Plumbing & Plumbers Forum - Salus RT500RF Thermostat not controlling boiler?
Like Tree4Likes

Salus RT500RF Thermostat not controlling boiler?

Discuss Salus RT500RF Thermostat not controlling boiler? at UK Plumbers Forums; Hi. I have just had a Gloworm 30 CXI Ultracom 2 installed with a Salus RT500RF Wireless Programmable Thermostat to control temperature. All my radiators have TRVs and I have ...
  1. #1
    Member
    Join Date
    Sep 2010
    Posts
    5
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Salus RT500RF Thermostat not controlling boiler?

    Hi. I have just had a Gloworm 30 CXI Ultracom 2 installed with a Salus RT500RF Wireless Programmable Thermostat to control temperature. All my radiators have TRVs and I have noticed that the Salus is not switching the boiler off or stopping flow to the rads when it should be. Eg at 10pm I am asking to it maintain a room temp of 10c, the Salus thermometer is reading the room temp circa 22c after the heating has been on, but the boiler is still in central heating mode and the rads hot all night.

    I have tested the device to make sure the transmitter is working with the receiver and the green light on the receiver does come on when a request to raise the temperature is sent, but I have never seen the green light on when I have either manually asked to drop the temp or when the program changes to say a "maintain 10c cycle" eg overnight.

    I have seen on the internet that these things are notoriously unreliable. Does anyone have any advice? Installer showed me it working so had no reason to doubt it worked? I would expect the central heating mode on the boiler to switch off when the room temp was being maintained well above the set level. Does this point to a communication problem with the Salus? Thanks in advance.

  2. #2
    Banned
    Join Date
    Aug 2009
    Posts
    1,512
    Thanks
    11
    Thanked 148 Times in 139 Posts

    Default Re: Salus RT500RF Thermostat not controlling boiler?

    Is there a TRV on the rad in the room where the Salus is located? If so, you should either set the TRV to maximum or remove the head from the TRV - no water will come out.

    Have you used all five time/temperature settings on the Salus? You must set no five to be the overnight one, even if it means setting two the same.

    Does the boiler go out if you turn the temperature down to minimum and relight if you turn it up to max?

  3. #3
    uɐɯ sɐƃ moderator



    gas man's Avatar
    Join Date
    Jan 2010
    Location
    maesteg,south wales,land of MTB
    Posts
    18,737
    Thanks
    1,175
    Thanked 1,795 Times in 1,696 Posts

    Default Re: Salus RT500RF Thermostat not controlling boiler?

    salus products are unreliable,used there rf stats nothing but problems only fit honeywell now
    gassafe and Darren Jackson like this.
    fear keeps you alive
    fearless gets you killed

    I have a banning hammer and I am not afraid to use it

  4. #4
    Member
    Join Date
    Sep 2010
    Posts
    5
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Salus RT500RF Thermostat not controlling boiler?

    Thanks for the responses. I have set all 5 cycles on the thermostat. TRV are on max setting in the living room where I keep the thermostat. At 10pm the thermostat will hit the 5th cycle and should tell the boiler to maintain a room temp of 5c. I am currently in the living room with the rads very hot to the touch and a reading of 22.5c so I would expect the boiler to switch off the CH mode and the heat to leave my rads. I am actually going to go and watch the boiler at 10pm to see what/ if anything happens. If my rads are still boiling hot at 11 then I know the Salus thermostat is bloody useless!!!

    Is there any chance that the TRV are actually controlling the boiler ie by keeping them on max they are continually trying to regulate the room temp? ( I think max is 25c+) I would have thought the Salus should be the one dictating what the boiler should do though otherwise is it impossible to have timed CH. Cheers.

    @Doitmyself - Do you mean turn the temp down on the stat or the actual boiler interface?
    Last edited by Grovis; 24-10-2010 at 09:09 PM.

  5. #5
    uɐɯ sɐƃ moderator



    gas man's Avatar
    Join Date
    Jan 2010
    Location
    maesteg,south wales,land of MTB
    Posts
    18,737
    Thanks
    1,175
    Thanked 1,795 Times in 1,696 Posts

    Default Re: Salus RT500RF Thermostat not controlling boiler?

    i just think the salus is knackered get a more reliable stat
    fear keeps you alive
    fearless gets you killed

    I have a banning hammer and I am not afraid to use it

  6. #6
    Member
    Join Date
    Sep 2010
    Posts
    5
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Salus RT500RF Thermostat not controlling boiler?

    @ gasman - I think you may be onto something lol

    55 mins on and my rads are blistering hot with no drop in temperature!

    I have reset the thermostat several times and tried to manuallyreduce the temperature on it using the overide, but no reaction from the boiler or the Salus wired receiver whatsoever.

    Just seems odd that it will allow me to raise the temperature (green led comes on) but never decrease it (no green led, "click" or reaction from the boiler). As is stands I have no way to control the heating via the thermostat so cannot have timed CH. I have had to switch the CH mode off on the boiler. I'll be getting in touch with my installer!

  7. #7
    UK Plumbersforums Trusted Advisor.

    tamz's Avatar
    Join Date
    Apr 2010
    Location
    Scotland
    Posts
    13,954
    Thanks
    409
    Thanked 1,717 Times in 1,526 Posts

    Default Re: Salus RT500RF Thermostat not controlling boiler?

