Old 4 Weeks Ago   #1 (permalink)
Monkfish
Junior Member
Info
 

Join Date: Jan 2010
Posts: 8

Default Corroded Pipe?

Hi, I had a new boiler installed about 5 months ago. The plumbers ran a new 22mm copper pipe from the gas supply alongside the existing 22mm copper pipe for the flow and return (30 years old).

Since the installation I have been losing around 1/10 bar pressure per week (sealed system) and have been topping up the pressure thinking that the system was just taking its time to stabilize. I was slightly worried it might be a small leak, but as I could find no signs I ignored the pressure drop.

This week I noticed the telltale sign of water dripping from a light socket. Investigating, I found a floor beam that was soaked just where the three pipes mentioned above passed through it (inconveniently right under a partitioning wall).

Further along the pipe I noticed a small bead of flux had been left bridging the return pipe and the new gas pipe. Cleaning off this flux I noticed a small pin hole in the return pipe (which later investigation revealed was about to breach the pipe). Thankfully, there was no such hole in the gas pipe (which seems strange as both are copper). Cutting out the pipe from under the wall revealed similar flux residue and many more holes (as shown in the image). This was the source of the leak.



Now I could have imagined that the return pipe which is over 30 years old had slowly corroded under the wall and the new pressurised system finally forced the water through, but the hole further up was clearly caused by a bead of flux left during the upgrade 5 months ago.

Is it normal for a small bead of flux to eat its way through a copper pipe in this period of time or could there be some additional electrolysis action between the gas pipe and the water pipe (both are earth at the boiler)?
Monkfish is offline  
Reply With Quote
Old 4 Weeks Ago   #2 (permalink)
WHPES
Senior Member
Info
 

Join Date: Jan 2008
Posts: 796

Default Re: Corroded Pipe?

I doubt it is all down to flux. If it is about 30 years old there was a copper shortage and inferior imported copper tube was used. This had inclusions of carbon and slag which causes cold water pitting (and hot water pitting) of the copper to form the telltale pinholes.

See

Wapedia - Wiki: Cold water pitting of copper tube

The chances are the rest of your water pipe is in a similar condition.

Last edited by WHPES; 4 Weeks Ago at 07:07 PM.
WHPES is offline  
Reply With Quote
Old 4 Weeks Ago   #3 (permalink)
wards
Member
Info
 

Join Date: Feb 2010
Location: pelsall
Posts: 76

Default Re: Corroded Pipe?

have to agree with monkfish,once you have had the old pipework replaced remember to treat the water with fresh inhibitor HTH
si

Re: Corroded Pipe?
have to agree with monkfish,once you have had the old pipework replaced remember to treat the water with fresh inhibitor HTH
si
grrr i meant whpes

Last edited by wards; 4 Weeks Ago at 07:22 PM. Reason: Automerged Doublepost
wards is offline  
Reply With Quote
Old 4 Weeks Ago   #4 (permalink)
WHPES
Senior Member
Info
 

Join Date: Jan 2008
Posts: 796

Default Re: Corroded Pipe?

A few areas I cover in the North York Moors have problems with pitting of copper pipe. This usually manifests in the pipe nearest to the supply, particularly on horizontal runs. Copper cylinders become eaten through and immersion elements soon rot. The only satisfactory remedy is to repipe in plastic and fit stainless cylinders and incolloy heating elements.

I have had water samples sent for anyalysis and we have found presence of ammonium salts and carbonic acid (as in fizzy drinks). Pitting is likely initiated through stagnation as described in my last link.
WHPES is offline  
Reply With Quote
Old 4 Weeks Ago   #5 (permalink)
oldplumber
Senior Member
Info
 

Join Date: Jul 2009
Location: North Devon
Posts: 377

Default Re: Corroded Pipe?

you mention sealed system, if vented previously the extra pressure starts to accelerate losses not previously noticed in the old pipework. Everything rots eventually as your system is now showing, and I have noticed certain area around me have acidic water which just eats immersion heaters (6 - 12 months and they are dust)
oldplumber is online now  
Reply With Quote
Old 4 Weeks Ago   #6 (permalink)
Monkfish
Junior Member
Info
 

Join Date: Jan 2010
Posts: 8

Default Re: Corroded Pipe?

The rest of the pipe looks okay on the outside and so does the inside of all the pipe I've removed. God I hope this isn't going to happen elsewhere as most of the piping is sealed under concrete flooring and behind tiled walls.

So you think the pressure is accelerating internal corrosion that has been developing over the years in the old pipe. I guess that bead of flux could just have been corrosion blown from the tiny hole.

Maybe it will just be that short run of piping. They used to be the heat-exchanger pipes linking the immersion tank to the boiler, but we never used them, so they had stagnant water sitting in them for at least 20 years. Now they are being used as the flow & return of the new boiler.

I use Sentinel X100 + X200. The X200 won't make things worse will it?

Last edited by Monkfish; 4 Weeks Ago at 11:50 PM.
Monkfish is offline  
Reply With Quote
Old 4 Weeks Ago   #7 (permalink)
Blackcatgas
Senior Member
Info
 

Join Date: Oct 2009
Location: Nottingham
Posts: 271

Default Re: Corroded Pipe?

Quote:
Originally Posted by Monkfish View Post
The rest of the pipe looks okay on the outside and so does the inside of all the pipe I've removed. God I hope this isn't going to happen elsewhere as most of the piping is sealed under concrete flooring and behind tiled walls.

So you think the pressure is accelerating internal corrosion that has been developing over the years in the old pipe. I guess that bead of flux could just have been corrosion blown from the tiny hole.

Maybe it will just be that short run of piping. They used to be the heat-exchanger pipes linking the immersion tank to the boiler, but we never used them, so they had stagnant water sitting in them for at least 20 years. Now they are being used as the flow & return of the new boiler.

I use Sentinel X100 + X200. The X200 won't make things worse will it?
Also dont forget that self cleaning flux (Laco) etc is more active when its heated which is why the heating pipe could be more afected than the gas pipe at room temperature.
If Iam doing all new copper piping with no new to old connections I like to use a less agressive flux like fluxite, I still use laco though and try to wipe off any excess.
Blackcatgas is offline  
Reply With Quote
Old 4 Weeks Ago   #8 (permalink)
WHPES
Senior Member
Info
 

Join Date: Jan 2008
Posts: 796

Default Re: Corroded Pipe?

You may find it's just a certain section which dates from a certain job.

Does any of your other pipework have any of the telltale green patches on the outside?
WHPES is offline  
Reply With Quote
Reply
  

Bookmarks

Tags
None



Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Outside Tap come apart from pipe zee Plumbing Forum 4 30-01-2010 06:07 PM
Combined F&E pipe problems WHPES Central Heating Forum 5 06-01-2010 03:29 PM
Shower Pump & Pipe Diameter Question spcdust Showers and Wetrooms 4 27-08-2009 01:13 PM
Pipe CHASING electric shower bureaucrazy Showers and Wetrooms 10 08-04-2009 10:06 PM
Relocating Soil Pipe Venting DazJWood Plumbing Forum 11 26-02-2009 09:20 PM


All times are GMT +1. The time now is 11:58 PM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.
Content Relevant URLs by vBSEO 3.0.0

u.m Network: Contractor Forum | Tilers Forum | Electrical Forum | Flooring Forum | Plastering Forum |
(c) 2007 Plumbing Advice Forum - UK Plumbers Forums

<Search Engine Optimisation Help

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89