Hi! Jimmy!
This is a bit like an old design we used in the 1970's.
If you look at it though where does the air get out?
Why does the cylinder return go on as the hot flow to the rads?
Why is there no by pass to allow circulation if all the valves close down?
Some oil boilers require a minimum of 40C Return temperature. If the water won't circulate because the valves are closed how will it do that?
An oil boiler runs hot and probably requires a pump over run to cool it after its fired, once again how are you going to do that without a by pass?
If the central heating and hot water are on, there is a chance the radiator return would force water back up the hot water return. Its usual to put the rad return behind the hot water return not in front as shown. You could of course use an injector tee on the rad return.
Incidentally I would check whether Irish standards are accepted as acceptable standards over here.