baxi 105e overheat problem
hi guys,
i have a baxi 105e and its overheating,the temp neon go up one by one until 80 degrees then lockout, once it cools the boiler fires up again until it reaches 80 degrees,the dhw works as it should no problems the diverter valve and micro switches all work as they should.
*the water in CH pipes/rads is noticeably hotter
*I have changed the thermister with no effect
Im beginning to think its either the PCB or a blocked heat exchanger but not sure hopefully somebody will have experienced this.
is there any way to identify the temp fault?
cheers
-
08-08-2012 #2Plumbers Arms member

- Join Date
- Jan 2012
- Location
- St Albans
- Posts
- 509
- Thanks
- 40
- Thanked 53 Times in 53 Posts
Re: baxi 105e overheat problem
try to search on forum. there is a lot of topics about baxi 105
Plumber and heating engineer in St Albans - http://www.galaxyplumbing.co.uk. Don't understand my English? Please ask me in Slovak then
GSR? Want gas safety or boiler repair advice? We will check out that you're genuine via the gas safe website, so please dont be offended when we ask for your details. DIYers, odd job people and have a go heroes need not apply.
-
The Following User Says Thank You to galaxy_plumbing For This Useful Post:
cdel2005 (10-08-2012)
-
08-08-2012 #3Plumbing Forum Contributor
- Join Date
- Jun 2011
- Posts
- 77
- Thanks
- 2
- Thanked 9 Times in 8 Posts
Re: baxi 105e overheat problem
Had the same problem last week, diverter valve stopped the heat going down the flow, only went to the plate to plate, got hot fast and locked out. Check that first. Flow pipe near boiler will get hot due to heat transfer but feel flow pipe about a meter away, if it isn't getting hot the valve has had it.
-
The Following User Says Thank You to casaco For This Useful Post:
cdel2005 (10-08-2012)
-
08-08-2012 #4UK Plumbersforums Trusted Advisor.


- Join Date
- Aug 2010
- Location
- stoke on trent
- Posts
- 1,857
- Thanks
- 412
- Thanked 82 Times in 77 Posts
Re: baxi 105e overheat problem
as others have said in other posts check the heating return filter. remove the front part of the diverter and check the pin is not seized in the back part of the diverter.
ant
-
The Following User Says Thank You to buckley plumb For This Useful Post:
cdel2005 (10-08-2012)
-
08-08-2012 #5
I had this exact problem. Found that the DHW sensor wasnt functioning right, changed the sensor. That day it kept doing the same fault.
Customer contacted me 5 days after and said the boilers been great and shes had constant hot water
Next port of call i was going to check the DHW Heat exchanger.
-
The Following User Says Thank You to Koogatubac For This Useful Post:
cdel2005 (10-08-2012)
-
08-08-2012 #6Plumbing Forum Contributor
- Join Date
- Jun 2011
- Posts
- 77
- Thanks
- 2
- Thanked 9 Times in 8 Posts
Re: baxi 105e overheat problem
The boiler is working ok on DHW, the Thermistor has been changed, so presumably the fault occurs on heating demand only, so would suspect water not passing through diverter valve to heating circuit, but CH thermistor doesn't know diverter valve is stuck so allows boiler to fire continuously to 80 degrees, boiler shuts down but latent heat exceeds over heat temp at 95 degrees and goes to lock out. simple really.
-
The Following User Says Thank You to casaco For This Useful Post:
cdel2005 (10-08-2012)
-
08-08-2012 #7
So the high limit stat sounds like its working if its cutting the boiler out.
Might be worth checking the heat exchanger isnt blocked
-
The Following User Says Thank You to Koogatubac For This Useful Post:
cdel2005 (10-08-2012)
-
08-08-2012 #8UK Plumbersforums Trusted Advisor.


- Join Date
- Aug 2010
- Location
- stoke on trent
- Posts
- 1,857
- Thanks
- 412
- Thanked 82 Times in 77 Posts
-
The Following User Says Thank You to buckley plumb For This Useful Post:
cdel2005 (10-08-2012)
-
10-08-2012 #9New to Plumbing Forum
- Join Date
- Apr 2009
- Posts
- 5
- Thanks
- 7
- Thanked 0 Times in 0 Posts
Similar Threads
-
baxi 105e problem
By glenno1 in forum Plumbing ForumReplies: 5Last Post: 20-09-2011, 12:35 PM -
baxi 105e problem
By REDSAW in forum Gas Safe Register Forum - Public ForumReplies: 5Last Post: 18-08-2011, 12:22 AM -
Baxi 105e problem - please help
By matt6r in forum Central Heating ForumReplies: 6Last Post: 09-07-2011, 11:48 PM -
baxi 105e dhw problem
By bryan in forum Central Heating ForumReplies: 5Last Post: 14-04-2010, 02:28 PM



Reply With Quote










Hello from totally new plumber
9 Minutes Ago in New Member Introductions