Plumbing & Plumbers Forum - Pressure relief drain problem

Pressure relief drain problem

Discuss Pressure relief drain problem in the Central Heating Forum at Plumbers Forums; Hi, I've got a combi boiler with sealed heating circuit which has just been temporarily condemned following a boiler service, because the previous owner of the property (or whoever built ...
  1. #1
    New to Plumbing Forum
    Join Date
    Aug 2012
    Posts
    6
    Thanks
    2
    Thanked 0 Times in 0 Posts

    Default Pressure relief drain problem

    Hi,

    I've got a combi boiler with sealed heating circuit which has just been temporarily condemned following a boiler service, because the previous owner of the property (or whoever built the extension on the house for him) has done a bit of DIY plumbing.

    The original pressure relief pipe would have exited the bathroom below the roofline of the new extension, about 4" below the bottom of the boiler. So they've used plastic right-angle connectors, and fashioned a "U" with the pipe going back up, and out through the wall about 6" above the bottom of the boiler. And the pipe that goes outside then isn't bent back in on itself so it's facing the wall. So as I understand it, it's an epic fail when it comes to building regs.

    It looks like I've got 3 options as I understand it:

    1. run a pretty fat pipe about 6 meters sideways through my bedroom (which will look awful)
    2. raise the existing boiler (Ideal Mini) by about a foot (preferred if it's cheap)
    3. get a new boiler installed (are Combi's really worth it...?)

    Anybody have any thoughts on this, including how much (ballpark) it's likely to cost? Furthermore, anyone have any thoughts about whether I'd have a claim against the previous owner or the local council (who signed off the building inspection for the extension)?

    All comments appreciated!

    Thanks,

    Stu


  2. #2
    Banned
    Join Date
    Dec 2009
    Location
    Portsmouth
    Posts
    672
    Thanks
    64
    Thanked 70 Times in 68 Posts

    Default Re: Pressure relief drain problem

    Any chance of a few pics?


  3. #3
    Plumbers Arms member Centralheatking's Avatar
    Join Date
    Jul 2010
    Location
    West Lancashire
    Posts
    738
    Thanks
    132
    Thanked 70 Times in 65 Posts

    Default Re: Pressure relief drain problem

    Yup, do some pics and we will sort you out

    centralheatking

  4. #4
    New to Plumbing Forum
    Join Date
    Aug 2012
    Posts
    6
    Thanks
    2
    Thanked 0 Times in 0 Posts

    Default Re: Pressure relief drain problem

    Cheers guys, I'll take some and get them uploaded this evening.

  5. #5
    UK Plumbersforums Trusted Advisor.

    AWheating's Avatar
    Join Date
    Dec 2010
    Location
    WestMidlands
    Posts
    5,803
    Thanks
    124
    Thanked 572 Times in 546 Posts

    Default Re: Pressure relief drain problem

    you could possible blank the boilers pressure relief pipe or pipe it back into the system and then fit another pressure relief valve on another part of the system where its easy to get it to a safe position outside. possible off radiator pipework on an external wall. This would be alot less work and cheaper than lifting the boiler.

    i would suggest phoning the manufacture and asking if they allow it to be done and how the require you to deal with the boilers prv. Ask your gas safe engineer to ask them.

    welcome to the forum.
    Ammonia is found on Pluto, Jupiter and, in small amounts, on Uranus.

    are you Gas Safe? want gas safety or boiler repair advice?we will check out that your genuine via the gas safe website,so please dont be offended when we ask for your details.Diyers,potchers,odd job people and have a go heroes need not apply!

    AW Heating and Plumbing Services. Take the Plunge!

    btw im commercial,
    NOT.


