fused spur

Discuss fused spur in the Central Heating Forum at Plumbers Forums; We changed a combi for a new main a few weeks ago, BG have been out and say they will not take it on as the main switch is a ...
  1. #1
    erj
    erj is offline
    Steady Plumbing Forum Contributor
    Join Date
    Dec 2010
    Posts
    198
    Thanks
    4
    Thanked 17 Times in 17 Posts

    Default fused spur

    We changed a combi for a new main a few weeks ago, BG have been out and say they will not take it on as the main switch is a 13 amp plug in to a socket, they say it has to be a fused spur, who is right?


  2. #2
    UK Plumbersforums Trusted Advisor.

    villa_tom's Avatar
    Join Date
    Sep 2010
    Location
    The Midlands
    Posts
    3,447
    Thanks
    230
    Thanked 261 Times in 241 Posts

    Default Re: fused spur

    They do like it to be a fused spur. And to be fair its only meant to be a temp fix running off a plug. Plus all boilers need to be ran off 3amp not 13amp

  3. If you could read my mind I'd get punched in the face a lot

  4. #3
    Steady Plumbing Forum Contributor
    Join Date
    Nov 2010
    Location
    Bexhill, East Sussex
    Posts
    112
    Thanks
    5
    Thanked 16 Times in 16 Posts

    Default Re: fused spur

    Fused spur as its a permanently fitted electrical appliance and 3 amp rated fuse.

  5. #4
    Top Plumbing Forum Contributor
    Join Date
    Jun 2010
    Location
    Cumberland
    Posts
    975
    Thanks
    11
    Thanked 86 Times in 82 Posts

    Default Re: fused spur

    3 amp plug with unswitched socket is fine. I prefer spur.

  6. #5
    Plumbing Forum Contributor
    Join Date
    Mar 2009
    Posts
    65
    Thanks
    0
    Thanked 5 Times in 5 Posts

    Default Re: fused spur

    Vaillant instructions say:
    "Connection to the mains supply shall be made via a fused 3 pin plug to an unswitched shuttered socket, both complying with the
    requirements of BS 1363. (Alternatively, connection may be made via a 3 A fused double pole isolator having a contact separation of at least 3 mm in all poles and supplying the boiler and controls only)."
    So I suppose that BG would ignore the manufacturers instructions. What do the Main instructions say? At least you could confirm with your customer that you've followed the MIs...

  7. #6
    uɐɯ sɐƃ moderator


    gas man's Avatar
    Join Date
    Jan 2010
    Location
    maesteg,south wales
    Posts
    13,349
    Thanks
    827
    Thanked 1,267 Times in 1,210 Posts

    Default Re: fused spur

    you should have a 3 amp double pole fused spur,but i prefer a 3 amp plug,you cant get killed if its unplugged

    GASMAN
    fear keeps you alive
    fearless gets you killed

    IMPOR
    TANT: Carbon Monoxide can be produced when ANY fuel is burnt, including oil, gas, wood and coal.
    GSR?want gas safety or boiler repair advice?we will check out that your genuine via the gas safe website,so please dont be offended when we ask for your details
    diyers,potchers,odd job people and have a go heroes need not apply
    ​BAXI/POTTERTON INSTALLER/SERVICE ENGINEER
    ​ land rover equipped,you can go faster,i can go anywhere


  8. #7
    Top Plumbing Forum Contributor
    Join Date
    Jun 2010
    Location
    Cumberland
    Posts
    975
    Thanks
    11
    Thanked 86 Times in 82 Posts

    Default Re: fused spur

    That was the logic we always followed Gas Man. Now I think spurs look neater, that said I do occasionaly use a plug always have a box of 3 amp plugs in the van

  9. #8
    Plumbing Forum Contributor
    Join Date
    Sep 2010
    Posts
    53
    Thanks
    2
    Thanked 6 Times in 6 Posts

    Default Re: fused spur

    it used to be that corgi required switch fused spurs only.
    then out came part P and plumber not on part P register - corgi then said ok plug and socket fitted with a 3 amp fuse is ok.(bypasses part P)
    now 17th edition reg 537.3.2.6 states
    A plug and socket-outlet or similar device of rating not exceeding 16 amps may be used as a device for switching off for mechanical maintenance.
    but reg 537.4.2.8 states
    A plug and socket -outlet or similar device shall not be selected as a device for emergency switching.
    confusing well yes when i bought the regs it said £15 on the front and £51 on the back - and it never got any less confusing in the middle.
    hope this helps cheers

  10. #9
    Steady Plumbing Forum Contributor
    Join Date
    Sep 2010
    Posts
    154
    Thanks
    2
    Thanked 23 Times in 21 Posts

    Default Re: fused spur

    Sounds like an excuse for BG not to take a main on contract

  11. #10
    SUPER MODERATOR


    REDSAW's Avatar
    Join Date
    Jan 2009
    Location
    sherrif county
    Posts
    9,101
    Thanks
    241
    Thanked 529 Times in 492 Posts

    Default Re: fused spur

    Quote Originally Posted by washer View Post
    Sounds like an excuse for BG not to take a main on contract
    i agree, nowt wrong with a 3amp plug, just a matter of choice and circumstance when installing. imo

    baxi main.

