Main 24HE flame failure
Hi went to a Main 24 he today (very much a B rated baxi combi HE)
Boiler works fine 50% of the time. There is a fault on CH & DHW mode which is as follows;
Pump runs, primary flow swith operates, fan runs at full speed but there is no atempt at igniton, then flame failure light comes on, will not reset, you have to turn selector swith on/off a couple of times. or;
When the boiler is fired up in either CH or DHW mode the flame will cut out then straight away fire up again and carry on working.
I have had this probem with the baxi 105he and it was the pcb, i keep a selection of pcbs in the van so tried it on this and it hasnt sorted it.
Im thinking check min burner pressure, air pressure switch (unlikey as it does fire up most of the time) flame sensing electrode.
Any iders?? Anybody come across this probem before??
Will be going back to carryout more checks so will update
Cheers!!
-
06-08-2010 #2Top Plumbing Forum Contributor
- Join Date
- Jun 2010
- Location
- Cumberland
- Posts
- 975
- Thanks
- 11
- Thanked 86 Times in 82 Posts
Re: Main 24HE flame failure
Try that air pressure switch. Had it a few times right on the edge of its pressure setting (tiny hole in diaphragm) just creeps off
-
06-08-2010 #3New to Plumbing Forum
- Join Date
- Jun 2009
- Location
- Devon
- Posts
- 25
- Thanks
- 4
- Thanked 0 Times in 0 Posts
Re: Main 24HE flame failure
I see what you mean, just enough for the boiler to cut out but not enough for it to not work at all.
I'll update and cheers for the reply!
-
06-08-2010 #4SUPER MODERATOR



- Join Date
- Jan 2009
- Location
- sherrif county
- Posts
- 9,084
- Thanks
- 241
- Thanked 528 Times in 491 Posts
Re: Main 24HE flame failure
weve had 3 new pcb's on these boilers a few times now, try another.
¡ƃuıɥʇou ʍouʞ ı˙˙˙ɹǝqɯǝɯǝɹ puɐ
˙ʎlddɐ ʇou pǝǝu sǝoɹǝɥ oƃ ɐ ǝʌɐɥ puɐ ǝldoǝd qoɾ ppo `sɹǝ,ʎıp ˙slıɐʇǝp ɹnoʎ ɹoɟ ʞsɐ ǝʍ uǝɥʍ pǝpuǝɟɟo ǝq ʇ,uop ǝsɐǝld os `ǝʇısqǝʍ ǝɟɐs sɐƃ ǝɥʇ ɐıʌ ǝuınuǝƃ ǝɹ,noʎ ʇɐɥʇ ʇno ʞɔǝɥɔ llıʍ ǝʍ ¿ǝɔıʌpɐ ɹıɐdǝɹ ɹǝlıoq ɹo ʎʇǝɟɐs sɐƃ ʇuɐʍ noʎ op
¿ʞɹoʍ sɐƃ

˙lɐoɔ puɐ pooʍ `sɐƃ `lıo ƃuıpnlɔuı `ʇuɹnq sı lǝnɟ ʎuɐ uǝɥʍ pǝɔnpoɹd ǝq uɐɔ ǝpıxouoɯ uoqɹɐɔ :ʇuɐʇɹodɯı
-
07-08-2010 #5uɐɯ sɐƃ moderator



