Plumbing & Plumbers Forum - diverter valve prolems
Like Tree2Likes
  • 2 Post By SimonG

diverter valve prolems

Discuss diverter valve prolems in the Central Heating Forum at Plumbers Forums; Hi I am having a problem with my potterton performa 28i boiler. Central heating works fine. Dhw giving cold water only. When you open a hot tap, Dhw diaphragm opens ...
  1. #1
    New to Plumbing Forum
    Join Date
    Apr 2012
    Posts
    4
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default diverter valve prolems

    Hi
    I am having a problem with my potterton performa 28i boiler.
    Central heating works fine. Dhw giving cold water only.
    When you open a hot tap, Dhw diaphragm opens and micro switch is made, boiler fires up and the temp sensor lights on the front panel go up from 30 deg up to 70 deg. but the diverter valve does not change position. No change in voltage on PCB [to move diverter]
    I have tried different positions of taps to give different flow rates but still the same. Flow of water from taps is good
    I have gone through the fault guide and tested and or changed the following items
    Diverter valve works if you press down plunger manually and diverts water.
    Dhw temp sensor 11 ohms cold 3 ohms very hot
    Diverter head new
    PCB tried 2 off brand new boards, not repaired.
    Checked both microswitchs for continuity both ok
    Both the pressure valve and the Dhw pressure differential valve are working fine and both microswitchs work ok.
    I have removed microswitchs and manually operated them and still the same fault


  2. #2
    UK Plumbersforums Trusted Advisor.

    diamondgas's Avatar
    Join Date
    Apr 2011
    Location
    Newcastle Upon tyne
    Posts
    6,052
    Thanks
    299
    Thanked 770 Times in 744 Posts

    Default Re: diverter valve prolems

    Sounds like you know a lot about your boiler ossie8743, welcome to the forum

    Could it be that the preheat diverter is stuck in preheat position? Deffo sounds like the water isn't getting through the plate hex.... Any temp rise at all on the hot water?

  3. "Put your hand on a hot stove for a minute, and it seems like an hour. Sit with a pretty girl for an hour, and it seems like a minute. THAT'S relativity." Albert Einstein

  4. #3
    Steady Plumbing Forum Contributor

    Join Date
    Dec 2011
    Location
    Bathgate
    Posts
    174
    Thanks
    8
    Thanked 15 Times in 15 Posts

    Default Re: diverter valve prolems

    Are you sure the microswitch is operating? When you turn on the taps does the flow/return get hot, if so the diaphragm is your prob

  5. #4
    New to Plumbing Forum
    Join Date
    Apr 2012
    Posts
    4
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: diverter valve prolems

    Quote Originally Posted by Atouchofgas View Post
    Are you sure the microswitch is operating? When you turn on the taps does the flow/return get hot, if so the diaphragm is your prob
    e

    both of the micro switchs are working,have put meter across connections and they come on when boiler calls for dhw. both
    the pressure diaphragm and diverter diaphragm operate. flow and return cold. boiler stays lit until water reaches 70 deg

  6. #5
    UK Plumbersforums Trusted Advisor.

    diamondgas's Avatar
    Join Date
    Apr 2011
    Location
    Newcastle Upon tyne
    Posts
    6,052
    Thanks
    299
    Thanked 770 Times in 744 Posts

    Default Re: diverter valve prolems

    Quote Originally Posted by ossie8743 View Post
    e

    both of the micro switchs are working,have put meter across connections and they come on when boiler calls for dhw. both
    the pressure diaphragm and diverter diaphragm operate. flow and return cold. boiler stays lit until water reaches 70 deg
    The diverter diaphragm can operate the microswitch but that doesn't say the diverter valve is moving from pre-heat to hot water position. Does the p-hex get hot when calling for h/w?
    "Put your hand on a hot stove for a minute, and it seems like an hour. Sit with a pretty girl for an hour, and it seems like a minute. THAT'S relativity." Albert Einstein