  6. #6
    New to Plumbing Forum
    Join Date
    Aug 2012
    Posts
    6
    Thanks
    2
    Thanked 0 Times in 0 Posts

    Default Re: Pressure relief drain problem

    OK, they're not great photos, but let me know if you need any more specifics:

    1. Bottom of boiler - copper pipe with plastic bends on the right is the pressure relief pipe. You can see where the pipe used to exit - that's now into a roof cavity. The existing pipe could probably exit an inch lower at most, given where the roof of the extension comes to.
    IMAG0351.jpg

    2. Top of boiler - more than enough room to move it up a foot if needed...? It's in an enclosed full-height cupboard in the bathroom.
    IMAG0352.jpg

  7. #7
    Plumbers Arms member
    Nostrum's Avatar
    Join Date
    Feb 2012
    Posts
    1,265
    Thanks
    39
    Thanked 99 Times in 94 Posts

    Default Re: Pressure relief drain problem

    As AWheating said, providing the manufacturer allows, you could tee off the return pipework under the boiler and take a length of pipe up the side of the boiler. Fit the PRV at the top and exit out beside flue (assuming the flue terminate outside!)

    Normally you fit a 2.5bar PRV to replace the 3 bar on the boiler. Some manufacturers sell this as an option, Baxi's part number is 5121379. I don't recall Ideal doing it though although there is no reason why as the principle is exactly the same. Might want to put an airvent on as well.
    Last edited by Nostrum; 18-08-2012 at 07:26 PM.

  8. The Following User Says Thank You to Nostrum For This Useful Post:

    bigstu82 (18-08-2012)

  9. #8
    Plumbing Forum Contributor
    Join Date
    Mar 2011
    Location
    Roscommon(Eire)
    Posts
    80
    Thanks
    0
    Thanked 8 Times in 8 Posts

    Default Re: Pressure relief drain problem

    I doubt a manufacture will put anything on paper as they would be responsible if it ever went pear shaped(slim chance I know) and they don't like moving a way from MI.

    If you cap the blow off and fit another one elsewhere you will have to remove the isolation valve(s) from the boiler to stop the boiler from being isolated from the blow off, if you repipe the blow off into the system you risk being reported again by someone who doesn't understand basic plumbing and these things can turn in to a ****ing competion .

  10. #9
    New to Plumbing Forum
    Join Date
    Aug 2012
    Posts
    6
    Thanks
    2
    Thanked 0 Times in 0 Posts

    Default Re: Pressure relief drain problem

    Quote Originally Posted by sambotc View Post
    As AWheating said, providing the manufacturer allows, you could tee off the return pipework under the boiler and take a length of pipe up the side of the boiler. Fit the PRV at the top and exit out beside flue (assuming the flue terminate outside!)

    Normally you fit a 2.5bar PRV to replace the 3 bar on the boiler. Some manufacturers sell this as an option, Baxi's part number is 5121379. I don't recall Ideal doing it though although there is no reason why as the principle is exactly the same. Might want to put an airvent on as well.
    OK, so just to clarify, the manual for the boiler's here (can't do a proper link as I'm a newbie):

    http www idealheating com/downloads/manuals/mini_is32.pdf

    On Page 11 is the systematic diagram of the boiler - item 10 is the PRV? So I'm guessing that the "output" side of this valve has been soldered onto the original pipe that drops out of the boiler? And what you're suggesting is to get someone to (with Ideal's blessing) take the valve off, and, say, run a pipe from where the valve was down, across, and up the side of the boiler, then add a new PRV onto the end of that, and take the "output" side of that valve out of the house in accordance with building regs - so the pipe which has a "U" in it is then constantly full of hot water (i.e. is part of the sealed system, isn't open to the environment), can't freeze or breed legionella, and will only vent externally if - God forbid - the pressure goes over 2.5 bar?

    What's the deal with the air vent? Just replace a standard brick with an air brick from outside into the cupboard, or something more? I think (presume) it's got one of those "co-axial" flues on it, and the CO figures on the annual test were well in the safe range - is it needed, or is a co-axial flue sufficient?

    Thanks

  11. #10
    New to Plumbing Forum
    Join Date
    Aug 2012
    Posts
    6
    Thanks
    2
    Thanked 0 Times in 0 Posts

    Default Re: Pressure relief drain problem

    Quote Originally Posted by Gary71 View Post
    I doubt a manufacture will put anything on paper as they would be responsible if it ever went pear shaped(slim chance I know) and they don't like moving a way from MI.

