Microbore balancing
Discuss Microbore balancing in the Central Heating Forum at Plumbers Forums; Hi all, I live in a 3 bedroom semi detatched new build house with a sealed system, condensing boiler ( ideal icos he15) and 10mm microbore plastic heating pipe system. ...-
01-09-2012 #1New to Plumbing Forum
- Join Date
- Dec 2011
- Posts
- 14
- Thanks
- 5
- Thanked 0 Times in 0 Posts
Microbore balancing
Hi all,
I live in a 3 bedroom semi detatched new build house with a sealed system, condensing boiler ( ideal icos he15) and 10mm microbore plastic heating pipe system.
I was wondering wether or not this requires balancing as our friends who live in a house identical to ours their heating system has every single radiator lockshield valve fully open on all Rads.
Our heating system has the pump on speed 3 (myson CP53) Auto bypass valve on 1.5 (honeywell DU145) and the rads are fully open downstairs and about half open upstairs. However after many hours of reading info on the net i wonder wether the system is set up correctly as i know only to well what new builds by persimmon are like and the fact that our friends house is completely different set up to ours. I wonder wether our pump speed is too high and if our rads need to be finely balanced as i have heard that microbore is nearly self balancing or wether i should open the lock shields fully like our friends. I also wonder about the auto bypass valve is it too lower a setting??? Any help is very much appreciated, Many thanks Will
-
01-09-2012 #2Moderator



- Join Date
- Jul 2010
- Location
- Portadown, United Kingdom
- Posts
- 7,665
- Thanks
- 446
- Thanked 533 Times in 494 Posts
Re: Microbore balancing
Do all your rads heat up at roughly the same time? You don't actually say whether you've a problem or not.
Propino Tibi Salutem! Usque ad Mortem Bibendum!
Croppie
(By the way, I'm commercial!)
IMPORTANT: Carbon Monoxide can be produced when ANY fuel is burnt, including oil, gas, wood and coal.
GSR? Want gas safety or boiler repair advice? We will check out that you're genuine via the gas safe website, so please don't be offended when we ask for your details. DIYers, odd job people and have a go heroes need not apply.
-
01-09-2012 #3Plumbers Arms member

- Join Date
- Jan 2012
- Location
- Essex
- Posts
- 3,201
- Thanks
- 80
- Thanked 243 Times in 239 Posts
In other words, if it ain't broke don't fix it!
Proud to be 'Part P', the world is now my mollusc!
-
01-09-2012 #4New to Plumbing Forum
- Join Date
- Dec 2011
- Posts
- 14
- Thanks
- 5
- Thanked 0 Times in 0 Posts
Re: Microbore balancing
Hi sorry I didn't actually put why I was asking I just wanted to ensure that my system was correctly setup and running as efficiently as it should be after my experience with "persimmon cowboys"!! I thought I would just ask the professionals opinion on how it should be setup.
-
01-09-2012 #5Plumbers Arms member

- Join Date
- Jan 2012
- Location
- Essex
- Posts
- 3,201
- Thanks
- 80
- Thanked 243 Times in 239 Posts
In reality, if you are happy with the performance then leave well alone.
Proud to be 'Part P', the world is now my mollusc!
-
01-09-2012 #6UK Plumbersforums Trusted Advisor.


- Join Date
- Dec 2010
- Location
- Bridgend, Wales
- Posts
- 3,609
- Thanks
- 69
- Thanked 358 Times in 348 Posts
"nothing is impossible"
GSR? Want gas safety or boiler repair advice? We will check out that you're genuine via the gas safe website, so please dont be offended when we ask for your details. DIYers, odd job people and have a go heroes need not apply.
-
01-09-2012 #7UK Plumbersforums Trusted Advisor.


- Join Date
- Apr 2010
- Location
- Scotland
- Posts
- 9,384
- Thanks
- 281
- Thanked 1,180 Times in 1,047 Posts
Re: Microbore balancing
Rather than worrying about the set up you should worry about the lifespan of your boiler. Best start sticking some money in a jam jar for when the time comes.
-
01-09-2012 #8New to Plumbing Forum
- Join Date
- Dec 2011
- Posts
- 14
- Thanks
- 5
- Thanked 0 Times in 0 Posts
Re: Microbore balancing
Ha yes I have read many a negative comment about the ideal boilers lol! It can only be a matter of time I guess?!?!! Ok if you guys think it's all sounds ok and like you say if it works leave it that sounds good to me!! I appreciate your help guys!
-
01-09-2012 #9UK Plumbersforums Trusted Advisor.