  7. #6
    New to Plumbing Forum
    Join Date
    Apr 2012
    Posts
    4
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: diverter valve prolems

    from cold with c/h t/stat turned to min so dhw only . open tap boiler fires up pri heat ex gets hot pipes from and to pri heat ex get hot diverter gets hot. but no dhw

  8. #7
    UK Plumbersforums Trusted Advisor.

    diamondgas's Avatar
    Join Date
    Apr 2011
    Location
    Newcastle Upon tyne
    Posts
    6,052
    Thanks
    299
    Thanked 770 Times in 744 Posts

    Default Re: diverter valve prolems

    Next stage is check flow rate at hot tap and temp diff hot/cold ... Check mi's for what you should be expecting ... If there is no significant diff between hot and cold I'd honestly think the water was being diverted away from the p-hex ... When you tried different flow rated did you crack the tap back as low as possible? Are you familiar with how the hydraulics work on this model boiler? Are you GSR?
    "Put your hand on a hot stove for a minute, and it seems like an hour. Sit with a pretty girl for an hour, and it seems like a minute. THAT'S relativity." Albert Einstein

  9. #8
    New to Plumbing Forum
    Join Date
    Apr 2012
    Posts
    4
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: diverter valve prolems

    many thanks for al l your help.
    went back to basics and re checked everything
    found that when dhw called for heat the diverter valve was heating the c/h side. and not the dhw side. i thing that the diverter main body is blocked and will fit a new one.

  10. #9
    Plumbers Arms member SimonG's Avatar
    Join Date
    Feb 2011
    Location
    The Land Of The Prince Bishops
    Posts
    7,230
    Thanks
    284
    Thanked 691 Times in 681 Posts

    Default Re: diverter valve prolems

    Quote Originally Posted by diamondgas View Post
    Are you GSR?
    That'll be a no then
    dancinplumba and Whn1 like this.
    If You Burn It, It Can Kill You.

  11. #10
    UK Plumbersforums Trusted Advisor.

    diamondgas's Avatar
    Join Date
    Apr 2011
    Location
    Newcastle Upon tyne
    Posts
    6,052
    Thanks
    299
    Thanked 770 Times in 744 Posts

    Default Re: diverter valve prolems

    Quote Originally Posted by ossie8743 View Post
    many thanks for al l your help.
    went back to basics and re checked everything
    found that when dhw called for heat the diverter valve was heating the c/h side. and not the dhw side. i thing that the diverter main body is blocked and will fit a new one.
    Thanks for letting us know ... It'd be interesting to know if that resolves the issue
    "Put your hand on a hot stove for a minute, and it seems like an hour. Sit with a pretty girl for an hour, and it seems like a minute. THAT'S relativity." Albert Einstein

  12. #11
    Banned
    Join Date
    Apr 2012
    Posts
    5
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: diverter valve prolems

    Valve stems should have a gasket or packing material, usually adjusted for proper sealing without too much stiffness turning by tightening the cap or nut in front.

    The valve stem can leak when turned to one direction and not leak when turned in another direction.

    Could there be a hole in the diverter assembly? A hole that is in the channel going down to the spout? Plummer

Similar Threads

  1. diverter valve
    By strom in forum Plumbing Forum
    Replies: 5
    Last Post: 15-01-2012, 09:40 PM
  2. diverter valve
    By dboi78 in forum Central Heating Forum
    Replies: 9
    Last Post: 31-10-2011, 07:49 PM
  3. Leak between DHW Flow Valve and Diverter Valve Assembly
    By prestonperson in forum Plumbing Forum
    Replies: 7
    Last Post: 01-04-2011, 01:25 PM
  4. 3 way diverter valve
    By pauls in forum Central Heating Forum
    Replies: 1
    Last Post: 25-04-2010, 11:07 PM
  5. Diverter valve
    By Matty A in forum Central Heating Forum
    Replies: 4
    Last Post: 03-12-2007, 12:12 AM