Plumbing & Plumbers Forum - elp choosing a system, microbore?

elp choosing a system, microbore?

Discuss elp choosing a system, microbore? in the Central Heating Forum at Plumbers Forums; i live in a very old house, timber framed with wattle and daub walls. i cant chase pipes into the walls nor can they go under the floor boards. So ...
  1. #1
    Steady Plumbing Forum Contributor
    Join Date
    Jun 2009
    Posts
    188
    Thanks
    1
    Thanked 0 Times in 0 Posts

    Default elp choosing a system, microbore?

    i live in a very old house, timber framed with wattle and daub walls.
    i cant chase pipes into the walls nor can they go under the floor boards. So ive been thinking a micro bore system might be least intrusive? underfloor heating is also a no.
    So can anybody give me a run down on how a microbore system works? does it use a central manifold for instance? or is it just the run from a main flow and return to the rads that is micro bore?


  2. #2
    Plumbing Forum Contributor
    Join Date
    Nov 2010
    Posts
    50
    Thanks
    6
    Thanked 1 Time in 1 Post

    Default Re: elp choosing a system, microbore?

    I would try stay clear of micro-bore heating systems....i know if there installed right they can be ok...but later on they can cause a few blockages if not treat correct!iam not a big fan of them.you do have 2 manifolds one for the flow and one for the return.......have you considerd surface mounting the pipes and maybe some sort of boxing on the top?you can buy white boxing which clips over the pipe clips from any decent plumb department.....and you can wall paper over them even! just a though?


  3. #3
    Steady Plumbing Forum Contributor
    Join Date
    Jun 2009
    Posts
    188
    Thanks
    1
    Thanked 0 Times in 0 Posts

    Default Re: elp choosing a system, microbore?

    cheers Fabio, boxing them in isnt an option im afraid, the house is 500 years old and there isnt a straight edge or right angle in the place.
    if i ran a 22 mil flow and return the lenth of the house (3 bay/2 floors) and T'd off in 10 mil for each rad what is the longest 10mil run i can hope to achieve? is it 5 meters? or would i need to reduce down from 15mil?

  4. #4
    Plumbing Forum Contributor
    Join Date
    Nov 2010
    Posts
    50
    Thanks
    6
    Thanked 1 Time in 1 Post

    Default Re: elp choosing a system, microbore?

    How many radiators are you having on the system?what are the size of the rads? make sure you get a boiler with enough kw for what you want.

  5. #5
    Top Plumbing Forum Contributor
    Join Date
    Aug 2010
    Posts
    326
    Thanks
    18
    Thanked 13 Times in 12 Posts

    Default Re: elp choosing a system, microbore?

    if it is a pressurised system micro bore is good I know some on here will say no but trust me I have fitted thousands (or maybe hundreds lol) of heating systems some micro bore some half inch and never had a problem but in saying that this has always been full new systems from scratch so dont have info on wether you are tying into existing pipework for your new rads as existing stuff may be full of sludge (could power flush though).
    I f system is pressurised go with the microbore 10mm.

  6. #6
    Plumbers Arms member
    Blackcatgas's Avatar
    Join Date
    Oct 2009
    Location
    Nottingham
    Posts
    1,672
    Thanks
    57
    Thanked 132 Times in 121 Posts

    Default Re: elp choosing a system, microbore?

    Quote Originally Posted by plumbster3456 View Post
    if it is a pressurised system micro bore is good I know some on here will say no but trust me I have fitted thousands (or maybe hundreds lol) of heating systems some micro bore some half inch and never had a problem but in saying that this has always been full new systems from scratch so dont have info on wether you are tying into existing pipework for your new rads as existing stuff may be full of sludge (could power flush though).
    I f system is pressurised go with the microbore 10mm.
    I agree with plumbstar, Ive put in loads of the stuff, as long as its on a sealed system ie combi and kept topped up with loads of x100 inhibiter or similiar itl be ok, Ive done 5m+ runs of 10mm pipe and the rads have worked lovely, 1000mmx600mm doubles etc.
    Its never my first choice but can be made to work satisfactory.

