Discuss Expansion vessel. in the Central Heating Forum at Plumbers Forums; Hi. I have a problem with my expansion vessel as the system pressure keeps rising and keeps blowing the pressure reief valve,I have read if I depress the valve in ...-
26-12-2010 #1New to Plumbing Forum
- Join Date
- Dec 2010
- Posts
- 6
- Thanks
- 0
- Thanked 0 Times in 0 Posts
Expansion vessel.
Hi.
I have a problem with my expansion vessel as the system pressure keeps rising and keeps blowing the pressure reief valve,I have read if I depress the valve in the top of the expansion vessel and water comes out then it means the vessel is broken.
What I would like to know is if the expansion vessel is faulty can I fit an external larger capacity vessel of 12 litres,I have an 8 litre vessel at the minute,the reason being is I have 8 rads with one of the rads being a large double.
If it is ok to fit a larger capacity vessel would I need to upgrade the pressure relief valve from 3 bar to 6 bar to which the maximum pressure of the new vessel would be.
Thanks in advance.
Lofty.
-
26-12-2010 #2Plumbing Forum Contributor
- Join Date
- Feb 2010
- Posts
- 53
- Thanks
- 0
- Thanked 9 Times in 8 Posts
Re: Expansion vessel.
Lofty - check your top up valve isn't open?
-
26-12-2010 #3Plumbers Arms member

- Join Date
- Jun 2008
- Location
- Nottingham
- Posts
- 1,064
- Thanks
- 20
- Thanked 107 Times in 98 Posts
Re: Expansion vessel.
As above first. If not first decide if it is the EV by isolating the boiler, draining and then checking the pressure in the EV.
If you fitted a new EV, you do not need to upgrade the PRV, the boiler needs it to be a 3 bar for safety reasons.
-
26-12-2010 #4Plumbers Arms member

- Join Date
- May 2009
- Posts
- 7,302
- Thanks
- 218
- Thanked 683 Times in 604 Posts
Re: Expansion vessel.
Never every increase the pressure release valve 3 bar activation point for the system it is designed for, the pressure release valve does not have a 3 bar release just for the protection of the expansion vessel, it is for the protection of boiler and all of the system and also you should never be near a units or parts maximum pressure, you may well find the expansion vessel fitted now ,also has a 6 bar max pressure or greater
To think about putting on a 6 Bar replacement p/r valve is a very dangerous thing to do and could cause serious injury to someone
You can fit another ,bigger expansion vessel externally near the boiler, the bigger size ,in fact will decrease the expansion within the system, thus system pressure when hot, so in theory ,you could decrease the p/r activation point
Back to problem, is the system pressure going up when system cold or when system being heated/hot, you may just need to just pump up/re prime existing expansion vessel to 1 bar,if pressure increasing when heated or if increasing when cold you have another problemLast edited by Puddle; 26-12-2010 at 08:46 PM.
-
26-12-2010 #5
Re: Expansion vessel.
I was told that as a temp fix for a faulty expansion vessel you can drop the system and vent all rads except 1 and this rad will act as an expansion vessel, can anybody tell me if this would work?
-
26-12-2010 #6Plumbers Arms member

- Join Date
- Sep 2009
- Location
- South Yorkshire
- Posts
- 2,449
- Thanks
- 49
- Thanked 205 Times in 199 Posts
Re: Expansion vessel.
Yes it will but it is only a temp measure and it must be a large radiator
-
The Following User Says Thank You to quality For This Useful Post:
mikegas (26-12-2010)
-
26-12-2010 #7New to Plumbing Forum
- Join Date
- Dec 2010
- Posts
- 6
- Thanks
- 0
- Thanked 0 Times in 0 Posts
Re: Expansion vessel.
Thanks for the replies.
What happened was when the boiler was heating,the prv was dribbling,so I changed the prv (3 bar) and the same thing happened later on that day with the new prv fitted,the reason I noticed was that the system pressure fell from 1 bar to .8 of a bar,so I topped the system up to 1 bar and switched the boiler on to heating and the new prv started dribbling again when it was at the set tempreture.
The system pressure gauge does not show bar when it is on heating.
I was going to test the pressure in the Ev,I have to buy a pressure gauge,it needs to be .5 of a bar,by top up valve do you mean the valve on top of the Ev,the cap is on the valve.
If I close the flow and return on the heating and open the drain cock will it empty the Ev.
I wouldn't have uprated the prv without asking as I know they are fitted for safety reasons.
Thanks.
Lofty.Last edited by lofty531135; 26-12-2010 at 10:35 PM.
-
26-12-2010 #8Top Plumbing Forum Contributor
- Join Date
- Aug 2010
- Posts
- 426
- Thanks
- 9
- Thanked 38 Times in 38 Posts
-
27-12-2010 #9Steady Plumbing Forum Contributor
- Join Date
- Aug 2010
- Location
- Archway, London UK
- Posts
- 238
- Thanks
- 18
- Thanked 9 Times in 9 Posts
Re: Expansion vessel.
yep would work lowest radwell!!!!!!!!!!!
If it aint broke don't try to fixit

-
27-12-2010 #10uɐɯ sɐƃ moderator



- Join Date
- Jan 2010
- Location
- maesteg,south wales
- Posts
- 13,564
- Thanks
- 836
- Thanked 1,284 Times in 1,225 Posts
Re: Expansion vessel.
GASMAN
fear keeps you alive
fearless gets you killed
IMPORTANT: Carbon Monoxide can be produced when ANY fuel is burnt, including oil, gas, wood and coal.
GSR?want gas safety or boiler repair advice?we will check out that your genuine via the gas safe website,so please dont be offended when we ask for your details
diyers,potchers,odd job people and have a go heroes need not apply
BAXI/POTTERTON INSTALLER/SERVICE ENGINEER
land rover equipped,you can go faster,i can go anywhere
Similar Threads
-
Expansion vessel sizing
By Dannypipe in forum Plumbing ForumReplies: 2Last Post: 04-12-2012, 09:11 AM -
Expansion vessel???
By professorplumb in forum Gas Safe Register Forum - Public ForumReplies: 4Last Post: 05-12-2010, 10:26 AM -
Expansion Vessel Question
By Quiz in forum Plumbing ForumReplies: 1Last Post: 17-09-2009, 02:03 PM -
Expansion Vessel
By stephens in forum Central Heating ForumReplies: 6Last Post: 10-05-2009, 11:26 PM


Reply With Quote