Pressure gauge keep creeping up to 2bar.

Discuss Pressure gauge keep creeping up to 2bar. in the Central Heating Forum at Plumbers Forums; Hi all, wonder someone can shed some lights to this, the gauge on my boiler (Valliant turbomax combi) keep increase to around 2bar. I bled the radiators and drain out ...
  1. #1
    Steady Plumbing Forum Contributor
    Join Date
    Jan 2012
    Posts
    135
    Thanks
    0
    Thanked 1 Time in 1 Post

    Default Pressure gauge keep creeping up to 2bar.

    Hi all, wonder someone can shed some lights to this, the gauge on my boiler (Valliant turbomax combi) keep increase to around 2bar. I bled the radiators and drain out some of the radiators water brought the pressure down to under 1bar but when the heating comes on for about 1 hr the gauge shows nearly 2bar. Tried this a few times, still the same. Could this be an expansion vessel fault in the boiler?

  2. something I do on the side I am trying

    www.myfootballgifts.co.uk my site!

    www.kokio.co.uk my wife's site!

  3. #2
    UK Plumbersforums Trusted Advisor.
    Howsie's Avatar
    Join Date
    Nov 2010
    Posts
    2,994
    Thanks
    85
    Thanked 169 Times in 167 Posts

    Default Re: Pressure gauge keep creeping up to 2bar.

    Up to 2bar isn't a problem. The water expands when it's heated and its natural to see a pressure increase.

    If it continues to increase it would seem that you're filling loop is connected and letting bye.


  4. #3
    Banned
    Join Date
    Dec 2009
    Location
    Portsmouth
    Posts
    672
    Thanks
    64
    Thanked 70 Times in 68 Posts

    Default Re: Pressure gauge keep creeping up to 2bar.


    If the exp vessel was faulty, or needed recharging, then the pressure would normally shoot up quite rapidly.

  5. #4
    Plumbers Arms member JCplumb's Avatar
    Join Date
    Mar 2012
    Location
    Bolton
    Posts
    942
    Thanks
    28
    Thanked 97 Times in 94 Posts

    Default Re: Pressure gauge keep creeping up to 2bar.

    If the filling loop was letting by, the system pressure would also rise when not in use, so easy diagnosis for that one - turn heating off, let it cool down, is it still rising?

  6. #5
    UK Plumbersforums Trusted Advisor.

    dontknowitall's Avatar
    Join Date
    Apr 2008
    Location
    South Shropshire
    Posts
    6,082
    Thanks
    514
    Thanked 679 Times in 613 Posts

    Default Re: Pressure gauge keep creeping up to 2bar.

    If you remove the filling loop you'll soon know whether it or the fittings around it are at fault. If it's not letting by then it's most likely to be the expansion vessel.
    I'm not a complete idiot; some parts are missing

  7. #6
    Steady Plumbing Forum Contributor
    Join Date
    Jan 2012
    Posts
    135
    Thanks
    0
    Thanked 1 Time in 1 Post

    Default

    Thx guys. Will recheck to see if it's letby although that was the first thing I checked and the valve was shut.
    something I do on the side I am trying

    www.myfootballgifts.co.uk my site!

    www.kokio.co.uk my wife's site!

  8. #7
    UK Plumbersforums Trusted Advisor.

    dontknowitall's Avatar
    Join Date
    Apr 2008
    Location
    South Shropshire
    Posts
    6,082
    Thanks
    514
    Thanked 679 Times in 613 Posts

    Default Re: Pressure gauge keep creeping up to 2bar.

    Aye - the valve may well be shut but it might not have isolated the water - if you remove the filling loop you'll see if it's letting some through.
    I'm not a complete idiot; some parts are missing

  9. #8
    Plumbers Arms member
    Whn1's Avatar
    Join Date
    Mar 2012
    Location
    London
    Posts
    1,295
    Thanks
    24
    Thanked 76 Times in 71 Posts

    Default Re: Pressure gauge keep creeping up to 2bar.

    Does it stop at 2bar?
    GSR engineer based in south east London

    IMPORTANT: Carbon Monoxide can be produced when ANY fuel is burnt, including oil, gas, wood and coal.

    GSR? Want gas safety or boiler repair advice? We will check out that you're genuine via the gas safe website, so please dont be offended when we ask for your details. DIYers, odd job people and have a go heroes need not apply.

  10. #9
    Steady Plumbing Forum Contributor
    Join Date
    Jan 2012
    Posts
    135
    Thanks
    0
    Thanked 1 Time in 1 Post

    Default

    Can't remove filling loop
    as it is built in. Yes it stop at around 2 bars - u got some idea?
    something I do on the side I am trying

    www.myfootballgifts.co.uk my site!

    www.kokio.co.uk my wife's site!

  11. #10
    UK Plumbersforums Trusted Advisor.
    Howsie's Avatar
    Join Date
    Nov 2010
    Posts
    2,994
    Thanks
    85
    Thanked 169 Times in 167 Posts

    Default

    How many rads do you have?
    EX VI TERMINI


  12. #11
    UK Plumbersforums Trusted Advisor.
    Howsie's Avatar
    Join Date
    Nov 2010
    Posts
    2,994
    Thanks
    85
    Thanked 169 Times in 167 Posts

    Default

    Stops at 2 bar, no problem.
    EX VI TERMINI


  13. #12
    Steady Plumbing Forum Contributor
    Join Date
    Jan 2012
    Posts
    135
    Thanks
    0
    Thanked 1 Time in 1 Post

    Default

    10 rads.
    something I do on the side I am trying

    www.myfootballgifts.co.uk my site!

    www.kokio.co.uk my wife's site!

Page 1 of 2 12 LastLast

Similar Threads

  1. Filling loop pressure gauge
    By M.Joshi in forum Central Heating Forum
    Replies: 42
    Last Post: 16-04-2012, 11:16 PM
  2. CH pressure gauge fluctuates between 0 and 1 bar?
    By BAAZ in forum Plumbing Forum
    Replies: 1
    Last Post: 14-11-2011, 10:42 PM
  3. How do I adjust my pressure gauge?
    By eric.e in forum Central Heating Forum
    Replies: 7
    Last Post: 15-12-2010, 05:39 PM
  4. pressure gauge
    By pauls in forum Plumbing Tools
    Replies: 5
    Last Post: 06-12-2010, 06:46 PM
  5. Pressure Gauge not responding to refill
    By wizardsaleem in forum Plumbing Forum
    Replies: 6
    Last Post: 17-07-2009, 11:15 AM