Plumbing & Plumbers Forum - Main 24 HE burner failure

Main 24 HE burner failure

Discuss Main 24 HE burner failure in the Central Heating Forum at Plumbers Forums; Just been out to see a Main 24 HE which fails to spark/ignite. Have followed fault finding sequence, fan runs, airflow switch proved but the PCB is not providing 240v ...
  1. #1
    New to Plumbing Forum
    Join Date
    Aug 2010
    Location
    Cardiff
    Posts
    21
    Thanks
    6
    Thanked 1 Time in 1 Post

    Default Main 24 HE burner failure

    Just been out to see a Main 24 HE which fails to spark/ignite.

    Have followed fault finding sequence, fan runs, airflow switch proved but the PCB is not providing 240v to the
    gas valve (connection 37 and 38). Have also tested the rest switch. I am 99% sure the PCB is faulty is there any other test i can do to be 100% sure.

    If PCB was not faulty would the voltage be present at connection 37 and 38 during start up and until boiler goes into failure mode


    many thanks


  2. #2
    Plumbers Arms member
    Hardy1's Avatar
    Join Date
    Sep 2011
    Location
    SE London
    Posts
    540
    Thanks
    9
    Thanked 29 Times in 28 Posts

    Default Re: Main 24 HE burner failure

    isit a new boiler?, cause funnily enough i was out with a gas safe engineer 3 days ago, and had exactly the same problem, it was just the purge volume of the run that had to be calculated and it fired like a piece of art, from what ive heard recently there is a faulty batch of main 24's out there with manufacturer's faults so people watch your backs. o and check the electrodes are working and the air vent is open on the pump and top.


  3. #3
    UK Plumbersforums Trusted Advisor.

    diamondgas's Avatar
    Join Date
    Apr 2011
    Location
    Newcastle Upon tyne
    Posts
    6,116
    Thanks
    306
    Thanked 779 Times in 753 Posts

    Default Re: Main 24 HE burner failure

    Are you getting a spark tonyacktar? and lights flashing? ...... you've described some of the process the boiler goes through but haven't mentioned whether it locks out and what indicator is showing?
    "Put your hand on a hot stove for a minute, and it seems like an hour. Sit with a pretty girl for an hour, and it seems like a minute. THAT'S relativity." Albert Einstein

  4. #4
    Plumbers Arms member
    Hardy1's Avatar
    Join Date
    Sep 2011
    Location
    SE London
    Posts
    540
    Thanks
    9
    Thanked 29 Times in 28 Posts

    Default Re: Main 24 HE burner failure

    fault code E133?

  5. #5
    uɐɯ sɐƃ moderator


    gas man's Avatar
    Join Date
    Jan 2010
    Location
    maesteg,south wales
    Posts
    13,567
    Thanks
    836
    Thanked 1,284 Times in 1,225 Posts

    Default Re: Main 24 HE burner failure

    band a or b they are mechanically different,and have you checked for reversed polarity

    GASMAN
    fear keeps you alive
    fearless gets you killed

    IMPOR
    TANT: Carbon Monoxide can be produced when ANY fuel is burnt, including oil, gas, wood and coal.
    GSR?want gas safety or boiler repair advice?we will check out that your genuine via the gas safe website,so please dont be offended when we ask for your details
    diyers,potchers,odd job people and have a go heroes need not apply
    ​BAXI/POTTERTON INSTALLER/SERVICE ENGINEER
    ​ land rover equipped,you can go faster,i can go anywhere


  6. #6
    Plumbers Arms member

    Join Date
    Jul 2009
    Location
    Liverpool
    Posts
    171
    Thanks
    0
    Thanked 31 Times in 30 Posts

    Default Re: Main 24 HE burner failure

    Quote Originally Posted by tonyacktar View Post
    Just been out to see a Main 24 HE which fails to spark/ignite.

    Have followed fault finding sequence, fan runs, airflow switch proved but the PCB is not providing 240v to the
    gas valve (connection 37 and 38). Have also tested the rest switch. I am 99% sure the PCB is faulty is there any other test i can do to be 100% sure.

    If PCB was not faulty would the voltage be present at connection 37 and 38 during start up and until boiler goes into failure mode


    many thanks
    How did you test the APS with a meter on continuity or suck it and listen for a click..PCB`s are pretty safe on these now.
    Last edited by Poxi; 19-10-2011 at 10:05 PM.

  7. #7
    Plumbers Arms member

    Join Date
    Jul 2009
    Location
    Liverpool
    Posts
    171
    Thanks
    0
    Thanked 31 Times in 30 Posts

    Default Re: Main 24 HE burner failure

    Quote Originally Posted by Hardy1 View Post
    from what ive heard recently there is a faulty batch of main 24's out there with manufacturer's faults so people watch your backs.
    Really...Do tell more im intrested
    Last edited by Poxi; 19-10-2011 at 10:09 PM.

