hi guys, just need some advise on this one.....
I got called to a job today and when i asked for the heating to come on the boiler fired up and the pipes round the cylinder were all hot and both sides of the pump!! I tried bleeding the rads to try drag any air out the system but this didnt work. the man said he would be happy for us to do a power flush to get rid of this problem and also any sludge in the system. i just want to know if you guys think that the flush would cure the problem.
thank a lot.
-
23-07-2010 #2Top Plumbing Forum Contributor
- Join Date
- Apr 2010
- Posts
- 838
- Thanks
- 0
- Thanked 33 Times in 32 Posts
Re: rads not getting hot, but hot water is!!!
You'll need to fault find on the ch/hw elect circuit, check the programmer/stats and zone valves are functioning correctly b4 u charge for a p/flush.
Have u done any fault finding at all?
-
23-07-2010 #3New to Plumbing Forum
- Join Date
- Jul 2010
- Posts
- 10
- Thanks
- 0
- Thanked 0 Times in 0 Posts
Re: rads not getting hot, but hot water is!!!
There is power going to the programmer and it is turning the heating on. The two port valve is working corectly too! one rad got warm closest to the boiler but that was it. so with the one rad getting warm i thought there must be a block????
He has no room stats anywhere in the house just one thermo rad valve downstairs.
-
23-07-2010 #4Top Plumbing Forum Contributor
- Join Date
- Apr 2010
- Posts
- 838
- Thanks
- 0
- Thanked 33 Times in 32 Posts
Re: rads not getting hot, but hot water is!!!
Is the pump Circulating?
Checking for blockages or airlocks would be my next step aswell. Do u know about the fridge magnet trick when checking for chokeages?
-
23-07-2010 #5New to Plumbing Forum
- Join Date
- Jul 2010
- Posts
- 10
- Thanks
- 0
- Thanked 0 Times in 0 Posts
Re: rads not getting hot, but hot water is!!!
fridge magnit??? no
ha
The pump is running yes, and what would you advise the best way to check were the block could be??
If it is a block, witch it sound like, i assume a flush would do the job?? I know its not the most cost effective but i think the guy would like one anyway.
-
23-07-2010 #6Top Plumbing Forum Contributor
- Join Date
- Apr 2010
- Posts
- 838
- Thanks
- 0
- Thanked 33 Times in 32 Posts
Re: rads not getting hot, but hot water is!!!
Yes but is it circulating? Take the bleed screw out the pump and check it's rotating.
Take a normal fridge magnet and check it against sections of copper pipework where u suspect the blockage may be, parts of the return or maybe the cold feed, the magnet will stick to copper pipework choked with magnetite, it will not stick to areas that are not blocked. If it is completely choked in a certain area then I doubt a p/flush will clear a choked pipe on it's own, it would usually need cut out and replaced.
-
23-07-2010 #7Top Plumbing Forum Contributor
- Join Date
- Oct 2008
- Location
- Scotland
- Posts
- 366
- Thanks
- 4
- Thanked 36 Times in 36 Posts
Re: rads not getting hot, but hot water is!!!
nice trick, never tried it myself. atleast you can probably say the blockage is either flow or return before first radiator. bit of a nightmare locating blockages, can see why your thinking power flush
-
24-07-2010 #8New to Plumbing Forum
- Join Date
- Jun 2010
- Location
- Harrow, Middx
- Posts
- 4
- Thanks
- 0
- Thanked 0 Times in 0 Posts
Re: rads not getting hot, but hot water is!!!
Is the header tank full? Check that the ball valve hasn't got stuck. I assume that you have tried manually opening the motorised valve?
-
24-07-2010 #9UK Plumbersforums Trusted Advisor.


- Join Date
- Apr 2010
- Location
- Scotland
- Posts
- 9,363
- Thanks
- 281
- Thanked 1,178 Times in 1,045 Posts
Re: rads not getting hot, but hot water is!!!
Taking the screw out and checking the pump is rotating is not sufficient to prove the pump is circulating properly. I have had a few cases where the impeller is worn or broken and although it may circulate somewhat it does not provide enough head.
Matty
Check the water quality and you will know if it needs a flush.
-
25-07-2010 #10New to Plumbing Forum
- Join Date
- Jul 2010
- Posts
- 10
- Thanks
- 0
- Thanked 0 Times in 0 Posts
Re: rads not getting hot, but hot water is!!!
yes the motorised valve is working corectly and the header tank is full. The pump is working but if your saying you had cases were the blades have worn, i have spare pumps in the van so will try a new pump and see if this resolves the problem. thanks
Similar Threads
-
central heating and hot water not working again..
By mad_cereal_love in forum Central Heating ForumReplies: 3Last Post: 02-02-2010, 08:47 PM -
Hot Water only luke warm
By baglartimus in forum Plumbing ForumReplies: 1Last Post: 07-01-2010, 11:47 AM -
Bungalow with requirement for instant hot water and more water pressure in bathrooms
By David Salter in forum Bathrooms, Showers and WetroomsReplies: 3Last Post: 06-10-2009, 11:56 PM -
Hwlo with wold water tank overflowing
By philwilliams in forum Plumbing ForumReplies: 2Last Post: 13-04-2009, 08:57 PM -
Brown hot water
By Leeky in forum Central Heating ForumReplies: 10Last Post: 14-12-2008, 02:50 PM



Reply With Quote










Pipe bender?
2 Minutes Ago in Plumbing Tools