Main 24 HE burner failure
Discuss Main 24 HE burner failure in the Central Heating Forum at Plumbers Forums; Just been out to see a Main 24 HE which fails to spark/ignite. Have followed fault finding sequence, fan runs, airflow switch proved but the PCB is not providing 240v ...-
18-10-2011 #1New to Plumbing Forum
- Join Date
- Aug 2010
- Location
- Cardiff
- Posts
- 21
- Thanks
- 6
- Thanked 1 Time in 1 Post
Main 24 HE burner failure
Just been out to see a Main 24 HE which fails to spark/ignite.
Have followed fault finding sequence, fan runs, airflow switch proved but the PCB is not providing 240v to the
gas valve (connection 37 and 38). Have also tested the rest switch. I am 99% sure the PCB is faulty is there any other test i can do to be 100% sure.
If PCB was not faulty would the voltage be present at connection 37 and 38 during start up and until boiler goes into failure mode
many thanks
-
19-10-2011 #2Plumbers Arms member

- Join Date
- Sep 2011
- Location
- SE London
- Posts
- 540
- Thanks
- 9
- Thanked 29 Times in 28 Posts
Re: Main 24 HE burner failure
isit a new boiler?, cause funnily enough i was out with a gas safe engineer 3 days ago, and had exactly the same problem, it was just the purge volume of the run that had to be calculated and it fired like a piece of art, from what ive heard recently there is a faulty batch of main 24's out there with manufacturer's faults so people watch your backs. o and check the electrodes are working and the air vent is open on the pump and top.
-
19-10-2011 #3UK Plumbersforums Trusted Advisor.


- Join Date
- Apr 2011
- Location
- Newcastle Upon tyne
- Posts
- 6,116
- Thanks
- 306
- Thanked 779 Times in 753 Posts
Re: Main 24 HE burner failure
Are you getting a spark tonyacktar? and lights flashing? ...... you've described some of the process the boiler goes through but haven't mentioned whether it locks out and what indicator is showing?
"Put your hand on a hot stove for a minute, and it seems like an hour. Sit with a pretty girl for an hour, and it seems like a minute. THAT'S relativity." Albert Einstein
-
19-10-2011 #4Plumbers Arms member

- Join Date
- Sep 2011
- Location
- SE London
- Posts
- 540
- Thanks
- 9
- Thanked 29 Times in 28 Posts
Re: Main 24 HE burner failure
fault code E133?
-
19-10-2011 #5uɐɯ sɐƃ moderator



- Join Date
- Jan 2010
- Location
- maesteg,south wales
- Posts
- 13,567
- Thanks
- 836
- Thanked 1,284 Times in 1,225 Posts
Re: Main 24 HE burner failure
band a or b they are mechanically different,and have you checked for reversed polarity
GASMAN
fear keeps you alive
fearless gets you killed
IMPORTANT: Carbon Monoxide can be produced when ANY fuel is burnt, including oil, gas, wood and coal.
GSR?want gas safety or boiler repair advice?we will check out that your genuine via the gas safe website,so please dont be offended when we ask for your details
diyers,potchers,odd job people and have a go heroes need not apply
BAXI/POTTERTON INSTALLER/SERVICE ENGINEER
land rover equipped,you can go faster,i can go anywhere
-
19-10-2011 #6Plumbers Arms member

- Join Date
- Jul 2009
- Location
- Liverpool
- Posts
- 171
- Thanks
- 0
- Thanked 31 Times in 30 Posts
-
19-10-2011 #7Plumbers Arms member

- Join Date
- Jul 2009
- Location
- Liverpool
- Posts
- 171
- Thanks
- 0
- Thanked 31 Times in 30 Posts
-
19-10-2011 #8uɐɯ sɐƃ moderator