  8. #8
    uɐɯ sɐƃ moderator


    gas man's Avatar
    Join Date
    Jan 2010
    Location
    maesteg,south wales
    Posts
    13,567
    Thanks
    836
    Thanked 1,284 Times in 1,225 Posts

    Default Re: Main 24 HE burner failure

    Quote Originally Posted by Poxi View Post
    Really...Do tell more im intrested
    well i have not come across that,2 reasons why pcb,s go on this boiler
    1,halfwits who reverse the polarity then wonder why the boiler keeps going to flame failure
    2,water leaks from the heat exchanger o rings if over pressured ,but this will see off a 105 instant with the Siemens pcb but on main 24/30 he with the Honeywell pcb you have a chance of drying it out and saving it....sometimes other than that they rarely have pcb failure this is the reason i asked the op if its a band a or b is because if its a band b he may have aps failure

    GASMAN
    fear keeps you alive
    fearless gets you killed

    IMPOR
    TANT: Carbon Monoxide can be produced when ANY fuel is burnt, including oil, gas, wood and coal.
    GSR?want gas safety or boiler repair advice?we will check out that your genuine via the gas safe website,so please dont be offended when we ask for your details
    diyers,potchers,odd job people and have a go heroes need not apply
    ​BAXI/POTTERTON INSTALLER/SERVICE ENGINEER
    ​ land rover equipped,you can go faster,i can go anywhere


  9. #9
    Plumbers Arms member
    Hardy1's Avatar
    Join Date
    Sep 2011
    Location
    SE London
    Posts
    540
    Thanks
    9
    Thanked 29 Times in 28 Posts

    Default Re: Main 24 HE burner failure

    Quote Originally Posted by Poxi View Post
    Really...Do tell more im intrested
    well went to a job with a engineer, and he couldnt couldnt figure it out, it was a new install we had been called to, the guy that installed it was on holiday(dont ask), and run all checks e.t.c, so rang up the guy the customer bought it from and he was like do this and that blah blah blah, and then in the end he was like well ive had a couple of complaints about these exact make same problem and then he goes manufacturers fault on a bunch of them, but then there was me thinking, while my engineer mate was on the phone and i took the gas pipe fitting of the elbow to the boiler and purged the pipework for atleast 5 Minz ( i fink), and all i could smell was air not gas so i was like :S :S :S :S :S :S,(engineer not even looking at me lol), and then i smelt gas properly so connected it all back up and it fired perfectly, what it was, was like 32mm PE pipe had been used for the run outside (obviousely) and then 28 inside reduced to 22mm to the boiler, so all it needed was a good purge volume which i worked out and was fine, Engineer face was like :|, o what a good day he evn brought me 3 pints after work for that.

  10. #10
    Plumbers Arms member

    Join Date
    Jul 2009
    Location
    Liverpool
    Posts
    171
    Thanks
    0
    Thanked 31 Times in 30 Posts

    Default Re: Main 24 HE burner failure

    Quote Originally Posted by Hardy1 View Post
    well went to a job with a engineer, and he couldnt couldnt figure it out, it was a new install we had been called to, the guy that installed it was on holiday(dont ask), and run all checks e.t.c, so rang up the guy the customer bought it from and he was like do this and that blah blah blah, and then in the end he was like well ive had a couple of complaints about these exact make same problem and then he goes manufacturers fault on a bunch of them, but then there was me thinking, while my engineer mate was on the phone and i took the gas pipe fitting of the elbow to the boiler and purged the pipework for atleast 5 Minz ( i fink), and all i could smell was air not gas so i was like :S :S :S :S :S :S,(engineer not even looking at me lol), and then i smelt gas properly so connected it all back up and it fired perfectly, what it was, was like 32mm PE pipe had been used for the run outside (obviousely) and then 28 inside reduced to 22mm to the boiler, so all it needed was a good purge volume which i worked out and was fine, Engineer face was like :|, o what a good day he evn brought me 3 pints after work for that.
    Good Man

    Cant wait to finish work tomorrow, Then will be on the pints all weekend myself

  11. #11
    Plumbers Arms member
    Hardy1's Avatar
    Join Date
    Sep 2011
    Location
    SE London
    Posts
    540
    Thanks
    9
    Thanked 29 Times in 28 Posts

    Default Re: Main 24 HE burner failure

    and i cant wait till all this revision is done and im doing my ACS then i will be sitting down with 5 pints of stella and a bottle of famous G on that friday for sure.

  12. #12
    Plumbers Arms member
    cdodds2004's Avatar
    Join Date
    Dec 2010
    Posts
    626
    Thanks
    17
    Thanked 30 Times in 29 Posts

    Default Re: Main 24 HE burner failure

    yea check polarity, first of all, turn spur on and boiler off and see if you have 240 at the live
    For a premier service in Telford and surrounding areas

    boiler,installation,servicing,landlords Certs
    breakdowns,plumbing and gas work


    www.firstcallgasandheating.co.uk

Page 1 of 2 12 LastLast

Similar Threads

  1. Main 24he flame failure light perminatly on
    By david bateman in forum Central Heating Forum
    Replies: 16
    Last Post: 17-07-2011, 01:00 AM
  2. glow worm ultimate 100ff - main burner lights and shuts off
    By Centralheatking in forum Central Heating Forum
    Replies: 3
    Last Post: 13-07-2011, 09:55 PM
  3. Ideal Icos HE 18 Burner Box Failure
    By willing2learn in forum Gas Safe Register Forum - Public Forum
    Replies: 11
    Last Post: 06-04-2011, 10:17 PM
  4. Main 24HE flame failure
    By dc84 in forum Central Heating Forum
    Replies: 10
    Last Post: 26-12-2010, 02:04 PM

Visitors found this page by searching for:

main combi 24 he flame failure flashing

main combi 24 he flame failure

main 24 he fault findingmain combi 24 he fault findingbaxi main 24 he flame failuremain combi 24 he faultsbaxi main combi 24 he flame failure