    In the meantime remove the batteries and reset it.
    Then get a honeywell fitted.
    Salus should be spelt shi..
    gas man likes this.

  8. #8
    Banned
    Join Date
    Aug 2009
    Posts
    1,512
    Thanks
    11
    Thanked 148 Times in 139 Posts

    Default Re: Salus RT500RF Thermostat not controlling boiler?

    Quote Originally Posted by Grovis View Post
    Is there any chance that the TRV are actually controlling the boiler ie by keeping them on max they are continually trying to regulate the room temp? ( I think max is 25c+)
    The TRV is a thermo-mechanical device and is completely independent of the the boiler. All it does is control the flow through the radiator to maintain the required room temperature.


    @Doitmyself - Do you mean turn the temp down on the stat or the actual boiler interface?
    I was meaning the wall thermostat.

    PS I agree about replacing it with a Honeywell.

  9. #9
    Member
    Join Date
    Sep 2010
    Posts
    5
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Salus RT500RF Thermostat not controlling boiler?

    Had the installer out and it was actually a setting inside the boiler which should have been switched off before they wired the Salus receiver. There was continous heating or something along those lines, so the boiler was overiding any requests from the stat to turn down. Anyway 2 days in and the Salus has been good as gold and totally responsive. I will see how it goes but have your recommendations for a Honeywell ready if anything does go pear shaped. Thanks for you help.

  10. #10
    Member
    Join Date
    Jan 2015
    Posts
    3
    Thanks
    2
    Thanked 0 Times in 0 Posts

    Default Re: Salus RT500RF Thermostat not controlling boiler?

    Hi I have the same problem as Grovis. I have the salus rt500rf and a potteron gold he. Does anyone know where the switch is inside the boiler to turn off the override that keeps it heating as abovr.
    Moved in to new property and its like a sauna in here at night!
    Thanks.

  11. #11
    Banned
    Join Date
    Sep 2010
    Posts
    3,261
    Thanks
    72
    Thanked 151 Times in 145 Posts

    Default Re: Salus RT500RF Thermostat not controlling boiler?

    1. you need to start a new thread
    2. you must be gas safe registered to open a boiler

  12. The Following User Says Thank You to jase158 For This Useful Post:


  13. #12
    uɐɯ sɐƃ moderator



    gas man's Avatar
    Join Date
    Jan 2010
    Location
    maesteg,south wales,land of MTB
    Posts
    18,737
    Thanks
    1,175
    Thanked 1,795 Times in 1,696 Posts

    Default Re: Salus RT500RF Thermostat not controlling boiler?

    Quote Originally Posted by Hornberrie View Post
    Hi I have the same problem as Grovis. I have the salus rt500rf and a potteron gold he. Does anyone know where the switch is inside the boiler to turn off the override that keeps it heating as abovr.
    Moved in to new property and its like a sauna in here at night!
    Thanks.
    there is no switch inside the boiler,as jase said,you need a gas safe engineer
    fear keeps you alive
    fearless gets you killed

    I have a banning hammer and I am not afraid to use it

  14. The Following User Says Thank You to gas man For This Useful Post:


Everybody loves a good deal: Deals and Discounts on Dozens of Powertools!
Everybody loves a good deal: Deals and Discounts on Dozens of Powertools!

Similar Threads

  1. salus RT500RF wiring
    By rob652nan in forum Central Heating Forum
    Replies: 0
    Last Post: 09-02-2013, 08:52 AM
  2. Salus rt500rf & glowworm 30? Help!
    By Hock in forum Central Heating Forum
    Replies: 6
    Last Post: 06-01-2013, 12:03 AM
  3. Salus RT500RF 868Mhz Unit Working When Switched OFF
    By andymanila in forum Central Heating Forum
    Replies: 9
    Last Post: 27-07-2012, 11:23 PM
  4. Salus RT500RF remote programmable room stat
    By simbo116 in forum Central Heating Forum
    Replies: 10
    Last Post: 02-03-2012, 05:07 AM
  5. Salus RT500RF Woes
    By Chromedome in forum Central Heating Forum
    Replies: 5
    Last Post: 24-01-2012, 03:14 PM
  6. Controlling ATAG, UFH, and radiators
    By evb222 in forum Central Heating Forum
    Replies: 6
    Last Post: 18-08-2011, 12:23 AM
  7. Replies: 5
    Last Post: 09-11-2010, 12:20 AM
  8. Adding a Salus RT500RF Room Thermostat to Ariston EuroCombi
    By BigManCheese in forum Central Heating Forum
    Replies: 0
    Last Post: 11-02-2010, 10:42 PM
  9. Combi boiler issue controlling non-thermo shower
    By Jimmy Gear in forum Plumbing Forum
    Replies: 2
    Last Post: 15-01-2010, 10:41 AM

Visitors found this page by searching for:

salus rt500rf problem

salus thermostat problems

salus rt500rf troubleshooting

rt500rf problems

salus wireless thermostat problems

Tags for this Thread


Try our Talk Electrician Forum and our popular Tilers Forums for more free advice from professional tradesmen.
Tens of thousands of tradesmen and over 2 million combined posts.


Plumbers Forums is a community-driven forum shared between all members.