- Join Date
- Jan 2010
- Location
- maesteg,south wales
- Posts
- 13,567
- Thanks
- 836
- Thanked 1,284 Times in 1,225 Posts
Re: Main 24 HE burner failure
well i have not come across that,2 reasons why pcb,s go on this boiler
1,halfwits who reverse the polarity then wonder why the boiler keeps going to flame failure
2,water leaks from the heat exchanger o rings if over pressured ,but this will see off a 105 instant with the Siemens pcb but on main 24/30 he with the Honeywell pcb you have a chance of drying it out and saving it....sometimes other than that they rarely have pcb failure this is the reason i asked the op if its a band a or b is because if its a band b he may have aps failureGASMAN
fear keeps you alive
fearless gets you killed
IMPORTANT: Carbon Monoxide can be produced when ANY fuel is burnt, including oil, gas, wood and coal.
GSR?want gas safety or boiler repair advice?we will check out that your genuine via the gas safe website,so please dont be offended when we ask for your details
diyers,potchers,odd job people and have a go heroes need not apply
BAXI/POTTERTON INSTALLER/SERVICE ENGINEER
land rover equipped,you can go faster,i can go anywhere
-
20-10-2011 #9Plumbers Arms member

- Join Date
- Sep 2011
- Location
- SE London
- Posts
- 540
- Thanks
- 9
- Thanked 29 Times in 28 Posts
Re: Main 24 HE burner failure
well went to a job with a engineer, and he couldnt couldnt figure it out, it was a new install we had been called to, the guy that installed it was on holiday(dont ask), and run all checks e.t.c, so rang up the guy the customer bought it from and he was like do this and that blah blah blah, and then in the end he was like well ive had a couple of complaints about these exact make same problem and then he goes manufacturers fault on a bunch of them, but then there was me thinking, while my engineer mate was on the phone and i took the gas pipe fitting of the elbow to the boiler and purged the pipework for atleast 5 Minz ( i fink), and all i could smell was air not gas so i was like :S :S :S :S :S :S,(engineer not even looking at me lol), and then i smelt gas properly so connected it all back up and it fired perfectly, what it was, was like 32mm PE pipe had been used for the run outside (obviousely) and then 28 inside reduced to 22mm to the boiler, so all it needed was a good purge volume which i worked out and was fine, Engineer face was like :|, o what a good day he evn brought me 3 pints after work for that.
-
20-10-2011 #10Plumbers Arms member

- Join Date
- Jul 2009
- Location
- Liverpool
- Posts
- 171
- Thanks
- 0
- Thanked 31 Times in 30 Posts
-
20-10-2011 #11Plumbers Arms member

- Join Date
- Sep 2011
- Location
- SE London
- Posts
- 540
- Thanks
- 9
- Thanked 29 Times in 28 Posts
Re: Main 24 HE burner failure
and i cant wait till all this revision is done and im doing my ACS then i will be sitting down with 5 pints of stella and a bottle of famous G on that friday for sure.
-
20-10-2011 #12
Re: Main 24 HE burner failure
yea check polarity, first of all, turn spur on and boiler off and see if you have 240 at the live
For a premier service in Telford and surrounding areas
boiler,installation,servicing,landlords Certs
breakdowns,plumbing and gas work
www.firstcallgasandheating.co.uk
Similar Threads
-
Main 24he flame failure light perminatly on
By david bateman in forum Central Heating ForumReplies: 16Last Post: 17-07-2011, 01:00 AM -
glow worm ultimate 100ff - main burner lights and shuts off
By Centralheatking in forum Central Heating ForumReplies: 3Last Post: 13-07-2011, 09:55 PM -
Ideal Icos HE 18 Burner Box Failure
By willing2learn in forum Gas Safe Register Forum - Public ForumReplies: 11Last Post: 06-04-2011, 10:17 PM -
Main 24HE flame failure
By dc84 in forum Central Heating ForumReplies: 10Last Post: 26-12-2010, 02:04 PM


Reply With Quote










nursery taps keep coming loose.....
8 Minutes Ago in Plumbing Forum