    If you cap the blow off and fit another one elsewhere you will have to remove the isolation valve(s) from the boiler to stop the boiler from being isolated from the blow off, if you repipe the blow off into the system you risk being reported again by someone who doesn't understand basic plumbing and these things can turn in to a ****ing competion .
    Fair enough on point one.

    As for point two, I'd have to make sure it was me at home when it gets serviced in future, not my missus who prefers fluffy kittens to pipes and wires...

  12. #11
    Plumbers Arms member
    Nostrum's Avatar
    Join Date
    Feb 2012
    Posts
    1,265
    Thanks
    39
    Thanked 99 Times in 94 Posts

    Default Re: Pressure relief drain problem

    Hi bigstu82

    Heres a picture

    remote prv.jpg

    The new PRV is exiting out the wall by the flue (assuming it is terminated outside after the extension!)

    The existing PRV stays in, hence the new PRV having a lower rating (2.5 bar)

    Air vent to release air in the vertical pipework, not knock a hole in your wall!

    You should ask ideal first but this is a recognised method, baxi call it a secondary remote pressure relief safety valve or similar. Pretty sure vaillant offer it as well, and all the boilers works on the same principle in this instance so theoretically the boiler make/model is irrelevant. That said you should always go by manufacturers instruction......
    Last edited by Nostrum; 18-08-2012 at 08:55 PM.

  13. The Following User Says Thank You to Nostrum For This Useful Post:

    bigstu82 (18-08-2012)

  14. #12
    New to Plumbing Forum
    Join Date
    Aug 2012
    Posts
    6
    Thanks
    2
    Thanked 0 Times in 0 Posts

    Default Re: Pressure relief drain problem

    Quote Originally Posted by sambotc View Post
    Hi bigstu82

    Heres a picture

    The new PRV is exiting out the wall by the flue (assuming it is terminated outside after the extension!)

    The existing PRV stays in, hence the new PRV having a lower rating (2.5 bar)

    Air vent to release air in the vertical pipework, not knock a hole in your wall!

    You should ask ideal first but this is a recognised method, baxi call it a secondary remote pressure relief safety valve or similar. Pretty sure vaillant offer it as well, and all the boilers works on the same principle in this instance so theoretically the boiler make/model is irrelevant. That said you should always go by manufacturers instruction......
    Thanks for the picture, that makes sense - does the air vent have some clever trickery inside it to stop pressurised water getting out (path of least resistance and all that)?

    If you wouldn't mind, as a rough idea, what would the cost of parts be (to the nearest £25 would be fine), and what would a reasonable labour effort look like? Couple of hours (presume the heating would have to be drained and refilled?), or more like a half/full day?

    Thanks :-)

  15. #13
    Plumbers Arms member
    Nostrum's Avatar
    Join Date
    Feb 2012
    Posts
    1,265
    Thanks
    39
    Thanked 99 Times in 94 Posts

    Default Re: Pressure relief drain problem

    Say £40-50 for the bits and 3 hours labour would cover it at a guess I reckon.

Similar Threads

  1. Pressure relief problem
    By Jasonh in forum Plumbing Forum
    Replies: 9
    Last Post: 23-02-2012, 08:54 PM
  2. Pressure relief pipework
    By Nat in forum Central Heating Forum
    Replies: 22
    Last Post: 11-12-2011, 06:38 PM
  3. Pressure relief valve
    By mickeyuk in forum Gas Safe Register Forum - Public Forum
    Replies: 20
    Last Post: 04-09-2011, 11:15 PM
  4. Pressure relief letting by
    By DemC in forum Gas Safe Register Forum - Public Forum
    Replies: 15
    Last Post: 18-07-2011, 09:36 PM
  5. Pressure relief pipe - where does it end
    By Daljit in forum Central Heating Forum
    Replies: 6
    Last Post: 14-12-2009, 12:39 PM

Visitors found this page by searching for:

baxi remote pressure relief valve

how does the baxi remote kit 5121379 work

pressure realese pipe plumbing forum

potterton remote prv installation guide

remote prv valve

potterton remote relief valve kit 5121379

relief valve drain problems