Plumbing & Plumbers Forum - optima 701 DHW problem

optima 701 DHW problem

Discuss optima 701 DHW problem in the Central Heating Forum at Plumbers Forums; Hi my hot water stoped working yesterday il describe what happens Nothing when you open the hot water tap not a sound comes from the boiler no clicks or anything.Central ...
  1. #1
    New to Plumbing Forum
    Join Date
    May 2010
    Posts
    6
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default optima 701 DHW problem

    Hi my hot water stoped working yesterday il describe what happens

    Nothing when you open the hot water tap not a sound comes from the boiler no clicks or anything.Central heating works fine.
    so today i decided to join the forum to see if i can get any help but before i did i downloaded the Manual and noticed the fault finding LEDs were fine no faults were showing so i decided to press the reset button on the clock and run the heating for 30 mins and the hot water decided to work it seems fine now working as it should but am pretty sure this wasnt a one off so need some advice if it happens again

    many thanks


  2. #2
    uɐɯ sɐƃ moderator


    gas man's Avatar
    Join Date
    Jan 2010
    Location
    maesteg,south wales
    Posts
    13,341
    Thanks
    827
    Thanked 1,266 Times in 1,209 Posts

    Default Re: optima 701 DHW problem

    could be a thermistor fault


  3. GASMAN
    fear keeps you alive
    fearless gets you killed

    IMPOR
    TANT: Carbon Monoxide can be produced when ANY fuel is burnt, including oil, gas, wood and coal.
    GSR?want gas safety or boiler repair advice?we will check out that your genuine via the gas safe website,so please dont be offended when we ask for your details
    diyers,potchers,odd job people and have a go heroes need not apply
    ​BAXI/POTTERTON INSTALLER/SERVICE ENGINEER
    ​ land rover equipped,you can go faster,i can go anywhere


  4. #3
    New to Plumbing Forum
    Join Date
    May 2010
    Posts
    6
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: optima 701 DHW problem

    ok great many thanks i shall order one just incase

    thanks again

  5. #4
    Top Plumbing Forum Contributor
    Join Date
    Apr 2010
    Posts
    838
    Thanks
    0
    Thanked 33 Times in 32 Posts

    Default Re: optima 701 DHW problem

    IT sounds like a dhw flow switch fault but i can't for the life of me remember if the optimas have a flow switch. If no flow switch then I'd say sensor also

  6. #5
    New to Plumbing Forum
    Join Date
    May 2010
    Posts
    6
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: optima 701 DHW problem

    Hi there is a Flowmeter acording to the manual and i will paste a section here of the only mention of a flow switch

    "
    The pump circuit also has a 6 minute over-run
    time. There is a Domestic Hot Water flow switch fitted and when there is a demand for Domestic Hot
    Water the Central Heating pump is switched off making available the maximum output of the gas burner
    for Domestic Hot Water"

  7. #6
    Top Plumbing Forum Contributor
    Join Date
    Apr 2010
    Posts
    838
    Thanks
    0
    Thanked 33 Times in 32 Posts

    Default Re: optima 701 DHW problem

    Quote Originally Posted by corbyboy View Post
    Hi there is a Flowmeter acording to the manual and i will paste a section here of the only mention of a flow switch

    "
    The pump circuit also has a 6 minute over-run
    time. There is a Domestic Hot Water flow switch fitted and when there is a demand for Domestic Hot
    Water the Central Heating pump is switched off making available the maximum output of the gas burner
    for Domestic Hot Water"
    there u go mate. It'll be this flow switch, it won't recognise that you are running a tap obviously if it's goosed, it's the same as not running hot water if it was working correctly as far as it's concerned at the min, therefore no fault code will show for this particular fault

    if u are able to link out the flow switch and the boiler fires for hw then it's defo at fault. This is the easiest way to prove a faulty component

    One last thing to add.

    U could try removing it and clean it. U may find it's not faulty and simply choked up
    Last edited by Mbear; 31-05-2010 at 06:50 PM. Reason: Automerged Doublepost

  8. #7
    New to Plumbing Forum
    Join Date
    May 2010
    Posts
    6
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: optima 701 DHW problem

    hi any idea were it is? my problem is in the manual the only part listed sith the word switch is
    Low water pressure switch
    is this it?

    many thanks

  9. #8
    Top Plumbing Forum Contributor
    Join Date
    Apr 2010
    Posts
    838
    Thanks
    0
    Thanked 33 Times in 32 Posts

    Default Re: optima 701 DHW problem

    Quote Originally Posted by corbyboy View Post
    hi any idea were it is? my problem is in the manual the only part listed sith the word switch is
    Low water pressure switch
    is this it?

    many thanks
    no that's the low system pressure switch ie pressure is at 0.25bar then this switch breaks for example.

    The flow switch will be on the mains in pipe internally in the boiler

  10. #9
    New to Plumbing Forum
    Join Date
    May 2010
    Posts
    6
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: optima 701 DHW problem

    Hi sorry all i can see on the diagram is a flowmeter

  11. #10
    Top Plumbing Forum Contributor
    Join Date
    Apr 2010
    Posts
    838
    Thanks
    0
    Thanked 33 Times in 32 Posts

    Default Re: optima 701 DHW problem

    Quote Originally Posted by corbyboy View Post
    Hi sorry all i can see on the diagram is a flowmeter
    That sounds like the culprit. I'm sure flowmeter is the term ferroli use. They definetely use a flowmeter on the ferroli Modena combi for the hw side

  12. #11
    New to Plumbing Forum
    Join Date
    May 2010
    Posts
    6
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: optima 701 DHW problem

    nice one i will strip it tomorrow failing that its only £38 to replace

Similar Threads

  1. CWSC overflow problem
    By pg1066 in forum Plumbing Forum
    Replies: 8
    Last Post: 19-05-2010, 12:21 AM
  2. baxi 105e dhw problem
    By bryan in forum Central Heating Forum
    Replies: 5
    Last Post: 14-04-2010, 02:28 PM
  3. ferrolli optima 701
    By metalmick in forum Central Heating Forum
    Replies: 3
    Last Post: 22-03-2010, 07:14 PM
  4. Potterton 30HE DHW cut out problem
    By pebrey in forum Central Heating Forum
    Replies: 4
    Last Post: 12-12-2009, 10:18 PM
  5. MicroGenus 23 DHW problem
    By Nigel 206 in forum Plumbing Forum
    Replies: 0
    Last Post: 15-03-2009, 01:21 PM

Visitors found this page by searching for:

optima 701

optima 701 manual

ferroli optima 701 manual

optima 701 boiler manual

optima 701 boiler

ferroli optima 701 boiler manual

how to test a flow switch on feroli optima 702

Tags for this Thread

Plumbers Forums is a Trading Style of Untold Developments Ltd. Search Engine Optimisation, Web Development and Online Marketing for the UK.