Plumbing & Plumbers Forum - Natural gas pipe sizing over 50 meter?
Like Tree1Likes

Natural gas pipe sizing over 50 meter?

Discuss Natural gas pipe sizing over 50 meter? in the Fittings & Pipes at Plumbers Forums; Originally Posted by akingpage You are right about the purging and commissioning of the pipework but the not being able to i nstall a domestic boiler in a commercial property ...
  1. #16
    UK Plumbersforums Trusted Advisor.

    dancinplumba's Avatar
    Join Date
    Nov 2011
    Location
    Beautiful Barlick
    Posts
    5,360
    Thanks
    291
    Thanked 378 Times in 372 Posts

    Default Re: Natural gas pipe sizing over 50 meter?

    Quote Originally Posted by akingpage View Post
    You are right about the purging and commissioning of the pipework but the not being able to install a domestic boiler in a commercial property I am questioning? The boiler is the only gas appliance and is running 3 domestic hot water points and 8 radiators. I don't think just because it is a commercial building a small installation like this warrants a commercial boiler install? I am going to get a commercial engineer to install the gas line up to the already installed 22mm gas pipe and purge and commission the boiler.
    yes no probs, can you not reposition boiler ?
    imo

  2. Last edited by dancinplumba; 26-02-2012 at 05:44 PM.
    >>>>>>>>>> I'M DANCIN, YOU ASKIN ? <<<<<<<<<<
    IMPORTANT: Carbon Monoxide can be produced when ANY fuel is burnt, including oil, gas, wood and coal.
    GSR? Want gas safety or boiler repair advice? We will check out that you're genuine via the gas safe website, so please dont be offended when we ask for your details. DIYers, odd job people and have a go heroes need not apply

  3. #17
    UK Plumbersforums Trusted Advisor.

    Mike Jackson's Avatar
    Join Date
    Nov 2008
    Location
    Hastings
    Posts
    3,886
    Thanks
    45
    Thanked 392 Times in 364 Posts

    Default Re: Natural gas pipe sizing over 50 meter?

    I'd personally get a commercial guy to run pipework up to the 22, fit a valve and purge to this point. You can then connect up to here and test and purge from this point on as it is then back within scope.
    Gas Safe Registered Engineer for all your Domestic gas, Heating and plumbing needs in Hastings, East Sussex. Check me out on the Gas Safe website, reg. No. 537192.

    GSR? Want gas safety or boiler repair advice? We will check out that you're genuine via the gas safe website, so please dont be offended when we ask for your details. DIYers, odd job people and have a go heroes need not apply.

    By the way I have a Land Rover.

  4. The Following User Says Thank You to Mike Jackson For This Useful Post:

    akingpage (26-02-2012)

  5. #18
    New to Plumbing Forum
    Join Date
    Nov 2011
    Posts
    24
    Thanks
    7
    Thanked 0 Times in 0 Posts

    Default Re: Natural gas pipe sizing over 50 meter?

    Thanks for the advice Mike, sounds like the best option so far. Only problem is the gas board went around on Friday to install the meter and cant find the main! So might be waiting a bit longer, might just see what the cost differences will be between getting a commercial engineer to run the gas or get the gas board to install the meter closer to the boiler?!?

  6. #19
    New to Plumbing Forum
    Join Date
    Nov 2011
    Posts
    24
    Thanks
    7
    Thanked 0 Times in 0 Posts

    Default Re: Natural gas pipe sizing over 50 meter?

    Quote Originally Posted by dancinplumba View Post
    yes no probs, can you not reposition boiler ?
    imo
    I cant reposition the boiler due to flue issues and the customer needs access to the boiler in his office space.

  7. #20
    New to Plumbing Forum
    Join Date
    Nov 2011
    Posts
    24
    Thanks
    7
    Thanked 0 Times in 0 Posts

    Default Re: Natural gas pipe sizing over 50 meter?

    Any commercial gas engineers in or around Coventry who would like to quote for this work please contact me on 07961768920

  8. #21
    New to Plumbing Forum
    Join Date
    Nov 2011
    Posts
    24
    Thanks
    7
    Thanked 0 Times in 0 Posts

    Angry Re: Natural gas pipe sizing over 50 meter?

    I have had a bit of conflicting information on this, so far i have been told by several commercial engineers that seen as though I am able to run 35mm copper on my domestic ticket I can do the pipework myself as they are going to run the 60 meters from the u6 meter in 32 steel in any case?

    I spoke to Gas safe and they have said that I can do the pipework run but the gas volumes would be too big for me to work on with my ticket so I will need a commercial engineer to purge the system, I was reading the trusty "essential gas safety" corgi book and it says that if I isolated the pipework at 0.035m³ intervals then I can purge each section and tightness test each section one by one ensuring I stay inside the domestic volumes for tightness testing?

