Old 20-12-2009   #1 (permalink)
bonesy60
Junior Member
Info
 

Join Date: Nov 2009
Posts: 21

Default Valliant VCW GB242EH no heating

Went to one of these today hot water works fine but no heating boiler lights runs about 10 to 20 secs then cuts out. The hot water circuit is very hot the pump, and plate exchanger and the Dhw diverter on the front are all hot. But the flow stays completely cold
bonesy60 is offline  
Reply With Quote
Old 20-12-2009   #2 (permalink)
so-solar
Senior Member
Info
 

Join Date: May 2009
Location: northampton
Posts: 158

Default Re: Valliant VCW GB242EH no heating

could well be the diverter valve mate!
so-solar is offline  
Reply With Quote
Old 20-12-2009   #3 (permalink)
bonesy60
Junior Member
Info
 

Join Date: Nov 2009
Posts: 21

Default Re: Valliant VCW GB242EH no heating

Are they separate on these boilers
bonesy60 is offline  
Reply With Quote
Old 20-12-2009   #4 (permalink)
puddle
Senior Member
Info
 

Join Date: May 2009
Location: London/Lincolnshire
Posts: 1,467

Default Re: Valliant VCW GB242EH no heating

is this the old 242e from the early ninties with door opening sideways at bottom and gray metal panel covering control box held in with two side screws ?
puddle is offline  
Reply With Quote
Old 20-12-2009   #5 (permalink)
bonesy60
Junior Member
Info
 

Join Date: Nov 2009
Posts: 21

Default Re: Valliant VCW GB242EH no heating

Yea that's the one the main diverter is under the pump but the dhw one is at the front I think.
bonesy60 is offline  
Reply With Quote
Old 20-12-2009   #6 (permalink)
puddle
Senior Member
Info
 

Join Date: May 2009
Location: London/Lincolnshire
Posts: 1,467

Default Re: Valliant VCW GB242EH no heating

could be divertor stuck but think the problem is the black plunger above the water section at the front of the boiler ,a common fault is it sticks in the up postion on hot water micro switches
If you open boiler look above dhw diaghram section you will see the black arm in question when tap opens it lifts and moves servo unit as required,when tap closed it should return to required position for heating
with taps off push down arm and heating should start working,if so remove arm and clean and greese pin sleeve underneath

Last edited by puddle; 20-12-2009 at 11:57 PM.
puddle is offline  
Reply With Quote
Old 21-12-2009   #7 (permalink)
bonesy60
Junior Member
Info
 

Join Date: Nov 2009
Posts: 21

Default Re: Valliant VCW GB242EH no heating

Would this case the water not to flow through the central heating circuit cheers Ian.
bonesy60 is offline  
Reply With Quote
Old 21-12-2009   #8 (permalink)
puddle
Senior Member
Info
 

Join Date: May 2009
Location: London/Lincolnshire
Posts: 1,467

Default Re: Valliant VCW GB242EH no heating

Quote:
Originally Posted by bonesy60 View Post
Would this case the water not to flow through the central heating circuit cheers Ian.
If black arm not seated back down correctly divertor valve will not be able to move to heating position
you will see a small servo valve behind black arm with small tubes going to it,as it moves pump flows water through the small tubes altering divertor valve position
puddle is offline  
Reply With Quote
Old 21-12-2009   #9 (permalink)
bonesy60
Junior Member
Info
 

Join Date: Nov 2009
Posts: 21

Default Re: Valliant VCW GB242EH no heating

Ok will give this a go tomorrow many thanks Ian.
bonesy60 is offline  
Reply With Quote
Old 22-12-2009   #10 (permalink)
bonesy60
Junior Member
Info
 

Join Date: Nov 2009
Posts: 21

Default Re: Valliant VCW GB242EH no heating

Went back to this boiler last night Dhw diverter arm was stuck in the up position pushed it down turned the boiler on and the heating worked. Stripped it out cleaned and greased put back together and the arm was returning but would not pull the main diverter down on the the micro switches. I had all the control tubes of and cleaned them out could not get the diverter apart cause the pins had seized so I think I will just put a new one in thanks for all the help Ian.
bonesy60 is offline  
Reply With Quote
Reply
  

Bookmarks

Tags
None



Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Worcester boiler heating water and CH whiskeyfrank Central Heating Forum 2 06-02-2010 12:27 AM
Heating Programmer Question southside Central Heating Forum 5 03-11-2009 03:29 PM
underfloor heating Danny boy Plumbing Forum 2 15-12-2008 08:50 AM
Landlord reduced heating to 4 hours cyberbird Central Heating Forum 2 14-10-2008 10:05 PM
Best practice for heating mrsimes Central Heating Forum 1 25-09-2008 09:05 AM


All times are GMT +1. The time now is 04:48 AM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.
Content Relevant URLs by vBSEO 3.0.0

u.m Network: Contractor Forum | Tilers Forum | Electrical Forum | Flooring Forum | Plastering Forum |
(c) 2007 Plumbing Advice Forum - UK Plumbers Forums

<Search Engine Optimisation Help

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89