Old 06-07-2009   #1 (permalink)
shuttlebasher
Junior Member
Info
 

Join Date: Jul 2009
Posts: 15

Default Hot water cylinder

Hi all hope you can help have just fitted a new cylinder moved the central heating pump and motorised valve to suite however filled the system and have heat to the radiators however no hot water has anybody got any ideas i think the motorissed valve is working as can here it kick in
shuttlebasher is offline  
Reply With Quote
Old 06-07-2009   #2 (permalink)
newbie1
Senior Member
Info
 

Join Date: Dec 2008
Posts: 752

Default Re: Hot water cylinder

assuming 3 port mid position valve it is either wired wrong or stuck as the 3 port is hw/ch or mid postn ch and hw
newbie1 is offline  
Reply With Quote
Old 06-07-2009   #3 (permalink)
shuttlebasher
Junior Member
Info
 

Join Date: Jul 2009
Posts: 15

Default Re: Hot water cylinder

Quote:
Originally Posted by newbie1 View Post
assuming 3 port mid position valve it is either wired wrong or stuck as the 3 port is hw/ch or mid postn ch and hw
If i have tried the manual overide and it still does not work could it be an airlock in the coil in the cylinder?
shuttlebasher is offline  
Reply With Quote
Old 06-07-2009   #4 (permalink)
Bernie2
Moderator
Info
 

Join Date: Mar 2009
Posts: 962

Default Re: Hot water cylinder

The cylinder coil sure can get air locked. But what valve or valves are you using?

Mid position three port, three port diverter, zone valves.

A mid position valve can usually be moved to its mid position and then you would have both legs getting hot. A diverter usually only heats one leg at a time. Zone valves are only electric stop taps so control each leg inidvidually.

If there are no air bleeds about to try for air. Get a bucket if you can and crack the backnut on the hot water side of the valve after making sure the valve is in the right position. This should bleed any air out of the coil, but wait till the system is cold to do it. And be quick or get wet. Watch the carpets and ceiling below.

Its a Plumbers game of chicken.
Bernie2 is offline  
Reply With Quote
Old 06-07-2009   #5 (permalink)
shuttlebasher
Junior Member
Info
 

Join Date: Jul 2009
Posts: 15

Default Re: Hot water cylinder

Thanks the valve fitted is a Grunfoss Hsa3 just notice when i put the water to heat only ,the radiators are heating up but not the cylinder may be an issue in the way the valve been positioned or i have rewired it wrong will have to check it as for the air locks got my wellies at the ready ...lol
shuttlebasher is offline  
Reply With Quote
Old 06-07-2009   #6 (permalink)
NickH
Senior Member
Info
 

Join Date: Mar 2008
Posts: 337

Default Re: Hot water cylinder

I've seen replacement cylinders installed where the new top coil connection sits higher than the old one. If you have just extended the existing pipework upwards to suit, you end up with a air lock in this "loop". If this is the case you have to fit an auto air vent in the top of it.
NickH is offline  
Reply With Quote
Old 06-07-2009   #7 (permalink)
puddle
Senior Member
Info
 

Join Date: May 2009
Location: London/Lincolnshire
Posts: 1,391

Default Re: Hot water cylinder

if you can hear the valve 'kick in' when on hot water mode,valve probably wired incorrectly as no power to valve motor gives you hot water only
A quick test for you to do is turn power off to system this will make sure valve in hot water position ,then remove valve head from body ,then turn power on to allow boiler and pump to operate,hot water should get hot as valve in correct position ,if so wire valve correctly,if rads get hot,valve wrong way round,is nothing gets hot possible air lock
puddle is offline  
Reply With Quote
Old 07-07-2009   #8 (permalink)
shuttlebasher
Junior Member
Info
 

Join Date: Jul 2009
Posts: 15

Default Re: Hot water cylinder

Quote:
Originally Posted by puddle View Post
if you can hear the valve 'kick in' when on hot water mode,valve probably wired incorrectly as no power to valve motor gives you hot water only
A quick test for you to do is turn power off to system this will make sure valve in hot water position ,then remove valve head from body ,then turn power on to allow boiler and pump to operate,hot water should get hot as valve in correct position ,if so wire valve correctly,if rads get hot,valve wrong way round,is nothing gets hot possible air lock

Thanks Puddle will try that must be something like that as when i switch just the hot water just the heating comes on?
shuttlebasher is offline  
Reply With Quote
Reply
  

Bookmarks

Tags
None



Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Bungalow with requirement for instant hot water and more water pressure in bathrooms David Salter Showers and Wetrooms 3 06-10-2009 11:56 PM
Hwlo with wold water tank overflowing philwilliams Plumbing Forum 2 13-04-2009 08:57 PM
Hot taps run cold - not the boiler, I reckon... plumb-line Plumbing Forum 4 30-03-2009 09:21 AM
Torrent hot water cylinder problems sasik Plumbing Forum 4 09-03-2009 08:56 AM
Brown hot water Leeky Central Heating Forum 10 14-12-2008 03:50 PM


All times are GMT +1. The time now is 02:16 AM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.
Content Relevant URLs by vBSEO 3.0.0

u.m Network: Contractor Forum | Tilers Forum | Electrical Forum | Flooring Forum | Plastering Forum |
(c) 2007 Plumbing Advice Forum - UK Plumbers Forums

<Search Engine Optimisation Help

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89