¿ʞɹoʍ sɐƃ

    ˙lɐoɔ puɐ pooʍ `sɐƃ `lıo ƃuıpnlɔuı `ʇuɹnq sı lǝnɟ ʎuɐ uǝɥʍ pǝɔnpoɹd ǝq uɐɔ ǝpıxouoɯ uoqɹɐɔ :ʇuɐʇɹodɯı


  14. #14
    UK Plumbersforums Trusted Advisor.

    tamz's Avatar
    Join Date
    Apr 2010
    Location
    Scotland
    Posts
    9,363
    Thanks
    281
    Thanked 1,178 Times in 1,045 Posts

    Default Re: suitable materials for filling gap around flue

    Quote Originally Posted by neily01 View Post
    speaking to our local vokera breakdown engineer about this very subject and he use fire cement to seal around flues if not done and the gap is not to big. i thought not a bad idea quick and easy, [messey stuff] but not to sure how it will react with the lack of heat?
    It still hardens, just takes longer.

  15. #15
    UK Plumbersforums Trusted Advisor.


    Join Date
    Nov 2008
    Location
    east london
    Posts
    6,666
    Thanks
    9
    Thanked 384 Times in 372 Posts

    Default Re: suitable materials for filling gap around flue

    when we was busy we carried a bag of sand and one of cement

Page 1 of 4 1234 LastLast

Similar Threads

  1. VAT on materials.
    By pjfplumbright in forum Plumbing Forum
    Replies: 7
    Last Post: 11-06-2012, 11:33 PM
  2. profit % on materials
    By mark_mc in forum Plumbing Forum
    Replies: 24
    Last Post: 02-05-2011, 10:08 PM
  3. Is my boiler suitable?
    By GuidancePlease in forum Central Heating Forum
    Replies: 22
    Last Post: 16-02-2011, 11:44 PM

Visitors found this page by searching for:

fill gap around boiler flue

expanding foam around flue

filling around boiler flue

fill hole around boiler flue

use of fire rated expandable foam around condensing boiler flue pipe

expanding foam arounf stove flie

expanding foam around boiler flue

Tags for this Thread

Plumbers Forums is a Trading Style of Untold Developments Ltd. Search Engine Optimisation, Web Development and Online Marketing for the UK.