Plumbing & Plumbers Forum - Why size of gas pipe?
Like Tree38Likes

Why size of gas pipe?

Discuss Why size of gas pipe? in the Central Heating Forum at Plumbers Forums; My boiler needs 22mm pipe from the meter, this I understand. So why is the gas connection on the boiler only 15mm, needing an adapter from 22mm to 15mm close ...
  1. #1
    stratobuddy
    Guest

    Default Why size of gas pipe?

    My boiler needs 22mm pipe from the meter, this I understand.

    So why is the gas connection on the boiler only 15mm, needing an adapter from 22mm to 15mm close to the boiler.

    Why isn't the boiler connection 22mm?


  2. #2
    UK Plumbersforums Trusted Advisor.

    Simon F's Avatar
    Join Date
    Nov 2011
    Location
    Nottingham
    Posts
    1,424
    Thanks
    64
    Thanked 284 Times in 276 Posts

    Default Re: Why size of gas pipe?

    if the manufacturer has made the gas connection 15mm then that's sufficient for connection to the boiler.

    its all to do with resistance from the pipe walls affecting the flow of gas, which is very low pressure (19-23mbar )
    the longer the run of pipe the bigger pipe size needed to compensate.
    so the fact that the connection at the boiler is 15mm does not mean that 15mm would be acceptable for the complete run.

    gas is not water which would be fine in 15mm due to a pressure probably 100-200 times higher!

  3. Last edited by Simon F; 09-08-2012 at 04:41 PM.
    If you like my post it was probably taken from a previous thread.
    GSR? Want gas safety or boiler repair advice? We will check out that your genuine via the gas safe website, so please don't be offended when we ask for your details.
    DIYers, bodgers, odd job people and have a go heroes need not apply.






  4. The Following User Says Thank You to Simon F For This Useful Post:


  5. #3
    stratobuddy
    Guest

    Default Re: Why size of gas pipe?

    Thanks for the above, but wouldn't it be easier for the installer if the boiler connection was also 22mm so the pipe could be connected straight in?

  6. #4
    UK Plumbersforums Trusted Advisor.

    Simon F's Avatar
    Join Date
    Nov 2011
    Location
    Nottingham
    Posts
    1,424
    Thanks
    64
    Thanked 284 Times in 276 Posts

    Default Re: Why size of gas pipe?

    some boilers particularly combi's do have a 22mm connection for the gas,
    its no great challenge to fit a reducer on the last stretch of pipe

    depending on the length of pipe and what its supplying could need to come from the meter in 28mm even 35mm and then be teed of to whatever appliances or reduced down as needed
    Last edited by Simon F; 09-08-2012 at 05:01 PM.
    If you like my post it was probably taken from a previous thread.
    GSR? Want gas safety or boiler repair advice? We will check out that your genuine via the gas safe website, so please don't be offended when we ask for your details.
    DIYers, bodgers, odd job people and have a go heroes need not apply.






  7. The Following User Says Thank You to Simon F For This Useful Post:


  8. #5
    UK Plumbersforums Trusted Advisor.

    tamz's Avatar
    Join Date
    Apr 2010
    Location
    Scotland
    Posts
    9,363
    Thanks
    281
    Thanked 1,178 Times in 1,045 Posts

    Default Re: Why size of gas pipe?

    Quote Originally Posted by stratobuddy View Post
    My boiler needs 22mm pipe from the meter, this I understand.

    So why is the gas connection on the boiler only 15mm, needing an adapter from 22mm to 15mm close to the boiler.

    Why isn't the boiler connection 22mm?
    Why does your gas hob come with a 15mm connection when the size of the burner jet is smaller than a pin hole?
    Simon F likes this.

  9. #6
    Plumbers Arms member
    Koogatubac's Avatar
    Join Date
    Jan 2011
    Posts
    1,210
    Thanks
    103
    Thanked 53 Times in 52 Posts

    Default

    Haha Newer boilers require bigger size gas pipe,

    Older boilers werent as big in demand for gas, therefore alot have been on 15mm.

    Nowadays its good practice to come off the gas meter in 28mm (all depends how far the boiler is and how many appliances is going to be run off it.)

    Just as those guys above have mentioned

  10. #7
    SUPER MODERATOR


    REDSAW's Avatar
    Join Date
    Jan 2009
    Location
    sherrif county
    Posts
    9,101
    Thanks
    241
    Thanked 529 Times in 492 Posts

    Default Re: Why size of gas pipe?

    Quote Originally Posted by tamz View Post
    Why does your gas hob come with a 15mm connection when the size of the burner jet is smaller than a pin hole?
    why does a duck spend most of its time with its head and mouth under water when there is a smaller hole in the rear, can they mimic a wave runner?........!...............
    ¡ƃuıɥʇou ʍouʞ ı˙˙˙ɹǝqɯǝɯǝɹ puɐ
    ˙ʎlddɐ ʇou pǝǝu sǝoɹǝɥ oƃ ɐ ǝʌɐɥ puɐ ǝldoǝd qoɾ ppo `sɹǝ,ʎıp ˙slıɐʇǝp ɹnoʎ ɹoɟ ʞsɐ ǝʍ uǝɥʍ pǝpuǝɟɟo ǝq ʇ,uop ǝsɐǝld os `ǝʇısqǝʍ ǝɟɐs sɐƃ ǝɥʇ ɐıʌ ǝuınuǝƃ ǝɹ,noʎ ʇɐɥʇ ʇno ʞɔǝɥɔ llıʍ ǝʍ ¿ǝɔıʌpɐ ɹıɐdǝɹ ɹǝlıoq ɹo ʎʇǝɟɐs sɐƃ ʇuɐʍ noʎ op
    ¿ʞɹoʍ sɐƃ

    ˙lɐoɔ puɐ pooʍ `sɐƃ `lıo ƃuıpnlɔuı `ʇuɹnq sı lǝnɟ ʎuɐ uǝɥʍ pǝɔnpoɹd ǝq uɐɔ ǝpıxouoɯ uoqɹɐɔ :ʇuɐʇɹodɯı


  11. #8
    UK Plumbersforums Trusted Advisor.