    How can I run the pipework myself if the maximum length of 35mm pipe I can run is 30 meters (insuring I stay within my 1mb differential pressure drop) my working out is just an example:

    [Power]-[Flow rate ]-[Assumed diameter]-[Measured length]-[Effective length]-[Maximum length]-[Pressure drop]
    [27kw]--[2.52m3/hr]------[35mm]-----------[30 meters]------[30 meters]--------[30 meter]-------[1mb]------

    This working out tells me I cant install anything over 30 meters in length on a u6 meter because my pressure drop would exceed 1mb? (right or wrong?)
    My questions are:
    If I cant run the whole 60 meter in 35mm (due to potentially exceeding my 1mb pressure drop) how can a commercial engineer run the 60 meters in 32mm steel and stay within the 1mb pressure drop on a u6 meter?

    Any help will be appreciated
    Last edited by akingpage; 29-02-2012 at 12:02 AM.

  9. #22
    UK Plumbersforums Trusted Advisor.

    Mike Jackson's Avatar
    Join Date
    Nov 2008
    Location
    Hastings
    Posts
    3,886
    Thanks
    45
    Thanked 392 Times in 364 Posts

    Default Re: Natural gas pipe sizing over 50 meter?

    I think you're getting yourself confused here. 30m of 35mm pipe will pass 8.5 cu m of gas per hour, and 30m of 32mm steel will pass 7.6 cu metres. This is over twice what you require so I would imagine 60m will leave you with a drop within specs.

    Including the meter the maximum length of 35mm pipe that you can test and purge is about 17m including allowances for fittings. Without a meter the length is around 40m so you could in theory install, test and purge in sections. The problem is each section of pipe will require an isolating valve and test point. Also with volumes of .035 cu m a lit purge will be required.
    Gas Safe Registered Engineer for all your Domestic gas, Heating and plumbing needs in Hastings, East Sussex. Check me out on the Gas Safe website, reg. No. 537192.

    GSR? Want gas safety or boiler repair advice? We will check out that you're genuine via the gas safe website, so please dont be offended when we ask for your details. DIYers, odd job people and have a go heroes need not apply.

    By the way I have a Land Rover.

  10. The Following User Says Thank You to Mike Jackson For This Useful Post:

    akingpage (29-02-2012)

  11. #23
    UK Plumbersforums Trusted Advisor.

    tamz's Avatar
    Join Date
    Apr 2010
    Location
    Scotland
    Posts
    9,308
    Thanks
    281
    Thanked 1,175 Times in 1,042 Posts

    Default Re: Natural gas pipe sizing over 50 meter?

    35mm copper or 32mm steel will take 4.5m³ with a 1mb drop over 100m
    Your 10m run of 22mm is too much. you have used up your 1mb drop on that.
    32mm (1 1/4") steel is around £35 /6.5m length. Much cheaper (and better) than copper.

    You can do it on a domestic ticket if you do it in sections. Test and purge as you go.

    Run around 20m of 1 1/4" from the meter and valve it. (volume of 20m 1 1/4" pipe and meter inc allowance for fittings = 0.0325m³). Test and purge the section.
    Run another 4 length of 1 1/4" (26m, volume 0.0318m³) and valve it again with a tee and test nipple in the section. Test and purge the section.
    Run the 1 1/4" up to near the boiler then reduce to 22mm for the last couple of metres. Put a test point in the pipe work here too.

    50m of 1 1/4" steel or 35mm copper will give a drop of around half a mb.

  12. The Following User Says Thank You to tamz For This Useful Post:

    akingpage (01-03-2012)

  13. #24
    New to Plumbing Forum
    Join Date
    Nov 2011
    Posts
    24
    Thanks
    7
    Thanked 0 Times in 0 Posts

    Default Re: Natural gas pipe sizing over 50 meter?

    Tamz, just what I was looking for, thanks for your help.

Page 2 of 2 FirstFirst 12

Similar Threads

  1. Gas Pipe Sizing
    By bob the plumber in forum Gas Safe Register Forum - Public Forum
    Replies: 21
    Last Post: 22-05-2011, 10:41 PM
  2. Pipe Sizing
    By ChrisPaws in forum Central Heating Forum
    Replies: 3
    Last Post: 23-12-2010, 12:31 PM
  3. pipe sizing
    By michael11 in forum Central Heating Forum
    Replies: 4
    Last Post: 06-06-2010, 02:47 PM
  4. pipe sizing help please
    By geezah in forum Central Heating Forum
    Replies: 8
    Last Post: 01-02-2010, 08:37 PM
  5. Pipe Sizing
    By Max-1stSaxon in forum Plumbing Forum
    Replies: 2
    Last Post: 18-08-2008, 12:54 AM

Visitors found this page by searching for:

commercial gas pipe sizing chart

commercial gas pipe sizing

natural gas pipe sizing chart uk

commercial gas pipe sizing calculator

commercial gas pipe sizing uk

commercial gas pipework sizing chartcommercial gas pipe sizing table

Tags for this Thread

Plumbers Forums is a Trading Style of Untold Developments Ltd. Search Engine Optimisation, Web Development and Online Marketing for the UK.