  7. #7
    uɐɯ sɐƃ moderator


    gas man's Avatar
    Join Date
    Jan 2010
    Location
    maesteg,south wales
    Posts
    13,357
    Thanks
    829
    Thanked 1,267 Times in 1,210 Posts

    Default Re: elp choosing a system, microbore?

    nothing wrong with minibore all i have ever used is 10mm never had a problem its all down to correct installation

    GASMAN
    fear keeps you alive
    fearless gets you killed

    IMPOR
    TANT: Carbon Monoxide can be produced when ANY fuel is burnt, including oil, gas, wood and coal.
    GSR?want gas safety or boiler repair advice?we will check out that your genuine via the gas safe website,so please dont be offended when we ask for your details
    diyers,potchers,odd job people and have a go heroes need not apply
    ​BAXI/POTTERTON INSTALLER/SERVICE ENGINEER
    ​ land rover equipped,you can go faster,i can go anywhere


  8. #8
    Steady Plumbing Forum Contributor
    Join Date
    Jun 2009
    Posts
    188
    Thanks
    1
    Thanked 0 Times in 0 Posts

    Default Re: elp choosing a system, microbore?

    thanks guys, ive heard some horror stories about small bore systems but when i was plumbing up barratt houses we used 10mm pipe taken off 22mm flow and return and it all seemed to work fine.

    i will be using a mix of 15 mm copper and plastic downstairs as i can conceal some pipework and any surface mount will be 15mm copper purely for aesthetics, its the upstairs that i need to use a smaller bore pipe so i can tuck it away out of sight.

    so if i were to use 22mil flow and return from the boiler and take each rad off it the mix of 15mm and 10mm shouldnt be a problem? There will be 9 rads feeding off a single 22mil 10 meter f+r run, three of which need to be 10mm.

    its a new system , 30kw combi boiler and sealed system.

  9. #9
    Plumbers Arms member

    Join Date
    Apr 2010
    Posts
    1,399
    Thanks
    61
    Thanked 167 Times in 157 Posts

    Default Re: elp choosing a system, microbore?

    If you are using plastic for your heating runs make sure you use a decent barrier pipe.
    Run it 15/22mm as far as you can before reducing to the 10mm. Give a good few hot & cold flushes and as Blackcatgas mentioned, plenty inhibitor and you should have a good system.

  10. #10
    New to Plumbing Forum
    Join Date
    Nov 2010
    Posts
    2
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: elp choosing a system, microbore?

    I would not choose microbore and to be honest, I don't know why any would anyway. It is best left for a 10mm oil supply than running the stuff through your house. I would stick to using 22mm copper on your flow and return and branch down to 15mm for the rad feeds.
    Microbore comes in coils and it is very difficult to get clean straight lines for your plumbing work. You can get blockages with small bits of stubborn solder that won't flush out before commissioning. Don't use push fit plastic either, vermin just love to chew that stuff..!

  11. #11
    uɐɯ sɐƃ moderator


    gas man's Avatar
    Join Date
    Jan 2010
    Location
    maesteg,south wales
    Posts
    13,357
    Thanks
    829
    Thanked 1,267 Times in 1,210 Posts

    Default Re: elp choosing a system, microbore?

    Microbore comes in coils and it is very difficult to get clean straight lines for your plumbing work.
    depends how skilled you are
    Last edited by gas man; 13-11-2010 at 05:33 PM.

    GASMAN
    fear keeps you alive
    fearless gets you killed

    IMPOR
    TANT: Carbon Monoxide can be produced when ANY fuel is burnt, including oil, gas, wood and coal.
    GSR?want gas safety or boiler repair advice?we will check out that your genuine via the gas safe website,so please dont be offended when we ask for your details
    diyers,potchers,odd job people and have a go heroes need not apply
    ​BAXI/POTTERTON INSTALLER/SERVICE ENGINEER
    ​ land rover equipped,you can go faster,i can go anywhere


  12. #12
    Top Plumbing Forum Contributor
    Join Date
    Aug 2010
    Posts
    326
    Thanks
    18
    Thanked 13 Times in 12 Posts

    Default Re: elp choosing a system, microbore?