    AWheating's Avatar
    Join Date
    Dec 2010
    Location
    WestMidlands
    Posts
    5,803
    Thanks
    124
    Thanked 572 Times in 546 Posts

    Default Re: Why size of gas pipe?

    the appliances connection has no bearing on the size of the pipework required to supply the gas to it. The gas pipe is sized on a number of factors like route and length of pipe run, appliance size/rate, type of material use ect.....
    Ammonia is found on Pluto, Jupiter and, in small amounts, on Uranus.

    are you Gas Safe? want gas safety or boiler repair advice?we will check out that your genuine via the gas safe website,so please dont be offended when we ask for your details.Diyers,potchers,odd job people and have a go heroes need not apply!

    AW Heating and Plumbing Services. Take the Plunge!

    btw im commercial,
    NOT.


  12. #9
    UK Plumbersforums Trusted Advisor.

    kirkgas's Avatar
    Join Date
    Dec 2009
    Location
    Coatbridge, Lanarkshire
    Posts
    3,515
    Thanks
    52
    Thanked 341 Times in 314 Posts

    Default Re: Why size of gas pipe?

    Quote Originally Posted by stratobuddy View Post
    Thanks for the above, but wouldn't it be easier for the installer if the boiler connection was also 22mm so the pipe could be connected straight in?
    who says the boiler needs 22mm for every install? if it has a 115mm connection there will be situations where 15mm is adequate, in different houses with different layouts 22/28/35 might be needed, as others have said some have a 22mm connection so they need

  13. #10
    Plumbers Arms member

    Join Date
    Dec 2009
    Posts
    865
    Thanks
    11
    Thanked 80 Times in 76 Posts

    Default Re: Why size of gas pipe?

    The real answer to your question is available after serving a five year apprenticeship, working on gas for a few years then proving competence by completing never ending expensive courses in Gas Safe procedures, you don't really expect a detailed answer free of charge?

    Or do you?
    Anton likes this.

  14. #11
    UK Plumbersforums Trusted Advisor.
    Howsie's Avatar
    Join Date
    Nov 2010
    Posts
    2,687
    Thanks
    79
    Thanked 151 Times in 149 Posts

    Default

    Why don't you ask the manufacture the question? Only they know the answer as they designed the thing.
    EX VI TERMINI


  15. #12
    Plumbers Arms member
    Koogatubac's Avatar
    Join Date
    Jan 2011
    Posts
    1,210
    Thanks
    103
    Thanked 53 Times in 52 Posts

    Default

    Lol howsie, i like you 'DESIGNED THE THING' HAHA

  16. #13
    stratobuddy
    Guest

    Default Re: Why size of gas pipe?

    All 4 plumbers that gave me an estimate said the existing 15mm supply would not be big enough and they would have to run a 22mm pipe.

  17. #14
    Moderator


    croppie's Avatar
    Join Date
    Jul 2010
    Location
    Portadown, United Kingdom
    Posts
    7,661
    Thanks
    446
    Thanked 533 Times in 494 Posts

    Default Re: Why size of gas pipe?

    There are far too many reasons which we know and you won't. Satisfy yourself with this answer.

    Because it does.
    Propino Tibi Salutem! Usque ad Mortem Bibendum!

    Croppie
    (By the way, I'm commercial!)

    IMPORTANT: Carbon Monoxide can be produced when ANY fuel is burnt, including oil, gas, wood and coal.

    GSR? Want gas safety or boiler repair advice? We will check out that you're genuine via the gas safe website, so please don't be offended when we ask for your details. DIYers, odd job people and have a go heroes need not apply.

  18. #15
    Plumbers Arms member

    Join Date
    Dec 2010
    Posts
    1,366
    Thanks
    103
    Thanked 100 Times in 99 Posts

    Default Re: Why size of gas pipe?

    Quote Originally Posted by stratobuddy View Post
    All 4 plumbers that gave me an estimate said the existing 15mm supply would not be big enough and they would have to run a 22mm pipe.
    What are the chances of all 4 qualified gas engineers being wrong?

Page 1 of 5 1234 ... LastLast

Similar Threads

  1. gas hob pipe size
    By gregg1908 in forum Plumbing Forum
    Replies: 28
    Last Post: 21-06-2011, 05:34 PM
  2. Replies: 1
    Last Post: 22-05-2011, 05:27 PM
  3. Pipe size
    By dylan in forum Central Heating Forum
    Replies: 4
    Last Post: 13-01-2011, 11:15 PM
  4. gas pipe size
    By stewarty in forum Central Heating Forum
    Replies: 20
    Last Post: 14-06-2010, 09:54 AM
  5. Pipe size?
    By plumbingdazman in forum Plumbing Forum
    Replies: 2
    Last Post: 27-05-2010, 05:20 PM

Visitors found this page by searching for:

15mm gas pipe combi boiler

hob gas pipe size 8mm

results of incorrectly sized gas pipe

can i put a 15mm to 22mm adaptor on boiler

central heating incorrect size of gas piping from meter

15mm or 22 mm pipe for 8 burner cooker

boiler pipe adapter size

Tags for this Thread

Plumbers Forums is a Trading Style of Untold Developments Ltd. Search Engine Optimisation, Web Development and Online Marketing for the UK.