Plumbing & Plumbers Forum - baxi 105e overheat problem

baxi 105e overheat problem

Discuss baxi 105e overheat problem in the Central Heating Forum at Plumbers Forums; hi guys, i have a baxi 105e and its overheating,the temp neon go up one by one until 80 degrees then lockout, once it cools the boiler fires up again ...
  1. #1
    New to Plumbing Forum
    Join Date
    Apr 2009
    Posts
    5
    Thanks
    7
    Thanked 0 Times in 0 Posts

    Default baxi 105e overheat problem

    hi guys,

    i have a baxi 105e and its overheating,the temp neon go up one by one until 80 degrees then lockout, once it cools the boiler fires up again until it reaches 80 degrees,the dhw works as it should no problems the diverter valve and micro switches all work as they should.

    *the water in CH pipes/rads is noticeably hotter

    *I have changed the thermister with no effect


    Im beginning to think its either the PCB or a blocked heat exchanger but not sure hopefully somebody will have experienced this.

    is there any way to identify the temp fault?

    cheers


  2. #2
    Plumbers Arms member
    galaxy_plumbing's Avatar
    Join Date
    Jan 2012
    Location
    St Albans
    Posts
    509
    Thanks
    40
    Thanked 53 Times in 53 Posts

    Default Re: baxi 105e overheat problem

    try to search on forum. there is a lot of topics about baxi 105

  3. Plumber and heating engineer in St Albans - http://www.galaxyplumbing.co.uk. Don't understand my English? Please ask me in Slovak then

    GSR? Want gas safety or boiler repair advice? We will check out that you're genuine via the gas safe website, so please dont be offended when we ask for your details. DIYers, odd job people and have a go heroes need not apply.

  4. The Following User Says Thank You to galaxy_plumbing For This Useful Post:

    cdel2005 (10-08-2012)

  5. #3
    Plumbing Forum Contributor
    Join Date
    Jun 2011
    Posts
    77
    Thanks
    2
    Thanked 9 Times in 8 Posts

    Default Re: baxi 105e overheat problem

    Had the same problem last week, diverter valve stopped the heat going down the flow, only went to the plate to plate, got hot fast and locked out. Check that first. Flow pipe near boiler will get hot due to heat transfer but feel flow pipe about a meter away, if it isn't getting hot the valve has had it.

  6. The Following User Says Thank You to casaco For This Useful Post:

    cdel2005 (10-08-2012)

  7. #4
    UK Plumbersforums Trusted Advisor.


    Join Date
    Aug 2010
    Location
    stoke on trent
    Posts
    1,857
    Thanks
    412
    Thanked 82 Times in 77 Posts

    Default Re: baxi 105e overheat problem

    as others have said in other posts check the heating return filter. remove the front part of the diverter and check the pin is not seized in the back part of the diverter.

    ant

  8. The Following User Says Thank You to buckley plumb For This Useful Post:

    cdel2005 (10-08-2012)

  9. #5
    Plumbers Arms member
    Koogatubac's Avatar
    Join Date
    Jan 2011
    Posts
    1,210
    Thanks
    103
    Thanked 53 Times in 52 Posts

    Default

    I had this exact problem. Found that the DHW sensor wasnt functioning right, changed the sensor. That day it kept doing the same fault.

    Customer contacted me 5 days after and said the boilers been great and shes had constant hot water

    Next port of call i was going to check the DHW Heat exchanger.

  10. The Following User Says Thank You to Koogatubac For This Useful Post:

    cdel2005 (10-08-2012)

  11. #6
    Plumbing Forum Contributor
    Join Date
    Jun 2011
    Posts
    77
    Thanks
    2
    Thanked 9 Times in 8 Posts

    Default Re: baxi 105e overheat problem

    The boiler is working ok on DHW, the Thermistor has been changed, so presumably the fault occurs on heating demand only, so would suspect water not passing through diverter valve to heating circuit, but CH thermistor doesn't know diverter valve is stuck so allows boiler to fire continuously to 80 degrees, boiler shuts down but latent heat exceeds over heat temp at 95 degrees and goes to lock out. simple really.

  12. The Following User Says Thank You to casaco For This Useful Post:

    cdel2005 (10-08-2012)

  13. #7
    Plumbers Arms member
    Koogatubac's Avatar
    Join Date
    Jan 2011
    Posts
    1,210
    Thanks
    103
    Thanked 53 Times in 52 Posts

    Default

    So the high limit stat sounds like its working if its cutting the boiler out.

    Might be worth checking the heat exchanger isnt blocked

  14. The Following User Says Thank You to Koogatubac For This Useful Post:

    cdel2005 (10-08-2012)

  15. #8
    UK Plumbersforums Trusted Advisor.


    Join Date
    Aug 2010
    Location
    stoke on trent
    Posts
    1,857
    Thanks
    412
    Thanked 82 Times in 77 Posts

    Default Re: baxi 105e overheat problem

    Quote Originally Posted by casaco View Post
    The boiler is working ok on DHW, the Thermistor has been changed, so presumably the fault occurs on heating demand only, so would suspect water not passing through diverter valve to heating circuit, but CH thermistor doesn't know diverter valve is stuck so allows boiler to fire continuously to 80 degrees, boiler shuts down but latent heat exceeds over heat temp at 95 degrees and goes to lock out. simple really.
    check filter first if hw is ok then could be heating rtn filter

  16. The Following User Says Thank You to buckley plumb For This Useful Post:

    cdel2005 (10-08-2012)

  17. #9
    New to Plumbing Forum
    Join Date
    Apr 2009
    Posts
    5
    Thanks
    7
    Thanked 0 Times in 0 Posts

    Default Re: baxi 105e overheat problem

    the dhw works when on dhw only and ch/dhw

    Quote Originally Posted by Koogatubac View Post
    I had this exact problem. Found that the DHW sensor wasnt functioning right, changed the sensor. That day it kept doing the same fault.

    Customer contacted me 5 days after and said the boilers been great and shes had constant hot water

    Next port of call i was going to check the DHW Heat exchanger.

Similar Threads

  1. baxi 105e problem
    By glenno1 in forum Plumbing Forum
    Replies: 5
    Last Post: 20-09-2011, 12:35 PM
  2. baxi 105e problem
    By REDSAW in forum Gas Safe Register Forum - Public Forum
    Replies: 5
    Last Post: 18-08-2011, 12:22 AM
  3. Baxi 105e problem - please help
    By matt6r in forum Central Heating Forum
    Replies: 6
    Last Post: 09-07-2011, 11:48 PM
  4. baxi 105e dhw problem
    By bryan in forum Central Heating Forum