    Default Problem with Ideal Concord CX

    Hi all, I'm having problems with my boiler.

    It fires up fine, will run for about 30 mins then all gas will cut off causing the burners and pilot to go out. Which I assume is the high temp stat doing its job? What I need to know is why is it over heating?

    I have a feeling the themostat isn't working. When you turn the dial, now matter what setting you have it on (1-6) the burners still 'run' the same. I'm assuming when the boiler reaches the temp setting its set at, the thermostat SHOULD turn off the burners and leave the pilot on before the high temp stat has a chance to shut it down? Would this be a faulty potentiometer or could it be the sensor? Or both?

    Any help appreciated!

  2. #2
    UK Plumbersforums Trusted Advisor.

    diamondgas's Avatar
    Join Date
    Apr 2011
    Location
    Newcastle Upon tyne
    Posts
    6,973
    Thanks
    366
    Thanked 926 Times in 899 Posts

    Default Re: Problem with Ideal Concord CX

    It's not just a dodgy pilot or t/cupl is it? 30 mins doesn't seem that long for a cx to get up to max temp...? What model is your boiler? What light is on as fault?
    "Put your hand on a hot stove for a minute, and it seems like an hour. Sit with a pretty girl for an hour, and it seems like a minute. THAT'S relativity." Albert Einstein

  3. #3
    uɐɯ sɐƃ moderator



    gas man's Avatar
    Join Date
    Jan 2010
    Location
    maesteg,south wales,land of MTB
    Posts
    18,661
    Thanks
    1,166
    Thanked 1,798 Times in 1,696 Posts

    Default Re: Problem with Ideal Concord CX

    call a gsr engineer it could be many things
    fear keeps you alive
    fearless gets you killed

    I have a banning hammer and I am not afraid to use it

  4. #4
    Member
    Join Date
    May 2011
    Posts
    6
    Thanks
    2
    Thanked 0 Times in 0 Posts

    Default Re: Problem with Ideal Concord CX

    Thankyou for replying. the thermocouple has recently been changed and is working fine( if electric is turned off the pilot will stay on) it is definately overheating as the overheat reset has to be pressed to re-light pilot. It may stay on for longer than 30 mins but it all depends on how long its been since it was last on!

    Its a concord cx340 and is ancient and has no lights!

  5. #5
    Plumbers Arms member
    villa_tom's Avatar
    Join Date
    Sep 2010
    Location
    The Midlands
    Posts
    4,254
    Thanks
    283
    Thanked 348 Times in 316 Posts

    Default Re: Problem with Ideal Concord CX

    Maybe time for an upgrade. As gasman says get a GSR engineer in to have a look.
    If you could read my mind I'd get punched in the face a lot

  6. #6
    UK Plumbersforums Trusted Advisor.

    diamondgas's Avatar
    Join Date
    Apr 2011
    Location
    Newcastle Upon tyne
    Posts
    6,973
    Thanks
    366
    Thanked 926 Times in 899 Posts

    Default Re: Problem with Ideal Concord CX

    Quote Originally Posted by RobbieHill View Post
    Thankyou for replying. the thermocouple has recently been changed and is working fine( if electric is turned off the pilot will stay on) it is definately overheating as the overheat reset has to be pressed to re-light pilot. It may stay on for longer than 30 mins but it all depends on how long its been since it was last on!

    Its a concord cx340 and is ancient and has no lights!
    Your first thoughts regarding temperature thermostat seems the more likely route to take but as gas man says ... call someone registered out to take a look, it ain't something you want to be messing with IHO
    "Put your hand on a hot stove for a minute, and it seems like an hour. Sit with a pretty girl for an hour, and it seems like a minute. THAT'S relativity." Albert Einstein

  7. The Following User Says Thank You to diamondgas For This Useful Post:


  8. #7
    Member
    Join Date
    May 2011
    Posts
    6
    Thanks
    2
    Thanked 0 Times in 0 Posts

    Default Re: Problem with Ideal Concord CX

    Hi, thanks for your help before. I can't afford to upgrade the system as I have been quoted 10k! I have changed the boiler thermostat and the sensor yet the burners will still not turn off. The thermostat 'clicks' as if it is sensing it has hit the set temperature but the burners continue to run until it overheats.

    Could it be the gas valve that controls the burners is jammed open? Or maybe a faulty PCB?