- Join Date
- Apr 2010
- Location
- Scotland
- Posts
- 9,384
- Thanks
- 281
- Thanked 1,180 Times in 1,047 Posts
Re: Microbore balancing
Maybe your bypass needs setting a bit better. 1 1/2 is too low for the pump setting you have.
This will tell you how to set it if you have a spare half hour
http://www.honeywelluk.com/Documents...ll/pdf/951.pdf
Otherwise don't worry about things
-
The Following User Says Thank You to tamz For This Useful Post:
bilco_21 (02-09-2012)
-
02-09-2012 #10New to Plumbing Forum
- Join Date
- Dec 2011
- Posts
- 14
- Thanks
- 5
- Thanked 0 Times in 0 Posts
Re: Microbore balancing
Cheers tamz thanks for the info on setting the bypass. I've hunted through my boiler installation instructions and also all the available literature on the ideal website but can't seem to find the minimum flow rate through the boiler, would anyone have any idea what it would be for an Ideal icos HE15?
-
02-09-2012 #11Top Plumbing Forum Contributor
- Join Date
- Aug 2012
- Location
- Central Scotland
- Posts
- 440
- Thanks
- 17
- Thanked 40 Times in 40 Posts
Re: Microbore balancing
That is to true to be good. 10mm plastic has roughly 6mm internal bore which is insufficient for most radiator sizes anyway. Then stick an insert at some manufacturer that is 4mm internal only. Feeding for example a 1200x600 K2.
This is a bit like shoving a full pig in your fridge. If you just heat it enough it will fit.
Wonder how some expect to run the boiler in condensing range without running enough water through the boiler. Pump has to run like mad to make good for that. But at least one wins, your energy supplier.
I would very much say if the system works be happy. Throttling the flow even more will definitely not make your boiler more efficient.
The self balancing story comes from the fact that the volume of water can not move because of the high internal resistance which leads to a pressure build up. This high resistance in the pipe work in conjunction with the raised pressure means that the differences in internal resistance of the radiators have barely any influence on the flow anymore.Last edited by DirksPlumbing; 02-09-2012 at 01:32 PM.
-
The Following User Says Thank You to DirksPlumbing For This Useful Post:
bilco_21 (02-09-2012)
-
02-09-2012 #12Top Plumbing Forum Contributor
- Join Date
- Aug 2012
- Location
- Central Scotland
- Posts
- 440
- Thanks
- 17
- Thanked 40 Times in 40 Posts
Re: Microbore balancing
Last edited by DirksPlumbing; 02-09-2012 at 01:48 PM. Reason: corrected
-
02-09-2012 #13New to Plumbing Forum
- Join Date
- Dec 2011
- Posts
- 14
- Thanks
- 5
- Thanked 0 Times in 0 Posts
Re: Microbore balancing
Hi dirksplumbing thanks for your help mate. I understand where your coming from as in balancing that you don't wanna be restricting the flow even more due to the small ID of the pipe. With regards to your second post I was looking for the minimum flow rate required by the boiler itself as needed on the Honeywell instructions of the auto bypass to set it correctly. I can find the myson pump curves that I need but I just can't find the boiler min flow rate in any instructions or anywhere!! Cheers mate
-
02-09-2012 #14Super Plumbing Forum Contributor
- Join Date
- Aug 2009
- Posts
- 1,109
- Thanks
- 2
- Thanked 108 Times in 104 Posts
Re: Microbore balancing
It's there - but not easy to find!
Page 10 of the Installation Manual says (Frame 3):
A suitable pump is a domestic circulator capable of providing a maximum 11oC (20°F) temperature differential across the boiler with the whole of the heating circuit open (e.g. Grundfos UPS 15/50, 15/60 or equivalent). With the minimum flow circuit allowed by the controls the differential must not exceed 25°C. (18°C for the HE15)
So at minimum output (8.8kW) the max differential for an HE15 is 18°C. The flow rate will therefore be 8.8/(4.18 x 18) = 0.12 litres/sec = 7.02 l/min = 421 l/hr = 0.42m³/hr.
As for the correct setting of the DU145, 1.5 is much too low; it should be 4 or even higher. Feel the pipe leaving the DU145 (arrow shows flow) about a foot away from valve. Most of the time it should be cold as the valve is closed and only opens when rads close down. If it is hot all the time, the valve needs to be on a higher setting.
-
The Following User Says Thank You to doitmyself For This Useful Post:
bilco_21 (02-09-2012)
-
02-09-2012 #15UK Plumbersforums Trusted Advisor.


- Join Date
- Dec 2010
- Location
- WestMidlands
- Posts
- 5,824
- Thanks
- 124
- Thanked 572 Times in 546 Posts
Re: Microbore balancing
i suppose it could be good news that whoever commissioned your heating actually balanced it and its morely like it was commissioned and flushed correcty compared to one that has not been balanced?? who knows..........
Ammonia is found on Pluto, Jupiter and, in small amounts, on Uranus.
are you Gas Safe? want gas safety or boiler repair advice?we will check out that your genuine via the gas safe website,so please dont be offended when we ask for your details.Diyers,potchers,odd job people and have a go heroes need not apply!
AW Heating and Plumbing Services. Take the Plunge!
btw im commercial, NOT.
Similar Threads
-
More than one rad off microbore??
By stratplus in forum Central Heating ForumReplies: 8Last Post: 09-08-2012, 10:30 PM -
Microbore...yay or nay?
By mrlennie in forum Central Heating ForumReplies: 37Last Post: 28-02-2011, 06:42 PM -
Microbore.
By Canberra Man in forum Central Heating ForumReplies: 3Last Post: 07-01-2011, 08:28 AM -
microbore
By daz1968 in forum Central Heating ForumReplies: 2Last Post: 20-01-2010, 10:15 PM -
microbore
By gates1979 in forum Fittings & PipesReplies: 3Last Post: 19-01-2010, 11:09 PM



14Likes
Reply With Quote










Virgin plumber in need of help
20 Minutes Ago in Bathrooms, Showers and Wetrooms