Default Re: Delay in reaching temperature.

news flash !! if you run high flow temps on a condensing boiler you are asking for trouble!!! especially ideal!! if ideals can t dump heat it causes loads of problems!!!!

you should be running a max flow temp of around 70 degrees C

i don't know off the top of my head but check the pump speed!!!
(don't know if ideal pumps have speed adjustment)

get installer to make sure they have 20 degrees differential between flow and return to make sure boiler condenses

also make sure there is 15 degrees differential across the the radiators