    Any help appreciated

  9. #8
    UK Plumbersforums Trusted Advisor.

    diamondgas's Avatar
    Join Date
    Apr 2011
    Location
    Newcastle Upon tyne
    Posts
    6,973
    Thanks
    366
    Thanked 926 Times in 899 Posts

    Default Re: Problem with Ideal Concord CX

    You could be on the money once again Robbie .... easiest way to check that out is to cut the power to the boiler (Not Literally) and see if the burner goes out straight away! I've known of gas valves to stick or open/close slowly. By turning off the power to the boiler you'll know whether the cause is electrical or mechanical.
    "Put your hand on a hot stove for a minute, and it seems like an hour. Sit with a pretty girl for an hour, and it seems like a minute. THAT'S relativity." Albert Einstein

  10. #9
    UK Plumbersforums Trusted Advisor.

    diamondgas's Avatar
    Join Date
    Apr 2011
    Location
    Newcastle Upon tyne
    Posts
    6,973
    Thanks
    366
    Thanked 926 Times in 899 Posts

    Default Re: Problem with Ideal Concord CX

    If it is the gas valve you will need to get someone qualified to replace it as there are perameters that will need checking/adjusting.
    "Put your hand on a hot stove for a minute, and it seems like an hour. Sit with a pretty girl for an hour, and it seems like a minute. THAT'S relativity." Albert Einstein

  11. #10
    Member
    Join Date
    May 2011
    Posts
    6
    Thanks
    2
    Thanked 0 Times in 0 Posts

    Default Re: Problem with Ideal Concord CX

    Thankyou for the quick reply! When the power to the boiler is turned off the burners go straight out ( this is how we have been turning it on and off without having to relight the pilot). Would this suggest it is the gas valve causing the problem?

  12. #11
    UK Plumbersforums Trusted Advisor.

    diamondgas's Avatar
    Join Date
    Apr 2011
    Location
    Newcastle Upon tyne
    Posts
    6,973
    Thanks
    366
    Thanked 926 Times in 899 Posts

    Default Re: Problem with Ideal Concord CX

    Less likely to be the gas valve, more likely one of the boards depending on how your boiler is set up. The thermostat should interrupt the power supply to the gas valve when shut off. What your describing seems to indicate that this is not happening. Possibly a fused relay on the board, but that's a guess! You'll need to get someone familiar with your boiler, it's a commercial appliance, to trace the cause.
    "Put your hand on a hot stove for a minute, and it seems like an hour. Sit with a pretty girl for an hour, and it seems like a minute. THAT'S relativity." Albert Einstein

  13. The Following User Says Thank You to diamondgas For This Useful Post:


  14. #12
    Member
    Join Date
    May 2011
    Posts
    6
    Thanks
    2
    Thanked 0 Times in 0 Posts

    Default Re: Problem with Ideal Concord CX

    Thankyou once again, ive ordered 2 new boards will see how I get on with those.

Everybody loves a good deal: Deals and Discounts on Dozens of Powertools!
Everybody loves a good deal: Deals and Discounts on Dozens of Powertools!

Similar Threads

  1. Ideal Concord WRS
    By willing2learn in forum Gas Safe Register Forum - Public Forum
    Replies: 9
    Last Post: 02-03-2016, 10:47 PM
  2. Looking for experience
    By Varley in forum Plumbing Forum
    Replies: 2
    Last Post: 16-06-2014, 11:17 PM
  3. Ideal concord CX 10e replacment
    By Petefinny in forum Gas Safe Register Forum - Public Forum
    Replies: 7
    Last Post: 11-03-2013, 08:15 PM
  4. Ideal concord 'c' 140
    By lewisplumber in forum Gas Safe Register Forum - Public Forum
    Replies: 13
    Last Post: 25-11-2012, 11:49 PM
  5. Ideal Concord WRS 240B
    By sdsparks in forum Central Heating Forum
    Replies: 6
    Last Post: 20-09-2012, 10:03 PM
  6. Ideal Concord CX possible leaking!
    By Dan the plumber in forum Central Heating Forum
    Replies: 10
    Last Post: 01-05-2012, 09:25 AM
  7. Ideal concord CXA 50 not loghting
    By Ryster in forum Gas Safe Register Forum - Public Forum
    Replies: 0
    Last Post: 20-09-2011, 11:35 PM
  8. old ideal concord c260
    By krav965 in forum Plumbing Forum
    Replies: 1
    Last Post: 08-02-2011, 07:07 PM

Visitors found this page by searching for:

ideal concord cxa overheat

ideal concord cx

ideal concord cx 340 manual

how to turn on ideal cxa

ideal concord cxa installation manual

Tags for this Thread


Try our Talk Electrician Forum and our popular Tilers Forums for more free advice from professional tradesmen.
Tens of thousands of tradesmen and over 2 million combined posts.


Plumbers Forums is a community-driven forum shared between all members.