- Join Date
- Jan 2010
- Location
- maesteg,south wales
- Posts
- 13,315
- Thanks
- 827
- Thanked 1,264 Times in 1,207 Posts
Re: Main 24HE flame failure
could be airswitch had a few go on the main,pcb tends to give the same fault but they are not weak boards
GASMAN
fear keeps you alive
fearless gets you killed
IMPORTANT: Carbon Monoxide can be produced when ANY fuel is burnt, including oil, gas, wood and coal.
GSR?want gas safety or boiler repair advice?we will check out that your genuine via the gas safe website,so please dont be offended when we ask for your details
diyers,potchers,odd job people and have a go heroes need not apply
BAXI/POTTERTON INSTALLER/SERVICE ENGINEER
land rover equipped,you can go faster,i can go anywhere
-
09-08-2010 #6New to Plumbing Forum
- Join Date
- Jun 2009
- Location
- Devon
- Posts
- 25
- Thanks
- 4
- Thanked 0 Times in 0 Posts
Re: Main 24HE flame failure
Went back and replaced the air pressure switch- Sorted it!
I noted in the manufactures instructions it says to take the fan out first in order to get to the air pressure switch (HE model) I just loosend off the side panel and got my hands in there, a lot quicker than taking the fan out!!
Good diagnosis guys, and thanks for the replys!
-
24-12-2010 #7New to Plumbing Forum
- Join Date
- Dec 2010
- Posts
- 2
- Thanks
- 0
- Thanked 0 Times in 0 Posts
Re: Main 24HE flame failure
pls help. my baxi 24 he burner fails. cannot get it to start up. i am not a plumber unfortunately but would like to see if i can try to rectify the prob with your help
-
25-12-2010 #8uɐɯ sɐƃ moderator



- Join Date
- Jan 2010
- Location
- maesteg,south wales
- Posts
- 13,315
- Thanks
- 827
- Thanked 1,264 Times in 1,207 Posts
Re: Main 24HE flame failure
GASMAN
fear keeps you alive
fearless gets you killed
IMPORTANT: Carbon Monoxide can be produced when ANY fuel is burnt, including oil, gas, wood and coal.
GSR?want gas safety or boiler repair advice?we will check out that your genuine via the gas safe website,so please dont be offended when we ask for your details
diyers,potchers,odd job people and have a go heroes need not apply
BAXI/POTTERTON INSTALLER/SERVICE ENGINEER
land rover equipped,you can go faster,i can go anywhere
-
25-12-2010 #9Plumbers Arms member

- Join Date
- Oct 2010
- Posts
- 1,654
- Thanks
- 0
- Thanked 81 Times in 81 Posts
Re: Main 24HE flame failure
a nice kettle of hot water on pipe should do it
-
26-12-2010 #10New to Plumbing Forum
- Join Date
- Dec 2010
- Posts
- 2
- Thanks
- 0
- Thanked 0 Times in 0 Posts
-
26-12-2010 #11uɐɯ sɐƃ moderator



- Join Date
- Jan 2010
- Location
- maesteg,south wales
- Posts
- 13,315
- Thanks
- 827
- Thanked 1,264 Times in 1,207 Posts
Re: Main 24HE flame failure
probable ap switch failing
GASMAN
fear keeps you alive
fearless gets you killed
IMPORTANT: Carbon Monoxide can be produced when ANY fuel is burnt, including oil, gas, wood and coal.
GSR?want gas safety or boiler repair advice?we will check out that your genuine via the gas safe website,so please dont be offended when we ask for your details
diyers,potchers,odd job people and have a go heroes need not apply
BAXI/POTTERTON INSTALLER/SERVICE ENGINEER
land rover equipped,you can go faster,i can go anywhere
Similar Threads
-
New connection from water main.
By sparky in forum Plumbing ForumReplies: 4Last Post: 20-07-2010, 10:18 PM -
Main combi 24 he dhw problem
By GrumpyOldGit in forum Central Heating ForumReplies: 8Last Post: 26-06-2010, 09:57 AM -
Rising main to cold water cistern in loft
By Gareth in forum Plumbing ForumReplies: 7Last Post: 20-02-2010, 01:55 AM -
Potterton Profile 60e Main Burner cuts out
By pickse in forum Central Heating ForumReplies: 7Last Post: 28-11-2009, 06:21 PM -
Trianco Eurostar 65 will not flame
By etaf in forum Central Heating ForumReplies: 0Last Post: 24-12-2008, 04:39 PM



Reply With Quote










Bad air lock in cold feed
21 Minutes Ago in Plumbing Forum