    NOTE: The method of connection to the
    electricity supply must facilitate complete electrical
    isolation of the appliance.

    Connection may be via a fused double-pole isolator
    with a contact separation of at least 3mm in all
    poles and servicing the boiler and system controls
    only.
    Last edited by REDSAW; 21-02-2011 at 11:22 PM.
    ¡ƃuıɥʇou ʍouʞ ı˙˙˙ɹǝqɯǝɯǝɹ puɐ
    ˙ʎlddɐ ʇou pǝǝu sǝoɹǝɥ oƃ ɐ ǝʌɐɥ puɐ ǝldoǝd qoɾ ppo `sɹǝ,ʎıp ˙slıɐʇǝp ɹnoʎ ɹoɟ ʞsɐ ǝʍ uǝɥʍ pǝpuǝɟɟo ǝq ʇ,uop ǝsɐǝld os `ǝʇısqǝʍ ǝɟɐs sɐƃ ǝɥʇ ɐıʌ ǝuınuǝƃ ǝɹ,noʎ ʇɐɥʇ ʇno ʞɔǝɥɔ llıʍ ǝʍ ¿ǝɔıʌpɐ ɹıɐdǝɹ ɹǝlıoq ɹo ʎʇǝɟɐs sɐƃ ʇuɐʍ noʎ op
    ¿ʞɹoʍ sɐƃ

    ˙lɐoɔ puɐ pooʍ `sɐƃ `lıo ƃuıpnlɔuı `ʇuɹnq sı lǝnɟ ʎuɐ uǝɥʍ pǝɔnpoɹd ǝq uɐɔ ǝpıxouoɯ uoqɹɐɔ :ʇuɐʇɹodɯı


  12. #11
    Plumbers Arms member

    Join Date
    Apr 2010
    Posts
    1,399
    Thanks
    61
    Thanked 167 Times in 157 Posts

    Default Re: fused spur

    At the end of the day the manufacturer is king here. If they specify a separate 3 amp fused spur must be used in the MI's then it is not installed correctly and BG are within their rights to refuse to cover.

  13. #12
    UK Plumbersforums Trusted Advisor.


    Join Date
    Nov 2008
    Location
    east london
    Posts
    6,666
    Thanks
    9
    Thanked 384 Times in 372 Posts

    Default Re: fused spur

    i prefer a plug easier to test meter across the pins tells you if theres a sort to earth without opening the boiler and when its out its of no question

  14. #13
    UK Plumbersforums Trusted Advisor.

    tamz's Avatar
    Join Date
    Apr 2010
    Location
    Scotland
    Posts
    9,363
    Thanks
    281
    Thanked 1,178 Times in 1,045 Posts

    Default Re: fused spur

    It is not and never has been a requirement to be fed solely from a fused spur. Unswitched sockets are fine. Switched are NOT. A plug face can be fused down just the same as a FCU.

    Just BG making up their own rules but as they are the ones offering the service they can state what they want.

    Spurs are neater and look more professional i suppose but you get more than a 3mm separation by pulling the plug. Seen too many spurs wired with commoned neutrals.

    Btw why would a customer want to get BG cover on a newly fitted boiler?

  15. #14
    erj
    erj is offline
    Steady Plumbing Forum Contributor
    Join Date
    Dec 2010
    Posts
    198
    Thanks
    4
    Thanked 17 Times in 17 Posts

    Default Re: fused spur

    Thanks for all the replys, yes the plug has a 3 amp fuse in, and the old boiler was wired this way, so we can ague al day both have good and bad pionts.

Similar Threads

  1. spur or own elec supply to boiler
    By desrob in forum Gas Safe Register Forum - Public Forum
    Replies: 22
    Last Post: 16-01-2011, 11:13 PM
  2. Replies: 14
    Last Post: 08-12-2010, 07:12 PM

Visitors found this page by searching for:

3 amp double pole fused spur

central heating fused spur

16 amp fused spur

3 amp fused spur

16amp fused spurfused spur ratinghow to wire a double pole fused spur

Tags for this Thread

Plumbers Forums is a Trading Style of Untold Developments Ltd. Search Engine Optimisation, Web Development and Online Marketing for the UK.