Plumbing & Plumbers Forum - Expansion vessel.

Expansion vessel.

Discuss Expansion vessel. in the Central Heating Forum at Plumbers Forums; Hi. I have a problem with my expansion vessel as the system pressure keeps rising and keeps blowing the pressure reief valve,I have read if I depress the valve in ...
  1. #1
    New to Plumbing Forum
    Join Date
    Dec 2010
    Posts
    6
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Expansion vessel.

    Hi.
    I have a problem with my expansion vessel as the system pressure keeps rising and keeps blowing the pressure reief valve,I have read if I depress the valve in the top of the expansion vessel and water comes out then it means the vessel is broken.

    What I would like to know is if the expansion vessel is faulty can I fit an external larger capacity vessel of 12 litres,I have an 8 litre vessel at the minute,the reason being is I have 8 rads with one of the rads being a large double.

    If it is ok to fit a larger capacity vessel would I need to upgrade the pressure relief valve from 3 bar to 6 bar to which the maximum pressure of the new vessel would be.

    Thanks in advance.
    Lofty.


  2. #2
    Plumbing Forum Contributor
    Join Date
    Feb 2010
    Posts
    53
    Thanks
    0
    Thanked 9 Times in 8 Posts

    Default Re: Expansion vessel.

    Lofty - check your top up valve isn't open?


  3. #3
    Plumbers Arms member
    Blake's Avatar
    Join Date
    Jun 2008
    Location
    Nottingham
    Posts
    1,064
    Thanks
    20
    Thanked 107 Times in 98 Posts

    Default Re: Expansion vessel.

    As above first. If not first decide if it is the EV by isolating the boiler, draining and then checking the pressure in the EV.

    If you fitted a new EV, you do not need to upgrade the PRV, the boiler needs it to be a 3 bar for safety reasons.

  4. #4
    Plumbers Arms member

    Join Date
    May 2009
    Posts
    7,302
    Thanks
    218
    Thanked 683 Times in 604 Posts

    Default Re: Expansion vessel.

    Never every increase the pressure release valve 3 bar activation point for the system it is designed for, the pressure release valve does not have a 3 bar release just for the protection of the expansion vessel, it is for the protection of boiler and all of the system and also you should never be near a units or parts maximum pressure, you may well find the expansion vessel fitted now ,also has a 6 bar max pressure or greater

    To think about putting on a 6 Bar replacement p/r valve is a very dangerous thing to do and could cause serious injury to someone

    You can fit another ,bigger expansion vessel externally near the boiler, the bigger size ,in fact will decrease the expansion within the system, thus system pressure when hot, so in theory ,you could decrease the p/r activation point

    Back to problem, is the system pressure going up when system cold or when system being heated/hot, you may just need to just pump up/re prime existing expansion vessel to 1 bar,if pressure increasing when heated or if increasing when cold you have another problem
    Last edited by Puddle; 26-12-2010 at 08:46 PM.

  5. #5
    Plumbers Arms member
    mikegas's Avatar
    Join Date
    Feb 2010
    Posts
    1,213
    Thanks
    159
    Thanked 166 Times in 155 Posts

    Default Re: Expansion vessel.

    I was told that as a temp fix for a faulty expansion vessel you can drop the system and vent all rads except 1 and this rad will act as an expansion vessel, can anybody tell me if this would work?

  6. #6
    Plumbers Arms member
    quality's Avatar
    Join Date
    Sep 2009
    Location
    South Yorkshire
    Posts
    2,449
    Thanks
    49
    Thanked 205 Times in 199 Posts

    Default Re: Expansion vessel.

    Yes it will but it is only a temp measure and it must be a large radiator

  7. The Following User Says Thank You to quality For This Useful Post:

    mikegas (26-12-2010)

  8. #7
    New to Plumbing Forum
    Join Date
    Dec 2010
    Posts
    6
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Expansion vessel.

    Thanks for the replies.

    What happened was when the boiler was heating,the prv was dribbling,so I changed the prv (3 bar) and the same thing happened later on that day with the new prv fitted,the reason I noticed was that the system pressure fell from 1 bar to .8 of a bar,so I topped the system up to 1 bar and switched the boiler on to heating and the new prv started dribbling again when it was at the set tempreture.

    The system pressure gauge does not show bar when it is on heating.

    I was going to test the pressure in the Ev,I have to buy a pressure gauge,it needs to be .5 of a bar,by top up valve do you mean the valve on top of the Ev,the cap is on the valve.

    If I close the flow and return on the heating and open the drain cock will it empty the Ev.



    I wouldn't have uprated the prv without asking as I know they are fitted for safety reasons.

    Thanks.
    Lofty.
    Last edited by lofty531135; 26-12-2010 at 10:35 PM.

  9. #8
    Top Plumbing Forum Contributor
    Join Date
    Aug 2010
    Posts
    426
    Thanks
    9
    Thanked 38 Times in 38 Posts

    Default Re: Expansion vessel.

    Quote Originally Posted by lofty531135 View Post
    Hi.,I have read if I depress the valve in the top of the expansion vessel and water comes out then it means the vessel is broken.
    To answer your question, yes that sounds like the diaphragm in the EV has failed. As others have said, a larger EV will be fine and leave PRV at original setting.

  10. #9
    Steady Plumbing Forum Contributor spanner's Avatar
    Join Date
    Aug 2010
    Location
    Archway, London UK
    Posts
    238
    Thanks
    18
    Thanked 9 Times in 9 Posts

    Default Re: Expansion vessel.

    yep would work lowest radwell!!!!!!!!!!!
    If it aint broke don't try to fixit

  11. #10
    uɐɯ sɐƃ moderator


    gas man's Avatar
    Join Date
    Jan 2010
    Location
    maesteg,south wales
    Posts
    13,564
    Thanks
    836
    Thanked 1,284 Times in 1,225 Posts

    Default Re: Expansion vessel.

    Quote Originally Posted by mikegas View Post
    I was told that as a temp fix for a faulty expansion vessel you can drop the system and vent all rads except 1 and this rad will act as an expansion vessel, can anybody tell me if this would work?
    yes this will work on a large rad as a temp measure

    GASMAN
    fear keeps you alive
    fearless gets you killed

    IMPOR
    TANT: Carbon Monoxide can be produced when ANY fuel is burnt, including oil, gas, wood and coal.
    GSR?want gas safety or boiler repair advice?we will check out that your genuine via the gas safe website,so please dont be offended when we ask for your details
    diyers,potchers,odd job people and have a go heroes need not apply
    ​BAXI/POTTERTON INSTALLER/SERVICE ENGINEER
    ​ land rover equipped,you can go faster,i can go anywhere


Similar Threads

  1. Expansion vessel sizing
    By Dannypipe in forum Plumbing Forum
    Replies: 2
    Last Post: 04-12-2012, 09:11 AM
  2. Expansion vessel???
    By professorplumb in forum Gas Safe Register Forum - Public Forum
    Replies: 4
    Last Post: 05-12-2010, 10:26 AM
  3. Expansion Vessel Question
    By Quiz in forum Plumbing Forum
    Replies: 1
    Last Post: 17-09-2009, 02:03 PM
  4. Expansion Vessel
    By stephens in forum Central Heating Forum
    Replies: 6
    Last Post: 10-05-2009, 11:26 PM

Visitors found this page by searching for:

repair expansion vessel