Quote:
Originally Posted by ajs heating View Post
for one you don't need to zone it.
next you have fitted a trv in the same room as your room stat which is wrong as they play against each other.
so when the trv shuts the room stat thinks the room is not hot enough and keeps the boiler on longer.
then try balancing your system, their is no such thing as can't balance a system it knowing how to do it right.
Thanks for the reply.

Sorry. I should have said that the room with the stat does not have a trv.

The main reason we want to have the zone upstairs, is my 6yr old son who has medical problems, keeps resetting the trv's to max in the upstairs rooms (he likes to play with things) and they are getting much hotter that the rest of the house. So as the bedrooms do not need to be as warm as downstairs, we would like to set the temp via a room stat.

Thanks.