    Quote Originally Posted by gas man View Post
    microbore comes in coils and it is very difficult to get clean straight lines for your plumbing work.
    Depends how skilled you are
    exactly

  13. #13
    fuzzy
    Guest

    Default Re: elp choosing a system, microbore?

    Quote Originally Posted by that bloke. View Post
    i live in a very old house, timber framed with wattle and daub walls.
    i cant chase pipes into the walls nor can they go under the floor boards. So ive been thinking a micro bore system might be least intrusive? underfloor heating is also a no.
    So can anybody give me a run down on how a microbore system works? does it use a central manifold for instance? or is it just the run from a main flow and return to the rads that is micro bore?
    yes it works do you know your heat losses?

  14. #14
    Steady Plumbing Forum Contributor
    Join Date
    Jun 2009
    Posts
    188
    Thanks
    1
    Thanked 0 Times in 0 Posts

    Default Re: elp choosing a system, microbore?

    dont know the heat losses yet, i can try to calculate it but it wont be anywhere near close. the house is timber framed with wattle and daub infill's, thatched roof vaulted inside so only the thatch as insulating , the upper floor has no ceiling below , just beams with wide oak floor boards nailed ontop , single glazing, no sealed doors just ill fitting ledge doors, 3 walls are external,exterior rendered in daub, the list goes on so how do you calculate heat loss on an old tea bag like this?

  15. #15
    uɐɯ sɐƃ moderator


    gas man's Avatar
    Join Date
    Jan 2010
    Location
    maesteg,south wales
    Posts
    13,357
    Thanks
    829
    Thanked 1,267 Times in 1,210 Posts

    Default Re: elp choosing a system, microbore?

    Quote Originally Posted by that bloke. View Post
    dont know the heat losses yet, i can try to calculate it but it wont be anywhere near close. The house is timber framed with wattle and daub infill's, thatched roof vaulted inside so only the thatch as insulating , the upper floor has no ceiling below , just beams with wide oak floor boards nailed ontop , single glazing, no sealed doors just ill fitting ledge doors, 3 walls are external,exterior rendered in daub, the list goes on so how do you calculate heat loss on an old tea bag like this?
    heatloss about a million btus lol

    GASMAN
    fear keeps you alive
    fearless gets you killed

    IMPOR
    TANT: Carbon Monoxide can be produced when ANY fuel is burnt, including oil, gas, wood and coal.
    GSR?want gas safety or boiler repair advice?we will check out that your genuine via the gas safe website,so please dont be offended when we ask for your details
    diyers,potchers,odd job people and have a go heroes need not apply
    ​BAXI/POTTERTON INSTALLER/SERVICE ENGINEER
    ​ land rover equipped,you can go faster,i can go anywhere


Page 1 of 2 12 LastLast

Similar Threads

  1. Microbore...yay or nay?
    By mrlennie in forum Central Heating Forum
    Replies: 37
    Last Post: 28-02-2011, 06:42 PM
  2. Replies: 2
    Last Post: 01-11-2010, 09:35 PM
  3. Replies: 4
    Last Post: 04-10-2010, 08:15 PM
  4. Advice on choosing a combi boiler please
    By chubsy in forum Central Heating Forum
    Replies: 17
    Last Post: 21-02-2010, 02:25 PM
  5. where can I drain microbore open system
    By mscg in forum Plumbing Forum
    Replies: 6
    Last Post: 07-08-2009, 09:02 PM

Visitors found this page by searching for:

small bore underfloor heating

small bore under floor heating

what is the largest radiator can be run off 10 mil pipe

microbore flow problems

small bore heating

mini bore heating system

small bore central heating systems